Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 145
    • 146
    • 147
    • …
    • 508
  • Next »

SPP920 Datasheet, Technical Information and Installation Instructions

Issue SPP920 Datasheet, Technical Information and Installation Instructions Product Line Field Device Environment SPP920 Differential Pressure Switch Cause No information available for the SPP920. The Sensor catalogue says it is supported by Huba. Resolution Either click link www.hubacontrol.com and search for 630. or the Technical information can be downloaded here. Installation Instructions can be downloaded here. Mechanical connections are: P1 = High Pressure (discharge/flow), P2 = Low Pressure (suction/vacuum) All of the various pressure range options come with the following options: - EPDM diaphram material - Brass Case - Spec Cover PG9 - IP65 Rating - Bracket Type A
View full article
Picard Product_Support
‎2018-09-10 10:48 PM

Labels:
  • Field Devices
9020 Views

Micronet LON (MNL) controller digital output (DO) turns off when the LON communications to the UNC / ENC fails

Issue Micronet LON (MNL) controller digital output turns off when the LON communications to the UNC / ENC fails. Programming a MNL controller so that the digital output will not turn off when the LON communications fail. Environment I/A Series R2 / G3 LonWorks integration I/A Series Micronet LON (MNL) controllers Cause LON input SNVT is used in the MNL controllers to bind to a command in an UNC / ENC. When the LON communications between the UNC / ENC and MNL fails, the SNVT in the MNL controller will default to the value 'NA'. The digital output (Binary Output object in WorkPlace Tech) turns off because it has received a 'NA' value. Resolution The programming logic in WorkPlace Tech for the MNL controller needs to have this factored in so that the digital output will not turn off when the LON communications fail. You can view an example of one such logic here. This has been created for an UNC LON integration to a MNL-800. The last command from the UNC will hold until the LON communications recover.
View full article
Picard Product_Support
‎2018-09-10 10:05 PM

Labels:
  • TAC IA Series
1189 Views

Using either Card or KeyPAD PIN to gain access through door

Notice NOTICE COMPLEX PROCEDURE REQUIRED. The resolution of this article has many complex steps that may result in unforeseen results if not performed correctly. If you are at all unfamiliar with the requirements, please contact Product Support for assistance. Issue Want to access door with 'Card only' or 'PIN only' not both of them.   Product Line TAC INET Environment I/NET Seven Access Cause I/NET has two door mode schedules, Secure, the default setting, which provides access via card number or Secure with PIN, which requires card entry AND a PIN entry.   In this case it is possible to use either card or PIN to gain access if using specialized readers that support a Wiegand PIN output. Resolution It is possible to achieve this provided the PIN output from your card reader supports one of the supported card types of I/NET (i.e. 26-bit, 32-bit Wiegand etc) you can assign a "card number" (PIN) for each individual. The PIN pad will output the entered PIN in Wiegand format and I/NET will then treat it as a normal card entry. Once the PIN pad / card reader has been configured you simply enter this into the Individual editor as the card number card and it acts exactly the same as swiping a card. What this means is that the Individual can use either their card or PIN to gain access (if entered in this fashion). So provided you have a suitable reader / pin pad (such as the P-640 Patagonia Proximity Reader from Keypad Farpointe Data, Inc (www.farpointedata.com))- here are the steps to configure this to work: In the Door editor set the reader type to Wiegand 26-bit (or other) Configure the PIN Type to 26-bit The Door mode is either left blank (Secure mode) or configured as 'Secure' Configure your Tenant (Refer to note below regarding Large Card number usage) Add your individual; The individual will have to have two card numbers associated to them: The number associated to the card, The number associated with the PIN number - what not to get confused with is that this PIN number is NOT the PIN number associated (or shown) in the Individual editor. Large Card number usage: How to calculate the "card number" if using Large Card Numbers: The following two Excel spreadsheet calculators; 26-bit and 32-bit can be used calculate you the large card number. Enter the details (Facility Code / Card number) and the calculator produces the large card number in both decimal and hexadecimal. For example if you use Facility Code 26 and card number 255, the results would be 1704191 (Decimal) and 001A00FF (Hexadecimal). Alternatively I/NET also displays this 'large card' number in the Message column if added to the Transaction window - you can use this also to ensure you have everything wired and configured correctly. How to calculate the "card number" if using the Facility Code / Card number: Once the reader has been programmed with the facility code and this number entered into the Tenant Code of the Tenant editor. The PIN number assigned to the individual then becomes the 'card number’. So for the same example used above, the Facility Code used is 26 and card number 255, the Tenant editor will have the Tenant code configured as 26 and the Individual number (ID) of 255 is used - so no card number is entered into I/NET. This ties the card number to the Individual ID. This is important and the major difference between using large card numbers and facility codes.
View full article
Picard Product_Support
‎2018-09-10 11:31 PM

Labels:
  • TAC INET
1925 Views

What is the replacement sensor for a Satchwell DR2252?

Issue Replacing a Satchwell DR2252 sensor. Environment DR2252 Sensor Detector Replacement Cause The Satchwell DR2252 sensor is obsolete, and there is not a direct replacement. Resolution The Satchwell DR2252 sensor is obsolete and the nearest replacement is the Schneider Electric STR614, but this is not a direct replacement. The DR2252 sensor had a sensing element with a resistance of 1690 ohms at 20'C, and a concealed 10/35'C adjustable scale. The Schneider Electric STR614 sensor has a sensing element with a resistance of 1690 ohms at 20'C, it does not have a concealed adjustment scale. For the Schneider Electric STR600 series of sensors, please click HERE.
View full article
Picard Product_Support
‎2018-09-10 11:58 PM

Labels:
  • Field Devices
1138 Views

What are the pulse input ratings for a Niagara G3 Jace-6?

Issue What are the pulse input ratings for a Niagara G3 Jace-6? Environment Niagara G3 Cause Job site has pulse meters which require termination to the Jace-6. Resolution The universal inputs support both pulse contacts and normal dry (equipment status) contacts. Pulse contacts may have a change-of-state (COS) frequency of up to 20 Hz with a 50% duty cycle.  Note: Minimum dwell time must be > 25ms. (Contacts must remain open at least 25ms and be closed at least 25ms.) Standard dry contacts must have a 1 Hz. (or less) COS frequency, with minimum dwell time > 500ms. (Contacts must remain open at least 500ms and be closed at least 500ms.) Both types of dry contacts support 3.3 Vdc open circuits or 330 μA short-circuit current. Click here for more information.
View full article
Picard Product_Support
‎2018-09-10 11:51 PM

Labels:
  • TAC IA Series
2987 Views

Can the S-x96-PSU replace a PSU card in a UNC196 or 296 Controller with separate communication and processor cards?

Issue Can the S-x96-PSU replace a PSU card in a UNC196 or 296 Controller with separate communication and processor cards? Environment BAS Sigma S-x96-PSU V53 196 296 UNC196 UNC296 Cause Can the S-x96-PSU replace a PSU card in a UNC196 or 296 Controller with separate communication and processor cards? Resolution The S-x96-PSU can only be used with V53 type processor boards in BAS. Download the PIB here. For BAS2800+, the separate comms and processor boards will need to be replaced with the V53 version. ****Note 1: For BAS2800+ V53 processor boards are only available till stocks are exhausted, and the upgrade path is to Sigma**** ****Note 2: For BAS2000 and BAS2800, the upgrade path is to Sigma****
View full article
Picard Product_Support
‎2018-09-10 11:50 PM

Labels:
  • Satchwell BAS & Sigma
1407 Views

Unable to learn on 3rd party device

Issue After receiving the CyberStations Who Is broadcast  via the BCX4040 the third party device responds with an I Am packet.  However, the BCX is not passing the information back to Cyberstation.  Product Line Andover Continuum Environment Cyberstation BACnet Who is I Am 3rd Party Find Bacnet device Learn Cause In the attached mstp capture images, neither of the responses from the Automated Logic device at packets 1713 and 5379 have the necessary information that would cause the bCX or any BACnet router to send the message to another network. 3rd Party device responds with an I Am Looking at the NPDU layer of either message, you’ll notice a destination network (DNET) is not indicated. If you compare these messages with those from the b3 (at packet 1716 or 5382), you’ll see a DNET of 1 indicated, which is why the I-Am’s from the b3 reach Cyber, as Cyber belongs to Network 1. BACnet end devices are expected to dynamically detect the presence of SNET/SADDR information in the NPDU and reply with a message that includes the matching values for the DNET/DADDR. b3 responds with an I Am In the preceding Who-is packets you can see that the network number has been communicated to the third party device Resolution BACnet routers or BACnet Building Controllers do not cache or otherwise correlate requests and responses. BACnet end devices are expected to dynamically detect the presence of SNET/SADDR information in the NPDU and reply with a message that includes the matching values for the DNET/DADDR. The role of the BACnet router is to remove the DNET/DADDR information and add the SNET/SADDR information when they route messages from one network to another.  
View full article
Picard Product_Support
‎2018-09-10 11:24 PM

Labels:
  • Andover Continuum
1651 Views

Replacement for valve V392

Issue Since the V392 is no longer available, a replacement valve is requested. Environment V392 Forta Cause Replacing old V392 valve. Resolution No direct replacement is available. Closest in application should be V311T with a Forta actuator, but it will require pipe work to fit.  To review the V392 data sheet, please click HERE.
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • Field Devices
1289 Views

IOUs going offline intermittently - estimating the power consumed from IOU modules

Issue There is a need to be able to calculate and estimate the amount of power being consumed by IOU modules and their readers Environment 99xx 9680 IOUs Cause Power supplies have a wattage limit and adding to many modules can cause the bus to become unstable Resolution To estimate the amount of wattage being consumed by IOU modules, please download the following Excel Spreadsheet. Continuum I/O Module Power
View full article
Picard Product_Support
‎2018-09-10 11:17 PM

Labels:
  • Andover Continuum
1048 Views

Is it possible to create a TGML slideshow in TAC Vista Workstation?

Issue Is it possible to create a TGML slideshow in TAC Vista Workstation? Environment TAC Vista 5.1.7 Cause Some customer would like to have a dashboard that cycles through different TGML graphics - perhaps on a large flat-screen TV. Resolution Whilst we don't have this functionality built in to workstation, it is possible to utilise layers in TGML editor to create the effect of a slide show. When creating complex graphics, it can be a challenge to keep track of all the graphic figures in the work area. Graphic figures get hidden under one another and selecting becomes difficult. Layers provide a way to manage the graphic figures that make up your graphic. Layers can be regarded as folders that contain graphic figures. Layers are not supported in static TGML viewer in TAC Vista Webstation or in the TGML Viewer in TAC Xenta 500/700 Series.  Download the example graphic here.
View full article
Picard Product_Support
‎2018-09-10 11:14 PM

Labels:
  • TAC Vista
1491 Views

In Niagara G3, the SNMP driver reference manual refers to three MIB files required so that the SNMP Point Manager can "discover" and "add" SNMP points as need...

Issue In Niagara G3, the SNMP driver reference manual refers to three MIB files required so that the SNMP Point Manager can "discover" and "add" SNMP points as needed.  The filenames are: TridiumR3-MIB.my RFC1155-SMI.mib RFC1213-MIB.mib Where can they be found? Environment Niagara G3 Cause The three files are not easily located. Resolution The TridiumR3-MIB.my file is installed with the version of Niagara G3 installed on the host computer. The other two files (RFC1155-SMI.mib & RFC1213-MIB.mib) can be found on the World Wide Web by searching using their specific filenames. All three files are available here:  SNMP_Files_for_G3
View full article
Picard Product_Support
‎2018-09-10 11:13 PM

Labels:
  • TAC IA Series
1686 Views

What are the jumpers labeled TERM3 through TERM6 used for on the I/A Series R2 UNC-520 and G3 ENC-520?

Issue What are the jumpers labeled TERM3 through TERM6 used for on the I/A Series R2 UNC-520 and G3 ENC-520? Environment I/A Series R2 UNC-520 I/A Series G3 ENC-520 Cause Hardware communications bus bias resistor pairs. Resolution The UNC-520-2 and ENC-520-2 hardware circuitry includes a set of bias resistors that can be individually enabled as pairs, one set for each of the four RS-485 ports. These jumpers change the default bias resistor set for each RS-485 COM port from a device level bias to a “pull-apart” level bias. These are NOT end-of-line terminators. In most cases, the bias resistors should remain enabled. Reference technical bulletin (TB06-09) for more details.
View full article
Picard Product_Support
‎2018-09-10 11:11 PM

Labels:
  • TAC IA Series
1347 Views

Is it possible to upgrade Vista's log database directly from SQL 2000 to SQL 2008?

Issue Is it possible to upgrade Vista's log database directly from SQL 2000 to SQL 2008? Version 5.1.7 no longer supports SQL MSDE or SQL server 2000. Environment Upgrade to Vista 5.1.7 from a vista version running with SQL 2000. Cause Upgrading older Vista sites to run with Vista 5.1.7 (or future versions). Resolution The simple answer is yes, it is possible to upgrade from SQL server 2000 but SQL server 2000 SP4 needs to be installed first. Follow the link below to go to Microsoft's download site: SQL 2000 SP4 There are a number of considerations which are explained in the attached White Paper from Microsoft.
View full article
Picard Product_Support
‎2018-09-10 11:16 PM

Labels:
  • TAC Vista
4726 Views

How do you stop the A for alarm from being displayed on the CMC/CSMC.

Issue A displayed on main display. Environment CMC CSMC A Alarm Cause Showing A for alarm on the display Resolution Set code B61 to 1 Click here to download the data sheets.
View full article
Picard Product_Support
‎2018-09-10 11:17 PM

Labels:
  • Field Devices
908 Views

I/A Series R2 and G3 MIB files

Issue I/A Series R2 and G3 MIB files Environment I/A Series R2 SNMP integration I/A Series G3 SNMP integration Cause A Management Information Base (MIB) describes a database of objects that can be monitored by a network management system. SNMP uses standardized MIB formats that allow any SNMP tool to monitor any device defined by a MIB. The Tridium MIB defines the information that can be exposed for a I/A Series Niagara station running the SnmpService. The third party system is having trouble reading the SNMP traps from I/A Series using the MIB file that was sent to them. Resolution Ensure that the correct MIB file is used. Starting in I/A Series R2 version 2.301.528 and above, a new TridiumR2-MIB was created that is supported by R2 Snmp stations. This was created because of the need to differentiate Tridium MIB object identifiers between R2 and G3. I/A Series G3 versions 3.4 and earlier uses TridiumR3-MIB.my MIB file. To view this file in WorkBench, go to 'File' > 'Open' > 'Open Ord' (or shortcut Ctrl + L) and key in 'local:|module://snmp/tridiumMib/TridiumR3-MIB.my'. Starting from I/A Series G3 versions 3.5 and above, there is a Workbench function (right-click menu on the local SNMP device) to create a MIB. See 'About locally generated MIBs' on page 3-17 to 3-21 of the Niagara Ax 3.5 SNMP Driver Guide.
View full article
Picard Product_Support
‎2018-09-06 12:24 PM

Labels:
  • TAC IA Series
1503 Views

Which SQL query can be used to identify the database layout being used?

Issue Which SQL query can be used to identify the database layout being used? Environment Vista 5.1.X log database Cause With the release of Vista 5.1.7 came a new logdatabase layout which is designed to improve performance especially in the area of trend and event log management. This means that there are now 2 possible logdatabase configurations. It can be important to know which version is being used before running any queries or accessing the external log data with external tools. Resolution The following query will return the database layout version when run in SQL management studio: select taclogdata.dbo.DSS_SchemaVersion() More information can be found in the Vista 5.1.7 release notes.
View full article
Picard Product_Support
‎2018-09-06 12:22 PM

Labels:
  • TAC Vista
5484 Views

How to uninstall Internet Explorer 9

Issue Internet Explorer 9 not supported Environment Internet Explorer 9 IE9 IE 9 webClient Continuum webClient Cause Internet Explorer 9 ( IE 9) is not supported in webClient 1.94 Resolution Please click HERE to see attachment for details on uninstalling Internet Explorer 9 This procedure will remove IE 9 and IE 8 will be available on the machine.
View full article
Picard Product_Support
‎2018-09-10 07:48 AM

Labels:
  • Andover Continuum
1228 Views

In a Door object, the tick box "Relock upon Door Closure" is greyed out on the Channels tab. Is it possible to activate this feature?

Issue "Relock upon Door Closure" option is greyed out and feature is not available.  Environment Continuum Access Control Cause The "Relock upon Door Closure" feature is not implemented at this time.  Resolution For this "Relock upon Door Closure" functionality you will need to use Plain English code. The code located here is a sample of how this can be accomplished.
View full article
Picard Product_Support
‎2018-09-10 11:42 AM

Labels:
  • Andover Continuum
1255 Views

Is the I/A Series product line compliant with federal regulations on being "American-made"? Is there documentation to support it?

Issue Is the I/A Series product line compliant with federal regulations on being "American-made"?  Is there documentation to support it?  This must include the MNB and MNL controllers, the Niagara UNC and ENC models, and field devices like valves, actuators, and sensors.  Environment I/A Series Cause Government buildings specification Resolution The "schedule" links below provide a list of all products in the I/A Series line that are American-made.  The third link provides a signed statement of declaration. Schedule A Schedule B Declaration
View full article
Picard Product_Support
‎2018-09-06 03:29 PM

Labels:
  • TAC IA Series
3007 Views

How does the dynamic updates property work in TGML?

Issue How does the dynamic updates property work in TGML? Product Line TAC Vista Environment TAC Vista 5.1.7 TGML graphics. Cause A graphic can contain numerous bindings to values that you want to be able to display in the graphic. When there are numerous bindings, reading the values can be time-consuming and can slow down the performance of the graphic. By setting the DynamicUpdates attributes in the Bind elements of the graphic to either disabled or enabled, you can control which values are updated (which values the graphic subscribes to) when the graphic is opened. Resolution Created a Bind object in the TGML Graphic Editor Look at the Properties for the object. Under Behavior, the property DynamicUpdates is set to Enable by default. This can be set to Disabled and a Script can be added in an appropriate object which follows the following format: Example - activate a binding by clicking on a button function Click(evt){ button = evt.getTarget(); //Identify the target that has been clicked. parent = button.getParentNode(); //Find the parent node. binding = parent.getChildRecursive(""); //Identify the binding to be activated. binding.setAttribute("DynamicUpdates","Enable"); //Activate the DynamicUpdate property. } A simple example is attached. Click to download DynamicUpdate.zip.
View full article
Picard Product_Support
‎2018-09-10 11:41 AM

Labels:
  • TAC Vista
2256 Views
  • « Previous
    • 1
    • …
    • 145
    • 146
    • 147
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of