Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Building Automation Knowledge Base

Access this self-service resource 24/7 and post your questions or scroll through forums for answers on building automation.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,192
  • TAC Vista 2,049
  • TAC IA Series 1,805
  • EcoStruxure Building Operation 1,715
  • TAC INET 1,461
  • Field Devices 712
  • Satchwell BAS & Sigma 475
  • EcoStruxure Security Expert 284
  • Satchwell MicroNet 254
  • EcoStruxure Building Expert 227
  • EcoStruxure Access Expert 124
  • CCTV 53
  • Project Configuration Tool 30
  • EcoStruxure Building Advisor 7
  • Automated Engineering Tool 4
  • EcoStruxure Workplace Advisor 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
3

Related Forums

  • Field Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1805 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 91
  • Next »
Label: "TAC IA Series" Show all articles

On a Niagara G3 server, the station fails to run with an out of memory error.

Issue A Niagara G3 server station was running well for a long time.  Then in a matter of a couple of days, the station began failing to run.  The error listed in the Application Director Output is:   ERROR [java.lang.OutOfMemoryError: GC overhead limit exceeded 13:46:17 20-Mar-14 EDTjava.lang.OutOfMemoryError: GC overhead limit exceeded][sys.leasejava.lang.OutOfMemoryError: GC overhead limit exceeded] Error in run Product Line TAC IA Series Environment I/A Series G3 Enterprise Server Cause There is not enough memory allocated to the Java Virtual Machine (JVM). The email service is keeping a very large outbox because the network email server's IP address was changed. Resolution Increase the Java Virtual Machine (JVM) memory allocation Using a text editor, open the nre.properties file (located in the niagara 'lib' subfolder on the server hard drive). Locate the line: java.options=-Xmx256M. Change it to java.options=-Xmx512M. Empty the outbox file (i.e. delete it) and/or update the email server's IP address.
View full article
Picard Product_Support
‎2018-09-06 09:42 AM

Last Updated: Administrator CraigEl Administrator ‎2023-03-15 06:10 PM

Labels:
  • TAC IA Series
1518 Views

Niagara Station Error Transfer failed. com.tridium.platform.daemon.DaemonResponseException:

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue If the passphrase is incorrect when trying to install a station .bog, the following error message can appear; Transfer failed. com.tridium.platform.daemon.DaemonResponseException: Request to platform daemon at (stationName) failed: bad return code to commit file instance at com.tridium.platform.daemon.DaemonFileUtil.transfer(DaemonFileUtil.java:661) at com.tridium.install.InstallScenario.commit(InstallScenario.java:1444) at com.tridium.platDaemon.ui.stationtransfer.FinalStep.run(FinalStep.java:341) at java.lang.Thread.run(Thread.java:750) Product Line TAC IA Series Environment I/A Series N4 Enterprise Server I/A Series N4 Jace Cause The .bog has not been properly placed in the User Home / Stations for copying into the device or the passphrase is not known. Resolution Always use the Station Copier to install the .bog from the User Home / Stations path If the error message appears, open Workbench and navigate to the "Stations" folder under the "User Home" Expand the station you are attempting to install Double-click the .bog (1) and locate the "Bog File Protection" icon at the top of the page (2) Select the (1) "Force the File to start..." radio button and (2) Update.  Note the information regarding existing passwords. If the message "Cannot display page" occurs when you double click the .bog, open the "Details" and look for missing modules "Cannot load module '......=.....'. Any missing modules will need to be available on the Jace or ES before attempting the force start operation.  
View full article
Spock RandyDavis Spock
‎2023-03-14 01:09 PM

on ‎2023-03-14 01:09 PM

Labels:
  • TAC IA Series
176 Views

WorkPlace Tech 5.8.x, 5.9.x, and 5.10.x Operating System and Microsoft Visio Compatibility

Issue WorkPlace Tech 5.8.x, 5.9.x, and 5.10x Operating System and Microsoft Visio Compatibility Product Line TAC IA Series Environment WorkPlace Tech Tool Software release 5.8.x, 5.9.x, and 5.10x Microsoft Windows and Microsoft Office Visio requirements, see the "Resolution" section, below. Visio 2010, 2013, 2016, 2019, 2021(.msi install)  Visio 2013, 2016, 2019, 2021 (subscription "Click to Run", Plan 2) Office 2010, 2013, 2016 (.msi install) Office 2013, 2016, 365 (subscription "Click to Run", Plan 2) Support for Workplace Tech 5.10 / previous and Workplace Tech Editor Note: Visio 2019 and Visio 2021 are not supported in 5.9.4 or EBO versions before EBO 2022.  Visio 2019 and Visio 2021 are supported when using Workplace Tech 5.10.x and EBO 2022. Cause What Microsoft Windows operating systems and what versions of Microsoft Visio are compatible with the WorkPlace Tech Tool version 5.8.x, 5.9.x, and 5.10.x? Resolution Microsoft Windows WorkPlace Tech Tool releases 5.8 through 5.8.6 are certified to run on the following versions of Microsoft Windows: Microsoft Windows XP Professional with Service Pack 2 or Service Pack 3 Microsoft Windows Vista 32-bit Business, Ultimate or Enterprise Microsoft Windows 7 32-bit Professional Microsoft Windows 7 64-bit Professional WorkPlace Tech Tool release 5.8.7 is certified to run on the following versions of Microsoft Windows: Microsoft Windows 7 32-bit Professional Microsoft Windows 7 64-bit Professional Microsoft Windows 8.1 32-bit Pro or Enterprise Microsoft Windows 8.1 64-bit Pro or Enterprise Microsoft Windows Server 2012 64-bit WorkPlace Tech Tool releases 5.9.1 to 5.9.4 are certified to run on the following versions of Microsoft Windows: Microsoft Windows 7   32-bit Professional Microsoft Windows 7   64-bit Professional Microsoft Windows 8.1   32-bit Pro or Enterprise Microsoft Windows 8.1   64-bit Pro or Enterprise Microsoft Windows 10    32-bit Professional Microsoft Windows 10    64-bit Professional Microsoft Windows Server 2012   64-bit WorkPlace Tech Tool release 5.10.0 to 5.10.x is certified to run on the same as WorkPlace Tech 5.9.x and the following versions of Microsoft Windows: Microsoft Windows Server 2016 64-bit Microsoft Windows Server 2019 64-bit Microsoft Windows Server 2022 64-bit Microsoft Visio Microsoft Windows 7 32-bit Professional Microsoft Windows 7 64-bit Professional Microsoft Windows 8 32-bit Pro or Enterprise Microsoft Windows 8 64-bit Pro or Enterprise Microsoft Windows 8.1 32-bit Pro or Enterprise Microsoft Windows 8.1 64-bit Pro or Enterprise Microsoft Windows Server 2012 64-bit WorkPlace Tech Tool releases 5.8 through 5.8.6 require one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2003 with Service Pack 3 (officially supported for WPT 5.8.0, WPT 5.8.1, no known issues with WPT 5.8.2 through 5.8.5) Microsoft Office Visio 2007 with Service Pack 1 or Service Pack 2 Microsoft Office Visio 2010 with or without Service Pack 1 NOTE: Standard or Professional edition of Microsoft Visio may be used. WorkPlace Tech Tool release 5.8.7 requires one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2007 with Service Pack 3 Microsoft Office Visio 2010 with Service Pack 2 NOTE: Standard or Professional edition of Microsoft Visio may be used. WorkPlace Tech Tool release 5.9.1 through 5.9.4 requires one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2010 with Service Pack 2 Microsoft Office Visio 2013 with Service Pack 1 Microsoft Office Visio 2016 NOTE: Standard or Professional edition of Microsoft Visio may be used. WorkPlace Tech Tool releases 5.10.0 through 5.10.x requires one of the following versions of Microsoft Visio (32-bit version ONLY) Microsoft Office Visio 2016 Microsoft Office Visio 2019 Microsoft Office Visio 2021 Microsoft Office Visio Office 365 Subscription Plans 2 Note: Workplace Tech Tool 5.10.0 and future releases will require .NET Framework 4.8 to support Open LDV 5.1 which is included in the installer.  .NET Framework 3.5 Sp1 is no longer required.   Follow the instructions in the article link for the security updates required. Workplace Tech 5.10.x and previous / Workplace Tech Editor (EBO) Microsoft Security Updates required for Visio and Office For the Visio requirements for earlier versions of the WorkPlace Tech Tool software, see What versions of Visio are required for WorkPlace Tech?.
View full article
Picard Product_Support
‎2020-12-15 10:46 AM

Last Updated: Spock RandyDavis Spock ‎2023-03-09 08:02 AM

Labels:
  • TAC IA Series
9047 Views

Workplace Tech 5.10 and previous / Workplace Tech Editor (EBO) Microsoft Security Updates required for Visio and Office

Issue WPT and WPTE require certain Microsoft Security updates for Visio and for Office running on the host machines. Issues currently observed: Different and various functions in the fluent ribbon do not work or the ribbon does not appear. The following error "Application compile failure during save operation" is seen when saving/compiling an application in WorkPlace Tech Editor Product Line EcoStruxure Building Operation, TAC IA Series Environment Visio 2010, 2013, 2016, 2019, 2021(.msi install)  Visio 2013, 2016, 2019, 2021 (subscription "Click to Run", Plan 2) Office 2010, 2013, 2016 (.msi install) Office 2013, 2016, 365 (subscription "Click to Run", Plan 2) Support for Workplace Tech 5.10 / previous and Workplace Tech Editor Note: Visio 2019 and Visio 2021 are not supported in 5.9.4 or EBO versions before EBO 2022.  Visio 2019 and Visio 2021 are supported when using Workplace Tech 5.10.x and EBO 2022. Cause Interoperability of Visio and Office can cause problems with Workplace Tech and Workplace Tech Editor if these MS16-70 updates are not applied.  If the Office / Visio product is "Click to Run" the software has not been updated to the latest version. Resolution Install the updates from Microsoft Update Catalog To use the catalog, copy and paste the KB number into the "search".  Always select the 32-bit version of the update. Visio 2010 32 bit KB3114872                Office 2010  KB3115198 select 32 bit  Visio 2013 32 bit KB3115020                Office 2013  KB3115173 select 32 bit  Visio 2016/2019 32 bit KB3115041       Office 2016  KB3115144 select 32 bit Visio 2016/2019 32 bit KB4484333 NOTE:  If the Visio or Office is "Click to Run" (subscription such as Office 365, Plan 2) rather than from a Microsoft Office .msi, the product should be upgraded by using the Update Options feature If you try and install the KB/.msi install patches, you will get this message
View full article
Picard Product_Support
‎2020-12-15 09:58 AM

Last Updated: Spock RandyDavis Spock ‎2023-03-09 07:50 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
6762 Views

Niagara Controller Diagnostics and Debug Basics

Issue What diagnostic information is available within Niagara that can be sent to Product Support or acted on locally? Product Line TAC IA Series Environment I/A Series Enterprise Server I/A Series Jace Cause Jace or Enterprise Server operating slow or specific problems are causing the need for debugging a station or platform Resolution There are several diagnostic tools available: Check the station Resource Manager Right-click on the station and select "Views - Station Summary" This will open up a resource monitor page where you can check CPU and memory usage.  The CPU should not be consistently above 80%.  Spiking is common as the process is executing and completing tasks.  There are other things easily referenced here also. Heap memory will vary as well.  It can slowly increase until a garbage collection cycle releases unused heap back to the pool.  You should never use more than 75% of the total available heap memory. Heap Memory is primarily used by station modules and java program objects, so if the memory usage is high, these 2 might be the main reasons Engine Hogs   Right-click on the station, and select "Spy". From the main view, click on "sysManagers". Click "engineManager" and then scroll down to find "Engine Hogs". Clicking Engine Hogs will open a list of the main components of the station and a column on the right-hand side will display the average execution time of the component. Review the top 10 or so and see if any are taking an extraordinary amount of time.  This can help to locate improperly executing objects. Driver Poll Rates Drivers that are based on polling data, like BACnet when COV is not enabled, or Modbus constantly run commands to read data based on the fast, normal, and slow configured rates.  Open the Poll Service under the network the points are being polled on. Looking at the property sheet of the driver, it is important to verify that the cycle time (1) for each rate (fast/normal/slow) is always equal to, or below the actual time configured (2) for that rate. The defaults are 1 second for Fast Cycle Time, 5 seconds for the Normal Cycle Time and 30 seconds for the Slow Cycle Time. Seeing a longer cycle time is usually an indication that the network is saturated with commands and may cause the Jace/Niagara controller to be slow with heavy use of controller resources.  There are several ways to correct this: changing the polling rate spreading the number of objects being polled at each rate, etc. In this example, all points (3) are in the "normal" bucket. Application Director console The "Application Director" (under "Platform") shows a live console output.  Open it by clicking the option under the platform Copy the content of the Application Director, or "stream to file" to send the content to support. It will be essential to help the support engineer to understand the problems in the station.  Add more debug information to the Application Director console You can add more granularity to the messages in the Application Director for a deeper look into possible issues. This can be accomplished in 2 different ways: Right-click on the station, and select "Spy". Then, select "logSetup" on the main view From the list that appears, you can scroll and find appropriate topics to log and you can select at what level you want the information to appear.  This will add traffic to the application Director window so be careful how "fine" and how many logs you enable.  It might be good to consult with support before enabling these logs. example; bacnet.debug/finest if you select this box. Debug Service   Select the "DebugService" from the station "Services" In the Log Category, type a few letters of the topic and scroll to find what you are interested in logging From the pulldown menu, determine the granularity of the log Click the plus Click "Save" Setting this logging and streaming the output to a file will allow information to be sent to support for better diagnostics if required.  Remember to set this logging back to "Default" when done so the Application Director is not overwhelmed with information when you are only trying to view normal station activity.
View full article
Spock RandyDavis Spock
‎2023-03-07 03:28 PM

Labels:
  • TAC IA Series
126 Views

Latest firmware version for the MNL-800

Issue What is the latest firmware version for the MNL-800? Product Line TAC IA Series Environment I/A MNL-800 Cause Upgrade the device to the latest firmware. Resolution The latest firmware version is 2.0 (p/n MNEA-810-200), which was released in January 2004. See Announcement 04-01 listing the features of this version. Announcement regarding the end of commercialization of this part 
View full article
Picard Product_Support
‎2018-09-07 04:12 AM

Last Updated: Spock RandyDavis Spock ‎2023-03-07 01:04 PM

Labels:
  • TAC IA Series
788 Views

LON card indicates fault (unique name required) when multiple LON cards installed in the JACE-6E, JACE-7, and JACE 8000

Issue LON card indicates fault (unique name required) when multiple LON cards are installed in the JACE-6E, JACE-7 or Jace 8000 Product Line TAC IA Series Environment I/A Series G3, JACE-600, JACE-600E, JACE-700 I/A Series N4 JACE 8000 Cause The default name when adding a LON network to the G3/N4 station is LON1.  Both networks will attempt to use the same LON card (LON1) causing a fault condition. Resolution Under each LonNetwork within the Lon Comm Config, specify a unique device name for each card or network (LON1 and LON2).  In the case of the JACE 8000, a total of (4) LON modules is acceptable but would not be advised.  Continue with LON3, and LON4 if required.  
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Last Updated: Spock RandyDavis Spock ‎2023-02-27 07:06 AM

Labels:
  • TAC IA Series
686 Views

Using telnet command to check for open ports

Issue Checking if a port is open Product Line Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices, Pelco, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment TCP/IP Communication Command Prompt Telnet Command Cause Suspect certain network ports are blocked and need to verify Resolution It is possible to check if a port is open in a network by issuing the Telnet command. Note:- Telnet operates using the TCP protocol. UDP connectivity cannot be tested using Telnet. If a port is open, a blank screen will be seen after issuing the command: telnet [domainname or ip] [port] where [domainname or ip] is the domain name or IP address of the server being checked [port] is the port number the server application is listening on For example: telnet 192.168.0.20 9001 (to a closed port would display a connect failed message)   telnet 192.168.0.20 9003 (to an open port would display a blank screen)   To exit the Telnet session, type Ctrl + ] and then type "quit".   For how to enable Telnet in Windows 7 please see Enable Telnet Client on a Windows 7 PC
View full article
Picard Product_Support
‎2018-09-11 05:57 AM

Last Updated: Commander GavinHe Commander ‎2023-02-23 06:32 AM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
7375 Views

Using Telnet to test connectivity

Issue How to use the Telnet command to troubleshoot network connectivity and check for blocked network ports. Product Line TAC INET, TAC Vista, Andover Continuum, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, Field Devices, EcoStruxure Building Operation, Other, Pelco, EcoStruxure Building Expert, Access Expert, Security Expert Environment TCP/IP Communication Command Prompt Telnet Command Cause Suspect certain network ports are blocked and need to verify Resolution Note:- Telnet operates using the TCP protocol. UDP connectivity cannot be tested using Telnet.  
View full article
LocNguyen Schneider Alumni (Retired)
‎2020-01-27 11:23 AM

Last Updated: Commander GavinHe Commander ‎2023-02-23 06:34 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
  • EcoStruxure Workplace Advisor
  • TAC IA Series
  • TAC INET
  • TAC Vista
1479 Views

ProView for LON configuration wizard installation and use with Niagara G3 and N4

Issue Provide the information required to support ProView for LON with Niagara G3 and N4 Product Line TAC IA Series Environment I/A Series G3 (3.5.34 or higher) I/A Series Niagara N4 (4.1.27.20 or higher) ProView for LON (MNL-PROV-WAL) Cause Required files for configuring the ProView for LON display with G3 and N4. Resolution Support for ProView for LON with I/A Series G3 and N4 requires the download and installation of the Distech Controls EC-NET-AX Support Package and EC-Display Configuration files.  Those files are available for download from The Exchange Download Center. Download the following files. BCS Distech Controls EC-Display Configuration v3.4.369 Setup.zip Distech Controls EC-NET AX Support Pack v4.4.17198.1 Setup.zip Unzip the files and run the executables to install the Distech Controls EC-NET-AX Support Package and Distech Controls EC-Display Configuration files. Follow the instructions to install the version(s) required. Install the Distech distribution file into the ENC (if required) using the platform distribution installer. The distribution file will be located in the Distech Controls Files directory added to G3 or N4 during the installation process. Open the distechControls palette (LonWorks - Services container) and add the LonWorksWizardService to the Services. Open the Drivers - ConfigurableControllers container and add the EcDis210 device object to the LonNetwork. Commission the ProView device using the LON Device Manager. Right-click on the EcDis210 and select Views - Ec Dis Wizard to test the wizard connection and launch the display wizard.
View full article
Picard Product_Support
‎2018-09-07 11:01 PM

Last Updated: Spock RandyDavis Spock ‎2023-02-23 12:17 PM

Labels:
  • TAC IA Series
1119 Views

Installing Niagara 4.9 or later generates a new Host ID

Issue Niagara 4.9 (or later) sometimes has a new Host ID that differs from the Host IDs of other versions of Niagara that were installed on the same host PC Product Line TAC IA Series Environment I/A Series N4 Enterprise Server Cause Niagara 4.9 and later, are only available in a 64-bit version. The older Niagara versions installed on the host PC are probably 32-bit versions, which will always have Host IDs different from 64-bit versions. Resolution If the older versions are Niagara 4.3 or lower, you may need to update the older versions, as per the following document… I/A Series G3 and N4 Eliminating multiple HostID on a single PC  Niagara 4.9 (or later) is only available in a 64-bit version.  The other Niagara versions installed on the host PC are probably 32-bit versions, which will always have Host IDs different from 64-bit versions.  In this case, the host PC will require one of the following Un-installing the 32-bit versions and re-installing 64-bit equivalents One license, to be "transferred" to a different Host ID when necessary Multiple licenses, one for each unique Host ID.
View full article
Spock RandyDavis Spock
‎2023-02-23 11:52 AM

on ‎2023-02-23 11:52 AM

Labels:
  • TAC IA Series
105 Views

Reimaging a Jace 8000 Micro SD Card

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Recovering non-functioning Jace 8000 caused by image corruption Product Line TAC IA Series Environment Jace 8000 Cause Improper management of the files on the Micro SD card of the Jace 8000, power brownouts, and other issues have been known to cause corruption of the installed "Golden Image" of the Jace Resolution Download and review the Product Announcement to determine which image should be used on your Jace based on the software to be installed and the Micro SD card version: PADV-IA-22-0001, JACE 8000 Hardware Changes Soon To Be In Effect   Download and select the image and tools for completing the process detailed in the video: I/A Series Niagara JACE 8000 Images and Raw Copy Utility - Installation Software   
View full article
Spock RandyDavis Spock
‎2023-02-23 09:15 AM

on ‎2023-02-23 09:15 AM

Labels:
  • TAC IA Series
245 Views

Tridium N4 Jace 8000 Commissioning Failure

Issue N4 software installation stops because; azul-zre-compact3-qnx7-arm tridium-qnx7-n4-titan-am335x software is missing Product Line TAC IA Series Environment I/A Series N4 Jace 8000 Cause A valid license including the features that meet the dependencies is not installed. Resolution Install a valid license containing the jre8J8000Azul, jre8Qnz7Zulu and qnx7, jreQnx7Zulu features before attempting to commission the Jace 8000
View full article
Spock RandyDavis Spock
‎2023-02-14 08:35 AM

on ‎2023-02-14 08:35 AM

Labels:
  • TAC IA Series
108 Views

Scheduled report generation in a Niagara G3 (AX) station

Issue Can report generation be scheduled in a Niagara G3 (AX) station? Product Line TAC IA Series Environment Niagara G3 (AX) station Cause Set the report schedule in the Export Source Object. Resolution Reports can be generated at scheduled times: Add an Export Source object (from the Report Palette) to the Report Service. Double-click the Export Source Object and set the built-in schedule to the desired time and frequency (e.g. 6:00 AM Daily) Click the chevron near “Source” and browse to the ReportPx file. Click “Next” and choose PxView to Pdf in the Exporter field. Then click “Finish.” Drag an Email or File Recipient to the Report Service and link the Export Source to the Recipient. Set up the Email Recipient with email addresses. Set up the File Recipient with a folder for the file. Force an export by right-clicking the Export Source object and choosing “Actions – Generate”.
View full article
Picard Product_Support
‎2018-09-06 02:37 PM

Last Updated: Spock RandyDavis Spock ‎2023-02-14 06:20 AM

Labels:
  • TAC IA Series
719 Views

Using provisioning Niagara to schedule (automated) ENC station backup

Issue Using provisioning Niagara to schedule (automated) ENC station backup Product Line TAC IA Series Environment I/A Series G3 (AX) version 3.3 and above Cause The station in an ENC (Enterprise Network Controller) can be copied to the ENS (Enterprise Network Server) computer for backup. This can be done by a user using the ENC's Platform Station Copier. There is a need to have an automated process to back up the ENC's station periodically. Resolution Use provisioning Niagara and configure an automated station backup. Provisioning Niagara means an administrator can configure the Enterprise Network Server automation of the following: one or more pre-defined tasks (station backups, install software, update licenses, and copy files) against one or more (potentially many) stations in its Niagara Network done from the Enterprise Network Server in a way where results are recorded and can be referred to later. Refer to this document for a summarized procedure. You should refer to the technical document 'Niagara Ax 3.5 Provisioning Guide for Niagara Networks' for detailed information on using provisioning in Niagara. This document is included with the installation of the I/A Series G3 software and it is located in '\niagara\niagara-3.x.xx\docs\docProvisioningNiagara'. 
View full article
Picard Product_Support
‎2018-09-10 09:05 PM

Last Updated: Spock RandyDavis Spock ‎2023-02-14 06:12 AM

Labels:
  • TAC IA Series
2342 Views

Niagara G3 (AX) Station Save and Backup Station

Issue In a Niagara G3 station, what is the difference between a Station Save and Backup Station? Product Line TAC IA Series Environment Niagara G3 (AX) Jace/ENC Niagara G3 (AX) Enterprise Server (ENS)  Cause Help determine which feature (Station Save and Backup Station) meet the requirement. Resolution A Station Save only saves the config.bog file to the local device (if an ENC, it will save the file on the ENC; if an ENS, it will save it on the ENS computer).  The Backup Station function performs a complete backup of the connected ENC or ENS station, saved as a dist file on the Workbench computer. The backup dist contains the entire station folder plus the specific NRE config used by that ENC or ENS platform, including license(s) and certificate(s). The dist also contains pointers to the appropriate NRE core, Java VM, modules, and OS. If ever needed, you can restore a backup dist using the platform Distribution File Installer view. The backup dist file also contains the TCP/IP configuration of the host when it is backed up. When restoring the backup, the choice to restore these settings, or retain the TCP/IP settings currently in use by the target host is available.
View full article
Picard Product_Support
‎2018-09-06 02:34 PM

Last Updated: Spock RandyDavis Spock ‎2023-02-14 06:05 AM

Labels:
  • TAC IA Series
1331 Views

Fixing Converted .VSDX Workplace Tech Drawings

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Correcting failed links between programming objects after upgrading files from .vsd to .vsdx Product Line TAC IA Series, EcoStruxure Building Operation Environment I/A Series WorkPlace Tech Building Operation Workstation (WorkPlace Tech Editor) Cause After existing .vsd files from pre-WorkPlace Tech 5.10 versions can have corrupted links that stay red when programming objects are added or modified. Resolution This video demonstrates how to correct binding failures that can occur when existing Visio drawings are converted from .vsd to .vsdx format when upgrading to Workplace Tech 5.10 and EBO 4.0 and newer WorkPlace Tech Editor. Note: The objects in the original drawing will no longer show a Master Shape reference (below) The frame around the object appears a little different as well.  The Mega Master will not be changed so this has no effect on the performance of these objects.
View full article
Spock RandyDavis Spock
‎2022-04-27 10:21 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
394 Views

Software and Firmware compatibility matrix for older versions of the traditional product lines

Issue Current information will be stored and updated in release notes and online documentation. Compatibility Matrix of Operating Systems, Video, Product Announcements, SQL Compatibility Product Line Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Windows Operating Systems and iBMS (intelligent Building Management System) Software Cause Compatibility, Firmware, Product Announcements Resolution Please see release documentation for current and recent products. For the Firmware compatibility matrix for: I/NET, it is available HERE or the EcoBuilding Download Center Continuum, click HERE Xenta Software Downloads HERE Vista, click HERE StruxureWare Building Operation, click HERE Product Announcements can be a great tool for discovering which products have been tested and are compatible with the different versions. These documents are available on the Extranet, but have been compiled here for ease of access: I/NET 2.40   Product Announcement 2.41   Product Announcement 2.41a Product Announcement 2.42   Product Announcement and Compatibility Matrix (page 5) 2.43   Product Announcement PA-00239 2.44a Software Available from Exchange Download Center 2.45   Software Available from Exchange Download Center 2.46 Software Available from Exchange Download Center 2.47 Software Available from Exchange Download Center 2.47a Software Available from Exchange Download Center 2.47b Software Available from Exchange Download Center 2.48 Software Available from Exchange Download Center Operating Systems and SQL Supported Video Compatibility Support Policy PA-00279 Software Support for TAC I/NET Continuum v1.92 Product Announcement v1.93 Product Announcement v1.94 Product Announcement PA-00210 1.94 SP1 Product Announcement PA-00273 1.9 - 2.1 Software, Firmware, & Video Compatibility Matrix Concerning IE10 and IE11 browser support  2.0 Feature Blast 2.0 + 2.01/ 2.02 Update Compatibility Matrix 2.0  Product Announcement PA-00353 2.0 CyberStation Installation Guide 2.0 WebClient Installation Guide 2.0 Software License and Ordering Activation Process 2.0 Software and Controller Upgrade Process Andover Continuum PA-00333 Support Policy PA-00272 for Andover Continuum Vista v5.1.5 Product Announcement v5.1.6 Technical Product Advisory v5.1.7 release note document, TAC Vista Compatibility Matrix, SNVT Matrix documents, and TPA-VSTA-11-0020.00 v5.1.7 Product Announcement x5.1.8 Release Note TAC Vista 5.1.8 and TAC Xenta 500/700/900 5.1.8 v5.1.9 Vista Compatibility Matrix SecurityIAS Product Announcement PA-00291 Product Announcement TAC Vista transition to SmartStruxure solution overview  Support Policy PA-00274 for TAC Vista Satchwell Sigma v4.05 SEB Release Notes v4.06 Release Notes v4.06 Release Note Supplement v4.07 Release Notes Satchwell Sigma Standard Edition Installation and User’s Guide Support Policy PA-00297 for Satchwell Sigma v4.08 Release Notes PA-00397 Sigma Version 4.08 Sigma server on a virtual machine Satchwell Micronet data sheet - MicroNet View 2.1 OS Compatibility - Micronet View PA-00228 Product Announcement Support Policy PA-00298 for Satchwell MicroNet PA-00228 Satchwell MicroNet End of Commercialization Announcement I/A Series PA-00163 I/A Series R2 & G3 Product Announcement PA-00114 Legacy Products Windows 7 Compatibility I/A Series R2 with Windows Compatibility Chart PA-00243 Software Product Update - Q2 2013 PA-00251 Hardware Product Update - Q2 2013 PA-00278 Software Product Update - Q3 2013 I/A Series (Niagara) R2 Windows Compatibility Matrix with additional detail I/A Series (Niagara) AX/G3/N4 Windows Compatibility Matrix with additional detail Support Policy PA-00280 R1 for TAC I/A Series StruxureWare Building Operation Please visit Maximum number using StruxureWare Building Operation (Scalability and Capacity) SmartStruxure Lite Please visit SmartStruxure Lite solutions
View full article
Picard Product_Support
‎2018-09-07 07:37 AM

Last Updated: Lieutenant JG MaximeLaudren Lieutenant JG ‎2022-11-09 12:44 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • TAC IA Series
  • TAC INET
  • TAC Vista
8613 Views

NiagaraD Fails to Start (ERROR CODE 1053)

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue In Niagara Enterprise Server versions older than N4.9, the Niagara Service fails to start. Typically the service successfully starts when the 'plat installdaemon' is executed. Product Line TAC IA Series Environment I/A Series N4 Enterprise Server (earlier than N4.9) Cause The Niagara daemon fails to restart automatically after a server reboot Resolution For older Niagara versions, these are two workarounds that may work in some cases:   Option 1:  Go to Start > Run > and type regedit  Navigate to: HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\Control  With the control folder selected, right click in the pane on the right and select new DWORD Value  Name the new DWORD: ServicesPipeTimeout  Right-click ServicesPipeTimeout, and then click Modify  Click Decimal, type '180000', and then click OK  Restart the computer Option 2: Create a Task Scheduler task that calls the command "net", with the arguments "start niagara" five minutes after boot.   Alternative Solution (reported to work on Niagara older than 4.7): There are two solutions to implement in the Niagara Service. Before performing the settings below you must first have NiagaraD successfully installed. After the computer has rebooted, manually install NiagaraD using 'Plat installdaemon'. Once the service is installed implement the two configurations below. Open Windows 'Services' and then double-click the 'Niagara' service to open the Niagara Service Properties window . You can select to delay the start of the Niagara Service which helps give Windows time to initialize before the service attempts to start. Set the recovery options on the 'Recovery' tab. It is recommended to set all three 'failure' options to 'Restart the Service'
View full article
Spock RandyDavis Spock
‎2022-10-19 01:25 PM

on ‎2022-10-19 01:25 PM

Labels:
  • TAC IA Series
123 Views

MSTP controllers go offline when changing the MaxMaster value in the Automation Server from it's default of 127.

Issue MSTP controllers go offline when changing the MaxMaster value in the Automation Server from it's default of 127 Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server MSTP Master Controllers Cause The MaxMaster value is being set lower than some or all of the MSTP controllers on the network Resolution EcoStruxure Building Operation supports MSTP Master controllers in the address range 0-127 (often refered to as the node id). The MSTP network is a token passing network where the token is passed around the network, until a controller has the token it cannot 'talk' to other devices.   The MaxMaster value is defaulted to 127 to allow all devices on the network to receive the token and reply to online status requests, send values etc. If the MaxMaster value is less than any of the MSTP Master controller addresses then those controllers never receive the token and cannot respond to online status requests.   The value for the MaxMaster needs to be equal to or greater than the highest addressed MSTP controller node id.  For example, if the highest node id=54 then the MaxMaster will need to be set to 54 or higher. For maximum efficiency the MaxMaster should be set 1 or 2 greater than the highest controller address, this allows for adding future devices without needlessly polling for many non-existent devices.    Please refer to BACnet MS/TP Network Properties – Basic Tab or Configuring the MS/TP Network for b3 Communication 
View full article
Picard Product_Support
‎2018-09-06 08:40 AM

Last Updated: Administrator CraigEl Administrator ‎2022-10-16 06:03 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • TAC IA Series
867 Views
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 91
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc