Export-Import issue

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

Solved
Oz_Ba
Lieutenant JG
Lieutenant JG
0 Likes
2
995

Export-Import issue

Hi,

 

It is me again...

I am currently experiencing difficulties with Geo SCADA.

I am in the development process of SCADA app and I have experienced many issues so far.

One of the issues is regarding exporting and importing objects.

I created a Group containing 7 ICMP digital points in order to have information if certain ethernet devices are available on the network.

Since I am having difficulties with copy-paste operations I decided to try everything on another machine. So I performed export of all items from main project folder. Then I imported all items to another Geo SCADA machine. I noticed that no ICMP digital points were imported. There is group tree created as it should be, ICMP group as well, but no ICMP digital points within ICMP group where they should be.

 

Am I doing something wrong?

 

 

 

 


Accepted Solutions
AndrewScott
Commander
Commander

Re: Export-Import issue

What messages were displayed in ViewX when you imported the SDE file?

 

It sounds like the ICMP driver isn't installed on the second machine and so the ICMP objects is the SDE file couldn't be imported and so were discarded. If this is the case then there will be an error message for each object that couldn't be created.

 


Andrew Scott, Lead Engineer, AVEVA

See Answer In Context

2 Replies 2
AndrewScott
Commander
Commander

Re: Export-Import issue

What messages were displayed in ViewX when you imported the SDE file?

 

It sounds like the ICMP driver isn't installed on the second machine and so the ICMP objects is the SDE file couldn't be imported and so were discarded. If this is the case then there will be an error message for each object that couldn't be created.

 


Andrew Scott, Lead Engineer, AVEVA
Oz_Ba
Lieutenant JG
Lieutenant JG
0 Likes
0
975

Re: Export-Import issue

@AndrewScott 

Thanks.