ClearSCADA 2017R2 Configuration Auditing duration?

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Re: ClearSCADA 2017R2 Configuration Auditing duration?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-02-20 06:25 PM . Last Modified: ‎2023-05-03 12:17 AM

1 Like
3
2436
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-20 06:25 PM . Last Modified: ‎2023-05-03 12:17 AM

ClearSCADA 2017R2 Configuration Auditing duration?

I am assisting a client configure the auditing feature.  (Configuration Changes Auditing)

Could someone kindly explain what Keep Online for, Archive after and Future messages mean as a whole.

 

The Defaults are set to 4, 0 and 4 respectively.  Does it mean audit log entries are kept for 4 weeks in the database, then after 4 weeks written to file and kept on the file system for 4 weeks?

 

Also what is the file path (name) of the audit log, when written to the file system?

 

Sorry, its just not very clear to me.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-21 02:51 AM

2 Likes
1
2425
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-21 02:51 AM

@Anonymous user What did the help say about these fields?

 

You should go to the server and 

http://localhost/Help/#ServerAdministrationGuide/ConfigurationChangesAuditing.htm

 

That should look like the page you're talking about.

Then there are links at the bottom of the page that would take you here:

 

http://localhost/Help/#ServerAdministrationGuide/SpecifytheDurationtoRetainHistoricDataOnline.htm

Specify the Duration to Retain Historic Data Online

The Keep online for field in the ClearSCADA Server Configuration Tool's Historic settings allows you to specify the duration that Alarm Summary, Configuration Changes Auditing, Event Journal or Historic Data., is retained online. When this period of time expires, the historic data is deleted from the disk to allow space for the latest messages or data.

 

 

http://localhost/Help/#ServerAdministrationGuide/DefinetheArchiveTimeforData.htm

Alarm Summary, Configuration Changes Auditing, Event Journal or Historic Data is stored online for a specified duration (see Specify the Duration to Retain Historic Data Online), then the data is deleted. You can define a period of time after, which data that is stored online can be archived. When historic data is marked as eligible for archiving, it can be archived for example to CD, DVD and so on, (it has to be archived before the duration of the online data expires).

During the period that data is stored online, the data can be altered (by having new values reported for the time period) unless it is marked as eligible for archiving. When historic data is marked as eligible for archiving, it can no longer be altered on the disk—the new records for that period / time cannot be written to; it can only be read.

 

and here

http://localhost/Help/#ServerAdministrationGuide/DefinetheFutureDataTimeforHistoricData.htm

Specify the Future Data Time for Historic Data

You can use the ClearSCADA Server Configuration Tool to define the lifetime setting for future data. The future data lifetime setting defines the maximum amount of time in the future that is permitted for future data—any data that has a time stamp that is further in the future than the defined time is not stored historically. For example, if the current date is October 1st 2014 and the future data life is set to 1 week, any data that has a time stamp between October 2nd and October 7th will be stored historically. A message that has a time stamp beyond October 7th will be lost as the date of the future data is further in the future than the defined future data life.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-23 09:01 PM

In response to BevanWeiss
1 Like
0
2402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-23 09:01 PM

@Anonymous user 

I note I didn't respond to your last question:

Also what is the file path (name) of the audit log, when written to the file system?


That's not really how this works.  It stores the records as a set of files, none of which are externally readable.

You would use the Query Processor internal to ClearSCADA / Geo SCADA Expert to query the Configuration Change 'table' which would provide the Configuration Change results you want.

There is further information in the help, and within the schema related to this.

 

If these have answered your questions appropriate, please mark the earlier response as 'the solution' to make it easier for others to find.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Omaelk
Janeway Omaelk
Janeway

Posted: ‎2020-02-21 02:04 AM

0 Likes
0
2433
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-21 02:04 AM

Hey @Anonymous user  , thank you for your question
 
I moved it to this forum where the community of experts will be able to provide you the right support and solve your issue! 
 
PS: don't hesitate to check the Knowledge base and use the search bar with keywords. there is a lot of content discussed everyday and your issue may have already been solved 😉

Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-21 02:51 AM

2 Likes
1
2426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-21 02:51 AM

@Anonymous user What did the help say about these fields?

 

You should go to the server and 

http://localhost/Help/#ServerAdministrationGuide/ConfigurationChangesAuditing.htm

 

That should look like the page you're talking about.

Then there are links at the bottom of the page that would take you here:

 

http://localhost/Help/#ServerAdministrationGuide/SpecifytheDurationtoRetainHistoricDataOnline.htm

Specify the Duration to Retain Historic Data Online

The Keep online for field in the ClearSCADA Server Configuration Tool's Historic settings allows you to specify the duration that Alarm Summary, Configuration Changes Auditing, Event Journal or Historic Data., is retained online. When this period of time expires, the historic data is deleted from the disk to allow space for the latest messages or data.

 

 

http://localhost/Help/#ServerAdministrationGuide/DefinetheArchiveTimeforData.htm

Alarm Summary, Configuration Changes Auditing, Event Journal or Historic Data is stored online for a specified duration (see Specify the Duration to Retain Historic Data Online), then the data is deleted. You can define a period of time after, which data that is stored online can be archived. When historic data is marked as eligible for archiving, it can be archived for example to CD, DVD and so on, (it has to be archived before the duration of the online data expires).

During the period that data is stored online, the data can be altered (by having new values reported for the time period) unless it is marked as eligible for archiving. When historic data is marked as eligible for archiving, it can no longer be altered on the disk—the new records for that period / time cannot be written to; it can only be read.

 

and here

http://localhost/Help/#ServerAdministrationGuide/DefinetheFutureDataTimeforHistoricData.htm

Specify the Future Data Time for Historic Data

You can use the ClearSCADA Server Configuration Tool to define the lifetime setting for future data. The future data lifetime setting defines the maximum amount of time in the future that is permitted for future data—any data that has a time stamp that is further in the future than the defined time is not stored historically. For example, if the current date is October 1st 2014 and the future data life is set to 1 week, any data that has a time stamp between October 2nd and October 7th will be stored historically. A message that has a time stamp beyond October 7th will be lost as the date of the future data is further in the future than the defined future data life.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-23 09:01 PM

In response to BevanWeiss
1 Like
0
2403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-23 09:01 PM

@Anonymous user 

I note I didn't respond to your last question:

Also what is the file path (name) of the audit log, when written to the file system?


That's not really how this works.  It stores the records as a set of files, none of which are externally readable.

You would use the Query Processor internal to ClearSCADA / Geo SCADA Expert to query the Configuration Change 'table' which would provide the Configuration Change results you want.

There is further information in the help, and within the schema related to this.

 

If these have answered your questions appropriate, please mark the earlier response as 'the solution' to make it easier for others to find.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore