Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

CIP browseable protocol

Digital Twin

This knowledge base is addressing usage of software Experior, Machine Expert Twin and future Automation Expert Twin. These softwares are used to create smaller instances of digital twins for use in industrial automation, warehouse management, design & engineering with more..

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Digital Twin
  • CIP browseable protocol
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Kasper.Vestrup
    Kasper.Vestrup

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Digital Twin
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
99 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

CIP browseable protocol

Kasper.Vestrup Explorer
‎2026-01-05 02:03 AM

There are two Connection types that utilize the CIP protocol. The Ethernet/IP – CIP connection and the Ethernet/IP – CIP Browsable. The former is made for performance and the latter is made for flexibility and is the subject of this article.

 

The connection is browsable, this means that it will scan for variables on the PLC and display them to the user. This contrasts with non-browsable connection that rely on the user to type in the correct address for each Input and Output.

 

Setting up the connection

 

First the connection needs to be created, then it must be configured. This includes settings the PLC type, the Rack Number, Slot number and the IP address of the PLC that the connection needs to communicate with:

 CIP-Properties.png

 

Next step is to connect to the PLC. Right click the connection in the Connections window and click Connect:

 

The connection will request a variable list as soon as it connects with the PLC. Once the connection has the variable list it’s ready to be used. Please note that the variable list will only be available while the connection to the PLC is maintained.

CIP-connection.png

 

Using the connection

 

The next step is to use the connection. This can be done by adding a button to the control panel. To do this select a square in the Control panel grid, right click and select a Button from the context menu:

CIP-Control-panel.png
 
Select the newly created button and expand the Pushed entry in the Properties window. Make sure that the connection ID property is the Browsable CIP Connection that was created earlier:
Connected-CIP-properties.png

 

This will add the variable list. Locate a variable in that is of the BOOL type and check the checkbox. The Pushed Output of the button is now linked to the selected variable. If the button is pressed then the value of the variable in the PLC will be true, otherwise if will be false. 

Pushed-Output.png

 

Labels (2)
Labels:
  • Exp-7 Communication Protocols
  • Experior 7

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore