Geo SCADA: Alarm Acknowledge Using Pick Action VBScript Function

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

PicardEarlGrey
Crewman
Crewman

Geo SCADA: Alarm Acknowledge Using Pick Action VBScript Function

Hi everyone!

 

I want to accept alarms from an alarm list using a VBScript function. I am not able to get the "cookie" value when selecting the row

 

'Assume for this purpose that strAlarmSource is fullname

 

     strAlarmSource = Mimic.Layers(strLayerName).Item(strListName).CurrentRowSource 

     objAlarm = Server.FindObject(strAlarmSource)

     objAlarm.Interface.Accept

 

and then when using the method "objAlarm.Interface.Accept" it would accept all active alarms on that object. Is there any way to select a row in an alarm list and get a reference to the Alarm Instance and not the object or "Alarm Source".

 

Thank you in advance!

1 Reply 1
BevanWeiss
Spock
Spock
0 Likes
0
294

Re: Geo SCADA: Alarm Acknowledge Using Pick Action VBScript Function

I think it's a little complicated there.

  strAlarmSource = Mimic.Layers(strLayerName).Item(strListName).CurrentRowSource

  objAlarm = Server.FindObject(strAlarmSource)

  objAlarm.Interface.Accept

 

The objAlarm item there is really the Alarm Object (CAlarmObject)

2022-05-26 14_25_44-GeoSCADA Expert 2021 Win2016 - VMware Workstation.png

 

And hence the Accept will 'Acknowledges all alarms associated with the object'

 

So somewhat painfully, you'd ideally want to access the CAlarm itself instead of the Alarm Object.


Lead Control Systems Engineer for Alliance Automation (VIC).