Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

[Imported] CS 2017 R3 WebX trends are not displayed

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] CS 2017 R3 WebX trends are not displayed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
337
AndrewScott
AndrewScott
128
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-07 03:39 AM . Last Modified: ‎2023-05-03 12:23 AM

0 Likes
1
1429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 03:39 AM . Last Modified: ‎2023-05-03 12:23 AM

[Imported] CS 2017 R3 WebX trends are not displayed

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: Alexey, originally posted: 2019-07-02 08:17:28 Id:462
Good day.
When attempting to display trends through WebX using the configured Trend, the following fact was detected. When the sum of the number of characters in the full name of the signals exceeds a certain maximum number, the web page does not display the Trend component. Has anyone encountered a similar situation?

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-07 03:40 AM

0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 03:40 AM

>>Responses imported from previous forum


Reply From User: geoffpatton, posted: 2019-07-02 18:24:04
Well in 2017 R2 I could not replicate it. I could still get trends on a Trend object and from selecting Display Historic Trend from the object menu on a mimic.
There is a limit of 254 characters to a FullName and you can only have 15 objects deep. I had 14 folder groups and then the point, trend, and mimic were at the 15th level. The full name was 254 characters. Then I tried with 3 folder groups and named them 63 characters long which is the name character limit. The Point, Mimic and Trend names were limited to 62 characters to stay at 254 total. the Name actually includes the "." so its total size limit is 64 characters for the name of an object as long as it will not cause the FullName to exceed 254. Anyway I still had 254 characters and could see the trends.

2010 is really old now is probably a good time to upgrade.


Reply From User: Alexey, posted: 2019-07-03 06:41:25
Hello. I use R3 May 2019, but it was discovered on R2 July 2018. You are right about 254 characters in total. But I have a problem with the total number of all characters in all full names of the database items displayed on the Pre-Configured Trends. For example, full name 1 has 200 characters, full name 2 is 180 characters ... full name N 210, etc., when FN1 + FN2 + ... + FN (n) is greater than a certain number, WebX does not display Pre- Configured Trend, only a blank web page.
For example, I attached a working config (R3 May 2019). If you add a letter (for example, "A") or a digit to the name of any instance, WebX stops displaying Pre-Configured Trends.
WebX login: operator, psswd: 2222222222

P.S. I am forced to use the national alphabet in the name of the database elements, and in my case the maximum number of characters at which everything works less than when using the Latin alphabet

Attached file: (editor/ev/8fcut782z8xa.zip), test_cfg.zip File size: 6746


Reply From User: geoffpatton, posted: 2019-07-03 14:10:03
Ah your tag says ClearSCADA 2010 R3.1
I only tried the original WebX.
I suspect you are using the new WebX that has the HTML5 Trend display.
I currently don't have any version of 2017 with the new WebX setup on anything so I do not have a test environment.
Being that you are on the latest I would contact your local support and have them check into it. It honestly sounds like something the Developers will have to address.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-07 03:40 AM

0 Likes
0
1430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-07 03:40 AM

>>Responses imported from previous forum


Reply From User: geoffpatton, posted: 2019-07-02 18:24:04
Well in 2017 R2 I could not replicate it. I could still get trends on a Trend object and from selecting Display Historic Trend from the object menu on a mimic.
There is a limit of 254 characters to a FullName and you can only have 15 objects deep. I had 14 folder groups and then the point, trend, and mimic were at the 15th level. The full name was 254 characters. Then I tried with 3 folder groups and named them 63 characters long which is the name character limit. The Point, Mimic and Trend names were limited to 62 characters to stay at 254 total. the Name actually includes the "." so its total size limit is 64 characters for the name of an object as long as it will not cause the FullName to exceed 254. Anyway I still had 254 characters and could see the trends.

2010 is really old now is probably a good time to upgrade.


Reply From User: Alexey, posted: 2019-07-03 06:41:25
Hello. I use R3 May 2019, but it was discovered on R2 July 2018. You are right about 254 characters in total. But I have a problem with the total number of all characters in all full names of the database items displayed on the Pre-Configured Trends. For example, full name 1 has 200 characters, full name 2 is 180 characters ... full name N 210, etc., when FN1 + FN2 + ... + FN (n) is greater than a certain number, WebX does not display Pre- Configured Trend, only a blank web page.
For example, I attached a working config (R3 May 2019). If you add a letter (for example, "A") or a digit to the name of any instance, WebX stops displaying Pre-Configured Trends.
WebX login: operator, psswd: 2222222222

P.S. I am forced to use the national alphabet in the name of the database elements, and in my case the maximum number of characters at which everything works less than when using the Latin alphabet

Attached file: (editor/ev/8fcut782z8xa.zip), test_cfg.zip File size: 6746


Reply From User: geoffpatton, posted: 2019-07-03 14:10:03
Ah your tag says ClearSCADA 2010 R3.1
I only tried the original WebX.
I suspect you are using the new WebX that has the HTML5 Trend display.
I currently don't have any version of 2017 with the new WebX setup on anything so I do not have a test environment.
Being that you are on the latest I would contact your local support and have them check into it. It honestly sounds like something the Developers will have to address.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore