Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

[Imported] SQL Join CGroup and CADVOUSTATION

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Re: [Imported] SQL Join CGroup and CADVOUSTATION
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
337
AndrewScott
AndrewScott
128
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-07 03:40 AM . Last Modified: ‎2023-05-03 12:23 AM

0 Likes
1
1747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 03:40 AM . Last Modified: ‎2023-05-03 12:23 AM

[Imported] SQL Join CGroup and CADVOUSTATION

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: hardin4019, originally posted: 2019-07-02 13:13:43 Id:463
Having some more fun with SQL queries.

I have a list that gives me several columns of meter data from the Group Points of from a template for said meter data that use OPC points, and a few modbus values from a valve associated with the meter location that are also mapped out in the Group Points. Inside the meter template is an instance of a valve Group template. The Valve Group contains its own comms folder and Advanced Modbus Outstation.

The modbus values from the valve can be assigned to the meter template/instance Group points without an issue, but I would like to assign the Modbus Outstation to the Group points or another metadata field and was failing to find a way to do that, so I resulted to SQL joining. Now I have a partially working list that shows the Modbus RTU Status, but I have lost the ability to click on points and see the object menu and cannot click on the RTU State and get any of the RTU object menu to appear. For clarification, the CGROUP.gChild01 contains the path of the MeterNumber.MOV.COMMS folder. Since it is nested inside of the meter folder 2 layers deeper, this is the only thing I could think of to match the Outstation to the grand parent group.

Sample of the Query:

Select
CGROUP.ID,
CGROUP.FullName AS "_FullName",
CGroup.objProperty02 AS "~Producer",
GPoint01-CurrentValueFormatted AS "Discharge Pressure", GPoint01 AS "_ID01,
CADVOUTSTATION.ID AS "_OSID",
CADVOUTSTATION.StateDesc
FROM
CGROUP Join CADVOUTSTATION ON CGROUP.gChild01 = CADVOUTSTATION.ParentGroupID


The script that appears to be checking the column # and Row # returns the correct column +1 and row +1 (assuming it is counting the header and an ID column not shown), but the script looks to be creating an additional query and has a resulting rs.rowcount = 0 where the script then ends. Not sure why after adding the SQL Join and new columns that this rs.rowcount suddenly stops working unless I somehow nerfed the query with the "From CGROUP Join CADVOUTSTATION On CGROUP.gChild01 = CADVOUTSTATION.ParentGroupID".

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-07 03:41 AM

0 Likes
0
1746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 03:41 AM

>>Responses imported from previous forum


Reply From User: hardin4019, posted: 2019-07-02 16:33:17
After further troubleshooting, there is a WHERE statement that is being used to limit the meter list to a certain types and regions. If it is present, then I don't get a rs.rowcount. Otherwise it works.

WHERE
CGroup.GrType IN ( 'Meter' ) and CGroup.ObjType IN ( 'Inlet' , 'Check' ) and "_FullName" Like 'Region 1.%'


Reply From User: BevanWeiss, posted: 2019-07-10 23:55:17
You haven't show what gChild01 would be... is it an ID which would match the CAdvOutstation ParentGroup's ID?

Or did you mean to use CAdvOutstatation.ParentGroupName instead?


Reply From User: hardin4019, posted: 2019-07-11 02:03:27
gChild01 in the meter group properties points to the comms folder and automatically populates since all of the groups are part of a template. The comms folder contains the RTU and would match the CAdvOutstation.ParentGroupName.

IE. MeterName.Valve.Comms.RTU where the MeterName group holds all of the OPC points, the Valve group holds all of the Modbus valve points, and in the comms folder is the RTU and channels for the valve points.

Since the valve comms folder is nested in the 3rd group, I couldn't find a way to join the two tables without giving some reference in the meter group that would bridge 2 groups deeper.


Reply From User: BevanWeiss, posted: 2019-07-11 05:38:43
[at]hardin4019 said:
gChild01 in the meter group properties points to the comms folder and automatically populates since all of the groups are part of a template. The comms folder contains the RTU and would match the CAdvOutstation.ParentGroupName.

IE. MeterName.Valve.Comms.RTU where the MeterName group holds all of the OPC points, the Valve group holds all of the Modbus valve points, and in the comms folder is the RTU and channels for the valve points.

Since the valve comms folder is nested in the 3rd group, I couldn't find a way to join the two tables without giving some reference in the meter group that would bridge 2 groups deeper.

You wrote this:
CGROUP.gChild01 = CADVOUTSTATION.ParentGroupID

If as you say gChild01 is "FullName".. this will not = 1897034 (i.e. the Parent Group ID).. since a number never 'equals' a string.

Provide your whole query, and an example of the data for every field referenced in the query.


Reply From User: hardin4019, posted: 2019-07-11 16:00:08
gChild01 only contains the parent group of the outstation. When I add CGroup.gChild01 to the query, the ID number and not the string name is what comes back as the result, and I can add the CAdvOustatation.ParentGroupID to the query, I can see that both ID's match. Doing the join and getting what I want displayed isn't the issue.

Are you saying that gChild01 returns a string (containing the ID number) instead of just an ID? I would have suspected that if that were the case, then the join would have never worked.

Full Query:

SELECT
CGROUP.ID,
CGROUP.FULLNAME AS "_FullName",
CGROUP.OBJPROPERTY02 AS "~Producer",
CGROUP.OBJSHORTDESC AS "~Meter\
Number",
CGROUP.OBJDISPLAYNAME AS "~Station",
CGROUP.OBJPROPERTY07 AS "~Gathering\
System",
CGROUP.OBJPROPERTY08 AS "~Compressor\
Station A",
CGROUP.OBJPROPERTY09 AS "~Compressor\
Station B",
GPOINT01-BACKGROUND AS "{Background01}", GPOINT01-FOREGROUND AS "{Foreground01}", GPOINT01-BLINK AS "{blink01}", GPOINT01-CURRENTVALUEFORMATTED AS "Discharge\
Pressure", GPOINT01 AS "_ID01",
GPOINT03-BACKGROUND AS "{Background03}", GPOINT03-FOREGROUND AS "{Foreground03}", GPOINT03-BLINK AS "{blink03}", GPOINT03-CURRENTVALUEFORMATTED AS "Temp", GPOINT03 AS "_ID03",
GPOINT04-BACKGROUND AS "{Background04}", GPOINT04-FOREGROUND AS "{Foreground04}", GPOINT04-BLINK AS "{blink04}", GPOINT04-CURRENTVALUEFORMATTED AS "Flow\
Rate", GPOINT04 AS "_ID04",
GPOINT05-BACKGROUND AS "{Background05}", GPOINT05-FOREGROUND AS "{Foreground05}", GPOINT05-BLINK AS "{blink05}", GPOINT05-CURRENTVALUEFORMATTED AS "T-day\
Volume", GPOINT05 AS "_ID05",
GPOINT07-BACKGROUND AS "{Background07}", GPOINT07-FOREGROUND AS "{Foreground07}", GPOINT07-BLINK AS "{blink07}", GPOINT07-CURRENTVALUEFORMATTED AS "Y-day's\
Volume", GPOINT07 AS "_ID07",
GPOINT15-BACKGROUND AS "{Background15}", GPOINT15-FOREGROUND AS "{Foreground15}", GPOINT15-BLINK AS "{blink15}", GPOINT15-CURRENTVALUEFORMATTED AS "MTR\
DCV", GPOINT15 AS "_ID15",
GPOINT16-BACKGROUND AS "{Background16}", GPOINT16-FOREGROUND AS "{Foreground16}", GPOINT16-BLINK AS "{blink16}", GPOINT16-CURRENTSTATEDESC AS "MTR\
Comms", GPOINT16 AS "_ID16",
GPOINT13-BACKGROUND AS "{Background13}", GPOINT13-FOREGROUND AS "{Foreground13}", GPOINT13-BLINK AS "{blink13}", GPOINT13-CURRENTSTATEDESC AS "Valve\
Status", GPOINT13 AS "_ID13",
GPOINT14-BACKGROUND AS "{Background14}", GPOINT14-FOREGROUND AS "{Foreground14}", GPOINT14-BLINK AS "{blink14}", GPOINT14-CURRENTSTATEDESC AS "Cmd\
Status", GPOINT14 AS "_ValveStatus",
GPOINT10-BACKGROUND AS "{Background10}", GPOINT10-FOREGROUND AS "{Foreground10}", GPOINT10-BLINK AS "{blink10}", GPOINT10-CURRENTVALUEFORMATTED AS "Upstream\
Pressure", GPOINT10 AS "_ID10",
GPOINT11-BACKGROUND AS "{Background11}", GPOINT11-FOREGROUND AS "{Foreground11}", GPOINT11-BLINK AS "{blink11}", GPOINT11-CURRENTVALUEFORMATTED AS "Downstream\
Pressure", GPOINT11 AS "_ID11",
GPOINT02-BACKGROUND AS "{Background02}", GPOINT02-FOREGROUND AS "{Foreground02}", GPOINT02-BLINK AS "{blink02}", GPOINT02-CURRENTVALUEFORMATTED AS "Differential\
Pressure", GPOINT02 AS "_ID02",
GPOINT12-BACKGROUND AS "{Background12}", GPOINT12-FOREGROUND AS "{Foreground12}", GPOINT12-BLINK AS "{blink12}", GPOINT12-CURRENTVALUEFORMATTED AS "MOV\
DCV", GPOINT12 AS "_ID12",
CADVOUTSTATION.STATEDESC,
CADVOUTSTATION.ID AS "_ID"
FROM
CGROUP JOIN CADVOUTSTATION ON CGROUP.GCHILD01 = CADVOUTSTATION.PARENTGROUPID
WHERE
CGROUP.GRPTYPE IN ( 'Meter' ) AND CGROUP.OBJTYPE IN ( 'Inlet', 'Check' ) AND "_FullName" LIKE 'Region1.%'
ORDER BY
"~Meter\
Number" ASC


Reply From User: BevanWeiss, posted: 2019-07-12 00:25:33
gChild01 is a customised Metadata field from YOUR custom configuration.
So you should be the person that knows what the configuration of it is :tongue:

Does the query return results if you remove the JOIN conditions (and fields from return)


Reply From User: hardin4019, posted: 2019-07-12 01:09:48
Yes if I leave off the join it returns results. It also returns results with the join. But with the where and join both present, I'm not getting a row count. That is what has me stumped.


Reply From User: BevanWeiss, posted: 2019-07-15 12:25:34
When you call the following query... how many of these entries have CGROUP.GRPTYPE = 'Meter', AND CGROUP.OBJTYPE = 'Inlet' or 'Check'?

SELECT
CGROUP.ID,
CGROUP.FULLNAME AS "_FullName",
CGROUP.OBJPROPERTY02 AS "~Producer",
CGROUP.OBJSHORTDESC AS "~Meter\
Number",
CGROUP.OBJDISPLAYNAME AS "~Station",
CGROUP.OBJPROPERTY07 AS "~Gathering\
System",
CGROUP.OBJPROPERTY08 AS "~Compressor\
Station A",
CGROUP.OBJPROPERTY09 AS "~Compressor\
Station B",
CGROUP.GRPTYPE,
CGROUP.OBJTYPE,
CGROUP.GCHILD01,
CADVOUTSTATION.PARENTGROUPID
FROM
CGROUP JOIN CADVOUTSTATION ON CGROUP.GCHILD01 = CADVOUTSTATION.PARENTGROUPID
WHERE "_FullName" LIKE 'Region1.%'
ORDER BY
"~Meter\
Number" ASC


I suspect the answer is 0 (zero)... hence why your query including the WHERE clause returns no rows.


Reply From User: hardin4019, posted: 2019-07-15 12:45:22
Approximately 130 rows.


Reply From User: hardin4019, posted: 2019-07-15 16:30:33
Found a working solution.

I was able to go in and add my own Metadata field to the CGroup table that is linked to the Modbus Outstation and add the new column to my query without issue. Pick Actions work and return the correct Pick Action menu for the Outstation.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-07 03:41 AM

0 Likes
0
1747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 03:41 AM

>>Responses imported from previous forum


Reply From User: hardin4019, posted: 2019-07-02 16:33:17
After further troubleshooting, there is a WHERE statement that is being used to limit the meter list to a certain types and regions. If it is present, then I don't get a rs.rowcount. Otherwise it works.

WHERE
CGroup.GrType IN ( 'Meter' ) and CGroup.ObjType IN ( 'Inlet' , 'Check' ) and "_FullName" Like 'Region 1.%'


Reply From User: BevanWeiss, posted: 2019-07-10 23:55:17
You haven't show what gChild01 would be... is it an ID which would match the CAdvOutstation ParentGroup's ID?

Or did you mean to use CAdvOutstatation.ParentGroupName instead?


Reply From User: hardin4019, posted: 2019-07-11 02:03:27
gChild01 in the meter group properties points to the comms folder and automatically populates since all of the groups are part of a template. The comms folder contains the RTU and would match the CAdvOutstation.ParentGroupName.

IE. MeterName.Valve.Comms.RTU where the MeterName group holds all of the OPC points, the Valve group holds all of the Modbus valve points, and in the comms folder is the RTU and channels for the valve points.

Since the valve comms folder is nested in the 3rd group, I couldn't find a way to join the two tables without giving some reference in the meter group that would bridge 2 groups deeper.


Reply From User: BevanWeiss, posted: 2019-07-11 05:38:43
[at]hardin4019 said:
gChild01 in the meter group properties points to the comms folder and automatically populates since all of the groups are part of a template. The comms folder contains the RTU and would match the CAdvOutstation.ParentGroupName.

IE. MeterName.Valve.Comms.RTU where the MeterName group holds all of the OPC points, the Valve group holds all of the Modbus valve points, and in the comms folder is the RTU and channels for the valve points.

Since the valve comms folder is nested in the 3rd group, I couldn't find a way to join the two tables without giving some reference in the meter group that would bridge 2 groups deeper.

You wrote this:
CGROUP.gChild01 = CADVOUTSTATION.ParentGroupID

If as you say gChild01 is "FullName".. this will not = 1897034 (i.e. the Parent Group ID).. since a number never 'equals' a string.

Provide your whole query, and an example of the data for every field referenced in the query.


Reply From User: hardin4019, posted: 2019-07-11 16:00:08
gChild01 only contains the parent group of the outstation. When I add CGroup.gChild01 to the query, the ID number and not the string name is what comes back as the result, and I can add the CAdvOustatation.ParentGroupID to the query, I can see that both ID's match. Doing the join and getting what I want displayed isn't the issue.

Are you saying that gChild01 returns a string (containing the ID number) instead of just an ID? I would have suspected that if that were the case, then the join would have never worked.

Full Query:

SELECT
CGROUP.ID,
CGROUP.FULLNAME AS "_FullName",
CGROUP.OBJPROPERTY02 AS "~Producer",
CGROUP.OBJSHORTDESC AS "~Meter\
Number",
CGROUP.OBJDISPLAYNAME AS "~Station",
CGROUP.OBJPROPERTY07 AS "~Gathering\
System",
CGROUP.OBJPROPERTY08 AS "~Compressor\
Station A",
CGROUP.OBJPROPERTY09 AS "~Compressor\
Station B",
GPOINT01-BACKGROUND AS "{Background01}", GPOINT01-FOREGROUND AS "{Foreground01}", GPOINT01-BLINK AS "{blink01}", GPOINT01-CURRENTVALUEFORMATTED AS "Discharge\
Pressure", GPOINT01 AS "_ID01",
GPOINT03-BACKGROUND AS "{Background03}", GPOINT03-FOREGROUND AS "{Foreground03}", GPOINT03-BLINK AS "{blink03}", GPOINT03-CURRENTVALUEFORMATTED AS "Temp", GPOINT03 AS "_ID03",
GPOINT04-BACKGROUND AS "{Background04}", GPOINT04-FOREGROUND AS "{Foreground04}", GPOINT04-BLINK AS "{blink04}", GPOINT04-CURRENTVALUEFORMATTED AS "Flow\
Rate", GPOINT04 AS "_ID04",
GPOINT05-BACKGROUND AS "{Background05}", GPOINT05-FOREGROUND AS "{Foreground05}", GPOINT05-BLINK AS "{blink05}", GPOINT05-CURRENTVALUEFORMATTED AS "T-day\
Volume", GPOINT05 AS "_ID05",
GPOINT07-BACKGROUND AS "{Background07}", GPOINT07-FOREGROUND AS "{Foreground07}", GPOINT07-BLINK AS "{blink07}", GPOINT07-CURRENTVALUEFORMATTED AS "Y-day's\
Volume", GPOINT07 AS "_ID07",
GPOINT15-BACKGROUND AS "{Background15}", GPOINT15-FOREGROUND AS "{Foreground15}", GPOINT15-BLINK AS "{blink15}", GPOINT15-CURRENTVALUEFORMATTED AS "MTR\
DCV", GPOINT15 AS "_ID15",
GPOINT16-BACKGROUND AS "{Background16}", GPOINT16-FOREGROUND AS "{Foreground16}", GPOINT16-BLINK AS "{blink16}", GPOINT16-CURRENTSTATEDESC AS "MTR\
Comms", GPOINT16 AS "_ID16",
GPOINT13-BACKGROUND AS "{Background13}", GPOINT13-FOREGROUND AS "{Foreground13}", GPOINT13-BLINK AS "{blink13}", GPOINT13-CURRENTSTATEDESC AS "Valve\
Status", GPOINT13 AS "_ID13",
GPOINT14-BACKGROUND AS "{Background14}", GPOINT14-FOREGROUND AS "{Foreground14}", GPOINT14-BLINK AS "{blink14}", GPOINT14-CURRENTSTATEDESC AS "Cmd\
Status", GPOINT14 AS "_ValveStatus",
GPOINT10-BACKGROUND AS "{Background10}", GPOINT10-FOREGROUND AS "{Foreground10}", GPOINT10-BLINK AS "{blink10}", GPOINT10-CURRENTVALUEFORMATTED AS "Upstream\
Pressure", GPOINT10 AS "_ID10",
GPOINT11-BACKGROUND AS "{Background11}", GPOINT11-FOREGROUND AS "{Foreground11}", GPOINT11-BLINK AS "{blink11}", GPOINT11-CURRENTVALUEFORMATTED AS "Downstream\
Pressure", GPOINT11 AS "_ID11",
GPOINT02-BACKGROUND AS "{Background02}", GPOINT02-FOREGROUND AS "{Foreground02}", GPOINT02-BLINK AS "{blink02}", GPOINT02-CURRENTVALUEFORMATTED AS "Differential\
Pressure", GPOINT02 AS "_ID02",
GPOINT12-BACKGROUND AS "{Background12}", GPOINT12-FOREGROUND AS "{Foreground12}", GPOINT12-BLINK AS "{blink12}", GPOINT12-CURRENTVALUEFORMATTED AS "MOV\
DCV", GPOINT12 AS "_ID12",
CADVOUTSTATION.STATEDESC,
CADVOUTSTATION.ID AS "_ID"
FROM
CGROUP JOIN CADVOUTSTATION ON CGROUP.GCHILD01 = CADVOUTSTATION.PARENTGROUPID
WHERE
CGROUP.GRPTYPE IN ( 'Meter' ) AND CGROUP.OBJTYPE IN ( 'Inlet', 'Check' ) AND "_FullName" LIKE 'Region1.%'
ORDER BY
"~Meter\
Number" ASC


Reply From User: BevanWeiss, posted: 2019-07-12 00:25:33
gChild01 is a customised Metadata field from YOUR custom configuration.
So you should be the person that knows what the configuration of it is :tongue:

Does the query return results if you remove the JOIN conditions (and fields from return)


Reply From User: hardin4019, posted: 2019-07-12 01:09:48
Yes if I leave off the join it returns results. It also returns results with the join. But with the where and join both present, I'm not getting a row count. That is what has me stumped.


Reply From User: BevanWeiss, posted: 2019-07-15 12:25:34
When you call the following query... how many of these entries have CGROUP.GRPTYPE = 'Meter', AND CGROUP.OBJTYPE = 'Inlet' or 'Check'?

SELECT
CGROUP.ID,
CGROUP.FULLNAME AS "_FullName",
CGROUP.OBJPROPERTY02 AS "~Producer",
CGROUP.OBJSHORTDESC AS "~Meter\
Number",
CGROUP.OBJDISPLAYNAME AS "~Station",
CGROUP.OBJPROPERTY07 AS "~Gathering\
System",
CGROUP.OBJPROPERTY08 AS "~Compressor\
Station A",
CGROUP.OBJPROPERTY09 AS "~Compressor\
Station B",
CGROUP.GRPTYPE,
CGROUP.OBJTYPE,
CGROUP.GCHILD01,
CADVOUTSTATION.PARENTGROUPID
FROM
CGROUP JOIN CADVOUTSTATION ON CGROUP.GCHILD01 = CADVOUTSTATION.PARENTGROUPID
WHERE "_FullName" LIKE 'Region1.%'
ORDER BY
"~Meter\
Number" ASC


I suspect the answer is 0 (zero)... hence why your query including the WHERE clause returns no rows.


Reply From User: hardin4019, posted: 2019-07-15 12:45:22
Approximately 130 rows.


Reply From User: hardin4019, posted: 2019-07-15 16:30:33
Found a working solution.

I was able to go in and add my own Metadata field to the CGroup table that is linked to the Modbus Outstation and add the new column to my query without issue. Pick Actions work and return the correct Pick Action menu for the Outstation.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore