Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Siemens Fetch & Write

Digital Twin

This knowledge base is addressing usage of software Experior, Machine Expert Twin and future Automation Expert Twin. These softwares are used to create smaller instances of digital twins for use in industrial automation, warehouse management, design & engineering with more..

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Digital Twin
  • Siemens Fetch & Write
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Kasper.Vestrup
    Kasper.Vestrup

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Digital Twin
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
227 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Siemens Fetch & Write

Kasper.Vestrup Explorer
‎2026-01-09 01:46 AM

The following section shows how to use the Siemens Fetch and Write protocol to program and run the basic psychics model example.

 

  • Click on the Communications tab on the right of the Experior window, just below the Catalogs tab
  • Now right click on the first line and select Siemens and then click Fetch

Basic32.png

 

  • Next, on the second line down, do the same again only this time select Write

Basic33.png

 

  • Now it is time to configure the two communications devices
  • Select the Fetch device first and fill out the Properties like so

Basic34.png

 

  • Next select the Write device and configure the Properties like so

Basic35.png

 

  • Now to setup the I/O for the devices that require it. For the moment just the addresses will be used
  • The I/O is laid out below along with the associated items:
INPUTS
1.1	Motor Control “Switch”
1.2	Feed Load “Button” & Feed Load “Sensor” (2nd Sensor in system)
1.3	Load In System “Sensor” (1st Sensor in system)
OUTPUTS
1.1	Motor Drive Control
1.2	Feeder “Feed Load” Control
1.3	Load In System “Lamp”
  • Let’s set up the Inputs first
  • Select the switch called Motor Control in the Control Panel
  • In the Properties panel, below PLC Input expand the properties by clicking the arrow to the left of where it says On/Off 
Basic36.png

 

  • Enter the Byte No. as 1 and the Bit No. as 1
  • Now select the push button Feed Load
  • In the Properties scroll down to PLC Input and expand the section by clicking the arrow to the left of where it says Pushed
Basic37.png

 

  • Enter the Byte No. as 1 and the Bit No. as 2
  • Now select the second sensor that was added to the model earlier
  • In the Properties scroll down to PLC Input and expand the section by clicking the arrow to the left of where it says Blocked

Basic38.png

 

  • Enter the Byte No. as 1 and the Bit No. as 2
  • Now select the first sensor that was added to the model
  • As before scroll down to PLC Input in the Properties and expand the section called Blocked by clicking on the arrow

Basic39.png

 

  • Enter the Byte No. as 1 and the Bit No. as 3
  • Now, if the Inputs tab at the bottom of the screen is selected, the list of the inputs in the model can be viewed

Basic40.png

 

  • Now to add the Outputs to the system
  • Select the Motor by clicking any of the red arrows in the model
  • In the Properties scroll down to where it says Operations and expand the section for Forward (Output) by clicking on the arrow to the left of it

Basic41.png

 

  • Enter the Byte No. as 1 and the Bit No. As 1
  • Now select the Feeder, that is the triangle/arrow located on the first straight that was added to the model
  • Scroll down the Properties to the section PLC Output and expand the section for Feed by clicking on the arrow to the left of it

Basic42.png

 

  • Enter the Byte No. as 1 and the Bit No. As 2
  • Lastly select the Lamp in the Control Panel
  • In the Properties scroll down to PLC Output and expand the properties under Lighting by clicking the arrow to the left of it

Basic43.png

 

  • Enter the Byte No. as 1 and the Bit No. As 3
  • Now if the Outputs tab at the bottom of the screen is selected the list of the outputs in the model can be viewed

Basic44.png

 

Labels (2)
Labels:
  • Exp-6 PLC
  • Experior 6

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore