Execute Control Method on Server Start?

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Execute Control Method on Server Start?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
308
AndrewScott
Admiral AndrewScott
98
BevanWeiss
Spock BevanWeiss
91
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
37
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
Praetoriate
Crewman Praetoriate
Crewman

Posted: ‎2025-04-23 10:48 AM

0 Likes
2
324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-23 10:48 AM

Execute Control Method on Server Start?

Hello All!
We want to reboot our SMS modem after the GeoSCADA (server) restarts. Currently able to do this on a modbus point with a button in ViewX, but would like to have some kind of automation in the server to 'push the button' automatically 30s after GeoSCADA starts on the server.
Is there a place to set 'on startup' methods?

Only other idea I have had is to write a little logic object that has a 30s timer against a count up trigger that only triggers the control method the once, but then there's a logic object executing all the time that wont ever do anything after the server starts?

Labels
  • Labels:
  • Logic
  • Redundancy
  • SCADA
  • Scripting
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2025-04-24 08:31 PM

0 Likes
1
294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 08:31 PM

I'd suggest avoiding anything like a 'timer' around this.  Just using the Server "Time Went Main" is probably the best.  Have a DateTime variable.  Then some server-side logic that checks if the "Time Went Main" doesn't equal your DateTime variable... in that event do some stuff, and set the DateTime variable to the new "Time Went Main"..

 

Have the ST run every minute.  It's a pretty quick check, so execution overhead is minimal.  Changing logic config (to minimise executions) will have significantly greater impact on overall DB performance, so avoid changing that...


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2025-04-24 08:31 PM

0 Likes
1
295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 08:31 PM

I'd suggest avoiding anything like a 'timer' around this.  Just using the Server "Time Went Main" is probably the best.  Have a DateTime variable.  Then some server-side logic that checks if the "Time Went Main" doesn't equal your DateTime variable... in that event do some stuff, and set the DateTime variable to the new "Time Went Main"..

 

Have the ST run every minute.  It's a pretty quick check, so execution overhead is minimal.  Changing logic config (to minimise executions) will have significantly greater impact on overall DB performance, so avoid changing that...


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Praetoriate
Crewman Praetoriate
Crewman

Posted: ‎2025-05-07 12:26 PM

In response to BevanWeiss
0 Likes
0
224
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-07 12:26 PM

Thank you! Got something similar setup and working.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of