Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Building Automation Knowledge Base

Access this self-service resource 24/7 and post your questions or scroll through forums for answers on building automation.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Field Devices
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,192
  • TAC Vista 2,049
  • TAC IA Series 1,805
  • EcoStruxure Building Operation 1,715
  • TAC INET 1,461
  • Field Devices 712
  • Satchwell BAS & Sigma 475
  • EcoStruxure Security Expert 284
  • Satchwell MicroNet 254
  • EcoStruxure Building Expert 227
  • EcoStruxure Access Expert 124
  • CCTV 53
  • Project Configuration Tool 30
  • EcoStruxure Building Advisor 7
  • Automated Engineering Tool 4
  • EcoStruxure Workplace Advisor 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
3

Related Forums

  • Field Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "field devices"

View in: "Building Automation Knowledge Base" | Community

712 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 36
  • Next »
Label: "Field Devices" Show all articles

Replacement of Satchwell "M 1201" Actuator forming part of combined Actuator / 2-port Valve Body assembly due to obsolescence.

Issue Satchwell “M 1201” Actuator forming part of combined Actuator / 2-port Valve Body assembly requires replacement. Environment Stand alone Satchwell “M 1201” Actuator forming part of combined Actuator / 2-port Valve Body assembly M 1201 Actuator 2-port Valve Body Cause Obsolescence of Satchwell “M 1201” forming part of combined Actuator / 2-port Valve Body assembly. Resolution There is no direct replacement for the "M 1201" Actuator and as a result both the "M 1201" Actuator and the 2-port Valve Body to which it is connected will also require replacement.  Replace Satchwell “M 1201” combined Actuator & 2-port Valve Body assembly with Schneider Electric MD10B-230 Actuator, LMD-MB Linkage Kit and Satchwell MB series 3-port Valve Body of appropriate size. Details of the original Satchwell “M 1201” combined Actuator & 2-port Valve Body assembly may be viewed here. Details of the replacement Schneider Electric MD10B-230 Actuator may be viewed here. Details of the replacement Schneider Electric LMD-MB Linkage Kit may be viewed here. Details of the replacement Satchwell MB 3-port Valve Body may be viewed here. N.B. Satchwell MB series 3-port Rotary Shoe Valve Body may be converted for use as a 2-port Zone Valve by means of the installation of a plumber’s plug in Port 3 Install plumber's plug in Port 3 of MB series 3-port Rotary Shoe Valve Body. Tighten plumber's plug sufficiently to ensure PN 10 rating of Valve Body is not compromised. It is possible that the "M 1201" Actuator may have been fitted with an Auxiliary Switch. If so then an MD-S1 Auxiliary Switch may be fitted to the MD10B-230 Actuator if required. Details of the MD-S1 Auxiliary Switch may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 04:56 AM

Last Updated: Administrator chris_clerc Administrator 2 weeks ago

Labels:
  • Field Devices
1201 Views

Viconics VT7600x1000x exceeding the set 3 Cool Cycles Per Hour (CPH)

Issue Tested the Viconics VT7600x1000x for Cool CPH set to 3.  Manually heated the thermostat and let it cool to cycle the cool stages and it cycled on and off 7 times before stopping the test.  According to the documentation it should have stopped after 3 on/off cycles. Product Line Field Devices Environment SSL SE7000 Cause Cooling/heating has to be within 15-85% of the proportional band. Resolution With the Viconics VT7600x1000x series products, the CPH only works when the cooling/heating demand is within 15 to 85% of the proportional band. The thermostat has a 2 degree proportional band (fixed) so at a setpoint of 72 and CPH of 3 (cooling CPH adjustable 3-4), if the temperature stays between 72.3 and 73.7 the CPH is at 3. Outside of that band the cooling/heating is allowed to cycle as often as needed.
View full article
Picard Product_Support
‎2018-09-06 02:33 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-31 07:45 PM

Labels:
  • Field Devices
549 Views

How do you reset the Viconics VT7200, VT7300, & VT7600 LON series thermostats back to factory default values?

Issue How do you reset the Viconics VT7200, VT7300, & VT7600 LON series thermostats back to factory default values? Product Line Field Devices Environment SSL SE7000 Cause There's no button or command that sets the thermostat to its default parameter settings. Resolution Either set them manually or through the snvts available via a LON integration.  The Viconics Lon Integration Manual will help with identifying the proper snvts to use.
View full article
Picard Product_Support
‎2018-09-06 02:29 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-29 04:57 PM

Labels:
  • Field Devices
1839 Views

BACnet/MSTP communication to Viconics VT thermostats is intermittent.

Issue BACnet/MSTP communication to Viconics VT thermostats is intermittent. Product Line Field Devices Environment SE7000 Room Controller Cause Possible cause is physical layer and device addresses. Resolution Verify the physical layer (i.e. wire, end of line resistors and bias resisters) is installed as recommended.  A common wiring error is landing the trunk cable shield to the "REF" terminal at the thermostat. The shield should be carried through but not landed at the thermostat and the trunk shield should be grounded in one place. Duplicate device addresses can cause this type of issue as well. Verify each controller has a unique "Com addr" which is part of its instance number. This can be viewed and modified from the display panel of the thermostat. To enter the configuration parameter menu: VT7200 series press and hold the button(OVERRIDE) for 8 seconds VT7300 series press and hold the middle button(°C/F or OVERRIDE)for 8 seconds. VT7600 series press and hold the button(MENU)for 8 seconds
View full article
Picard Product_Support
‎2018-09-06 02:44 PM

Last Updated: Administrator CraigEl Administrator ‎2023-03-28 09:20 PM

Labels:
  • Field Devices
778 Views

SLPSXC2 CO2 sensor calibration using both ABC standard and Fresh Air process

Issue Can SLPSXC2 CO2 sensor calibration be used with both methods (ABC standard and Fresh Air process) at the same time? Product Line Field Devices. Environment Building Operation SmartX Living Space Sensor. Cause SLPSXC2 CO2 can be calibrated using two different methods. Automatic Baseline Calibration(ABC) The ABC algorithm constantly keeps track of the sensor’s lowest reading over a pre-configured time interval and slowly corrects for any long-term drift detected when compared to the expected fresh air value of 400 ppm. ABC calibration is enabled/disabled through coil 4 (invoke = enable ABC). Manual Calibration Coil 11 triggers the manual calibration (FRC 400ppm) => this will tell the sensor that the current level of CO2 should be interpreted as 400ppm. When setting this register to 1, it automatically goes back to 0 a couple of seconds later. Setting Coil 11 to value 1 is the same as pressing the calibration button. Resolution The both methods of calibration can be used simultaneously since one method is for correcting drift over time (1 week intervals), the other is a manually executed reset.   The only error would come if the unit was exposed to high CO2 concentrations at night, inducing abnormal averages. If ABC is disabled, manual calibration would need to be performed more frequently.
View full article
Spock MikaelKrantz Spock
‎2023-03-07 03:48 PM

on ‎2023-03-07 03:48 PM

Labels:
  • Field Devices
111 Views

Using telnet command to check for open ports

Issue Checking if a port is open Product Line Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices, Pelco, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment TCP/IP Communication Command Prompt Telnet Command Cause Suspect certain network ports are blocked and need to verify Resolution It is possible to check if a port is open in a network by issuing the Telnet command. Note:- Telnet operates using the TCP protocol. UDP connectivity cannot be tested using Telnet. If a port is open, a blank screen will be seen after issuing the command: telnet [domainname or ip] [port] where [domainname or ip] is the domain name or IP address of the server being checked [port] is the port number the server application is listening on For example: telnet 192.168.0.20 9001 (to a closed port would display a connect failed message)   telnet 192.168.0.20 9003 (to an open port would display a blank screen)   To exit the Telnet session, type Ctrl + ] and then type "quit".   For how to enable Telnet in Windows 7 please see Enable Telnet Client on a Windows 7 PC
View full article
Picard Product_Support
‎2018-09-11 05:57 AM

Last Updated: Commander GavinHe Commander ‎2023-02-23 06:32 AM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
7375 Views

SE8xxx Room Controller Password

Issue Unable to access the SE8xxx or SER8xxx Room Controller configuration parameters menu - displays an error code. Product Line EcoStruxure Building Expert, Field Devices  Environment SE8xxx and SER8xxx Room controller SE8000 and SER8000 Series Ex. Viconics branding VT8000 Series Cause The PswrdSet parameter sets a protective access password to prevent unauthorized access to the configuration menu parameters. An error code is displayed whenever the password lockout is active and an incorrect password is used. Resolution Contact your region's Customer Care Center for a temporary password. The error code which is unique to that controller will be required by the Customer Care Center to calculate the temporary password.
View full article
Sisko DavidChild Sisko
‎2020-03-13 08:26 AM

Last Updated: Administrator CraigEl Administrator ‎2023-02-14 03:36 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
827 Views

Have the VZ22, VZ32, VZ42 valves been replaced by the VZ219, VZ319, VZ419 series?

Issue Have the VZ22, VZ32, VZ42 valves been replaced by the VZ219, VZ319, VZ419 series? Product Line Field Devices Environment Vista Satchwell Continuum Micronet Sigma Cause VZ*19* zone valves now available with equal or better specification than the older VZ*2 valves Resolution As per PA-00911 the VZ22, VZ32, VZ42 series valves are no longer available for sale.  The alternative is the standard catalogue zone offer, either the VZ*08* with MZ140 for thermal (low cost, silent) solutions, or the VZ*19* with MZ20 for a Motoric actuator solution. The alternative range VZ*08E or VZ*19*, is lower in cost and would be a suitable replacement in most applications. For high pressure applications, the VP228E PIBCV would be a suitable alternative. There should be no technical concern with changing over a PIBCV from a zone valve if the system pressure is above 25 kPa. There will be slight dimensional differences in the zone valve body length but for most installations the existing pipework should be able to accommodate the difference. A cross reference from the discontinued offer to the new offer is detailed PA-00911.   Datasheets for all valves and actuators can be found here or here for MZ18A, MZ18B, MZ20A, MZ20B, VZ*19*
View full article
Picard Product_Support
‎2018-09-06 12:02 PM

Last Updated: Administrator CraigEl Administrator ‎2022-12-14 05:07 PM

Labels:
  • Field Devices
1109 Views

How to read the accuracy and repeatability on CO2 sensors

Issue How to read and understand the accuracy and repeatability on CO2 sensors. The sensors shows 380 ppm, is it defect? Product Line Field Devices Environment CO2 Sensors Cause Accuracy +- 30ppm +-2% of measured value Repeatability +- 20ppm +-1% of measured value Resolution   Accuracy The accuracy of a unit is defined as the tolerance between the actual absolute gas concentration and the measured value. For example, if a unit has a specified accuracy of ±30ppm, this implies that the displayed value will be within 30 parts‐per‐million of the actual gas concentration under standard ambient operating conditions. If the gas concentration in a room is 400ppm, then the sensor is operating within rated parameters if it reads anywhere between 370ppm and 430ppm on average.   Repeatability Repeatability is closely related to precision. Repeatability is defined as the variance in measured values of a known, unchanging gas sample upon repeat measurements. To put it another way repeatability is the range of acceptable values the sensor will read, relevant to a previous measurement, when measuring a gas, independent of the actual gas concentration.  For example, if the gas concentration in a room is 400ppm and the sensor has a rated repeatability of ±10ppm, then if originally the sensor reads 420ppm, upon future measurements the sensor will read between 410ppm and 430ppm.  Repeatability is generally specified as having a tighter tolerance than accuracy. Even if a sensor is reading a value that is slightly high when compared to the actual gas concentration, it is likely that it will read close to the same slightly higher value upon repeat measurements.   How to understand the accuracy and repeatability Accuracy +- 30ppm +-2% of measured value Repeatability +- 20ppm +-1% of measured value Accuracy at 400ppm:                     Min =  – (30 + 400*0.02) = -38                     Max = + (30 + 400*0.02) = 38 Repeatability at 400pm:                     Min = - (20 + 400*0.01) = -24                     Max = (20+400*0.01) = 24   This means that in a 400ppm environment, the sensor output can vary between                     400-38-24 = 328 ppm                     400+38+24 = 462 ppm Finally, based on the explanation given above, 380ppm would still be in spec. However, another reason could be that the calibration was done in an environment that was not the “purest” and by doing so, an offset was created on the 400-baseline explaining why values below 400ppm are reported.   As said 380ppm is still in spec but the customer could try to recalibrate the CO2 sensor to see if it changes anything.
View full article
Spock MikaelKrantz Spock
‎2022-11-24 01:44 AM

on ‎2022-11-24 01:44 AM

Labels:
  • Field Devices
142 Views

Frequency of Zigbee device SED-CO2-G-5045 sending its values

Issue Frequency of Zigbee device SED-CO2-G-5045 sending its values. Product Line Field Devices. Environment Zigbee SED-CO2-G-5045 CO2 sensor with room temperature and humidity Cause Unsure how frequently the sensor updates it's values to the network. Resolution The sensor has a Transmission Period (writable) that sets how often the device will send a measurement. Default value = 150 seconds Minimum period = 30 seconds maximum period = 600 seconds   Note that there is also a “Night Mode” to help extend battery life. During “Night Mode”, the transmission period is multiplied by 4.   Night mode is entered when the CO2 level falls below the “Comfort Limit Value”, which is 600 ppm by default.  
View full article
Spock MikaelKrantz Spock
‎2022-11-15 03:10 PM

on ‎2022-11-15 03:10 PM

Labels:
  • Field Devices
102 Views

Frequency of  Zigbee device SED-MTH-G-5045 sending its values

Issue Frequency of  Zigbee device SED-MTH-G-5045 sending its values Product Line Field Devices. Environment Zigbee SED-MTH-G-5045 Motion/Humidity/Temperature Sensor Cause Unsure how frequently the sensor updates it's values to the network. Resolution Motion Transmitted immediately on sensing of motion. Temperature  Transmitted, by default at least once every 10 minutes. If it has changed by 0.5 C or more, than it will be sent immediately with a limit on sending no more often than every 2.5 minutes. Minimum interval = 2.5 minutes Maximum interval = 10 minutes Reportable Change = 0.5 degrees C Relative Humidity Transmitted, by default at least once every 10 minutes If it has changed by 0.5%RH or more, it will be sent immediately with a limit on sending no more often than every 2.5 minutes. Minimum interval = 2.5 minutes Maximum interval = 10 minutes Reportable Change = 0.5% RH   These reporting rates are configurable for the sensor.  
View full article
Spock MikaelKrantz Spock
‎2022-11-15 02:57 PM

on ‎2022-11-15 02:57 PM

Labels:
  • Field Devices
100 Views

SPP110 Pressure transmitter Wet media wiring identification

Issue Wire colour coding for the SPP110 Product Line Field Devices Environment SPP110: 004702020 004702040 004702060 004702080 004702100 004702120 004702140 Cause Wire colour coding SPP110 required. Resolution Due to supply problems, between week 23 to week 32, there was a change to the sensor's cable and the wire colours. This was implemented by the manufacturer without Schneider Electric's knowledge. So no product announcement was produced.                      Original       Week 23 to Week 32 No. Function Colour                Colour 1     Y            Brown                Green 2    GO         Black                  White 3    G            Red                    Brown   Standard                                                                                           Week 23 to Week 32   Refer to the SPP110 Pressure Transmitter Wet Media Specification Sheet for more information.   The SPP110 installation sheet showing the standard wire colouring is available here The SPP110 installation sheet showing the wire colouring is attached.
View full article
Picard Product_Support
‎2018-09-11 03:56 AM

Last Updated: Captain Gary Captain ‎2022-11-09 04:53 AM

Labels:
  • Field Devices
2555 Views

Replacement for Satchwell AVUE, AVUX or AVUM mark 5 range

Warning Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source. Issue Need to replace an AVUE, AVUX or AVUM Mark 5 Actuator Product Line Field Devices Environment AVUE5305 AVUE5355 AVUE5304 AVUE5354 AVUX5202 AVUM5601 Cause Need to find a replacement for the obsolete AVUE, AVUX or AVUM Mark 5 actuator, that will allow the valve to be retained. Resolution The AVU* Mark 5 range of actuators can be replaced from the MZ300S range. AVUE5305 replace with MZ300S-24M AVUE5355 replace with MZ300S-24M AVUE5304 replace with MZ300S-24M AVUE5354 replace with MZ300S-24M AVUX5202 replace with MZ300S-24F AVUM5601 replace with MZ300S-230F The AVUE, AVUX, AVUM Mk 5 Datasheet is attached   MZ300S Specification sheet   MZ300S-24M Installation Instructions MZ300S-24F Installation Instructions   MZ300S-230F Installation Instructions
View full article
Captain Gary Captain
‎2022-10-19 05:50 PM

on ‎2022-10-19 05:50 PM

Labels:
  • Field Devices
146 Views

SpaceLogic SLO/SLR Label showing incorrect kL range value

Warning Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source. Issue The SLO Label shows an incorrect value range for kL. Product Line Field Devices Environment SpaceLogic SLO series Lux sensor Cause The label on the SLO shows the incorrect value range for kL. Resolution SLO: The product specification sheet states the Ranges for the jumper as: - 0 to 500 lx and 0 to 20 kLx The range to 500 lx can be seen on the circuit board. The product’s label shows 0 – 4kL The manufacturer has confirmed the label is incorrect the value should be 500 lx, New labels will be used in production from August 2022.   SLR: The tense delivery situation during the pandemic, especially for electronic components, has forced the manufacturer to make technical changes to the SLR in order to stay able to continue to deliver reliably. The range has extended from 0.4 to 0.5 kLux. These changes are incorporated in the corresponding instructions, provided with the devices. New labels will show the extended range.
View full article
Captain Gary Captain
‎2022-08-24 08:37 AM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • TAC Vista
119 Views

What is difference between valve rangeability and turndown ratio?

Issue What is difference between valve rangeability and turndown ratio? Product Line Field Devices Environment Valves Cause Definition of the terms helps explain the flow outcomes. Resolution Rangeability - maximum controllable flow divided by minimum controllable flow Turndown ratio - normal maximum system flow divided by minimum controllable flow.   Rangeability is the inherent characteristic of the valve and turndown ratio is the installed characteristic.
View full article
Picard Product_Support
‎2018-09-06 02:30 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-30 11:12 PM

Labels:
  • Field Devices
2836 Views

Data sheet for MD-S1 / MD-S2 auxiliary switch

Issue Unable to locate data sheet for the MD-S1 and MD-S2 auxiliary switch Product Line Field Devices Environment MD-S1 auxiliary switch MD-S2 auxiliary switch Cause No data sheets can to be found. Resolution Data sheets for the MD-S1 and MD-S2 auxiliary switches are not available. To review the MD-S Auxiliary Switch Installation Sheet, please click HERE.
View full article
Picard Product_Support
‎2018-09-10 10:33 PM

Last Updated: Captain Gary Captain ‎2022-08-24 06:36 AM

Labels:
  • Field Devices
2843 Views

Modbus Protocol Information

Issue What resources are available to get more information on the Modbus protocol? Product Line Andover Continuum,EcoStruxure Building Operation,Field Devices,Satchwell BAS & Sigma,Satchwell MicroNet,TAC IA Series,TAC INET,TAC Vista Environment Modbus ASCII/RTU Modbus TCP/IP Cause The Modbus protocol information is available on www.modbus.org Use the menu on the left and select Technical Resources. Select the Modbus Specifications. Resolution Found on www.modbus.org are the protocol specifications: Modbus ASCII/RTU Modbus TCP
View full article
Picard Product_Support
‎2018-09-10 01:26 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-22 08:47 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
2207 Views

Replacement of VTRA Valve Body by VTRE or MB/MBF Valve Body due to obsolescence.

Issue VTRA Valve Body requires replacement due to obsolescence. Product Line Field Devices Environment VTRA 3-port Mixing Valve Body Cause Obsolescence of VTRA Valve Body Resolution VTRA Valve Bodies are obsolete and have been for many years. VTRA Valve Bodies were available with either Flanged or Screwed connections.  Details of the various size / connection combinations available appear VTRA Specification Sheet. REPLACEMENT OF VTRA FLANGED CONNECTION VALVE BODY A replacement for the VTRA Flanged Valve Body (32-80mm) may be selected from the VTRE range of Flanged Valve Bodies, see VTRE S-E Specification Sheet for more datails. N.B. It should be noted that the VTRE Valve Body is rated PN6 whereas the VTRA was rated PN10. The VTRE Flanged Valve Body may be operated by the EM9 Actuator, see Alternatively the VTRE Flanged Valve Body may be operated by the M9B Actuator, See EM 9 Specification Sheet for more details. No Linkage Kit is required to mount the EM9 or M9B Actuator on the VTRE Valve Body. Alternatively a replacement for the VTRA Flanged Valve Body (65-80mm only) may be selected from the the S-E VG311F and V321 3-Port Flanged Valve Bodies, more details can be found in the Venta VG311F 65-150C Specification Sheet and the Venta V321 Specification Sheet N.B. It should be noted that the S-EVG311F and V321 Valve Body are rated PN16 whereas the VTRA was rated PN10.   REPLACEMENT OF VTRA SCREWED CONNECTION VALVE BODY A replacement for the VTRA Screwed Valve Body (15-50mm) may be selected from the MB range of Screwed Valve Bodies, see the MB/MBF data sheet for more details. The MB Screwed Valve Body may be operated by the MD10B series Actuator, see the MD10B specification sheet for more details. Alternatively the MB Screwed Valve Body may be operated by the MD10A Actuator, see the MD10A specification sheet for more details.  
View full article
Picard Product_Support
‎2018-09-10 05:19 AM

Last Updated: Captain Gary Captain ‎2022-08-22 07:08 AM

Labels:
  • Field Devices
1950 Views

Replacement of Satchwell ALE series Linear Actuator by Schneider Electric M800 Linear Actuator due to obsolescence. (Actuator Selection)

Issue Satchwell ALE series Linear Actuator requires replacement. Product Line Field Devices Environment Satchwell ALE series Linear Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF series Plug and Seat Valve Body.  Actuator type :- ALE series.  Cause Obsolescence of Satchwell ALE series Linear Actuator. Resolution Replace Satchwell ALE series Linear Actuator with Schneider Electric M800 Linear Actuator and Linkage Kit :-   Linkage kit to mount a M800 actuator to a Satchwell valve (MZ,MZF, VZ, VZF, VSF and MJF) = L2SV Replace ALE Actuator with M800 + L2SV combined part number 880-0650-000 Replace ALE with Auxilary Switch kit with M800-S2 + L2SV combined part number 880-0651-000 Just linkage kit = 880-0124-000 Just M800 = 880-0310-030 N.B.  Should the Satchwell ALE series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the S-E M800 Actuator as appropriate :-  S2 - Two independent 24 volt 4amp AC-1 rated SPDT Auxiliary End Point Switches. (880-0104-000)   Particular care should be taken when selecting an Schneider Electric Forta M800 Actuator to replace an existing Satchwell ALE series Actuator. The Schneider Electric Forta M800 Actuator may be used to replace an existing Satchwell ALE series Actuator but it should be noted that where an existing Satchwell ALE series Actuator has been connected directly to a Satchwell Controller, an independent Transformer rated to provide the greater level of power required by a single Schneider Electric Forta M800 Actuator (50VA) will also be required. (e.g. Schneider Electric Transformer Type TR60)   Where an existing Satchwell ALE series Actuator has been connected via an independent Transformer, it is possible that the Transformer may have been rated to provide the level of power required by a single ALE series Actuator (9.5VA) only.   In such circumstances the existing independent Transformer may also require replacement by another independent Transformer, rated to provide the greater level of power required by a single Schneider Electric Forta M800 Actuator (50VA) (e.g. Schneider Electric Transformer Type TR60) Details of the Schneider Electric M800 Actuator may be viewed here Details of the Schneider Electric TR60 Transformer may be viewed here
View full article
Picard Product_Support
‎2018-09-07 06:43 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-22 08:00 PM

Labels:
  • Field Devices
2216 Views

Replacement of Satchwell AR Series 7 Rotary Actuator by Schneider Electric MD Series Rotary Actuator due to obsolescence. (Actuator Wiring)

Issue Satchwell AR Series 7 Rotary Actuator requires replacement Product Line Field Devices Environment Satchwell AR Series 7 Rotary Actuators installed on Air Dampers, Satchwell MB Series or MBF Series Rotary Shoe Valve Bodies. Actuator types :- ARE ARM ARX Cause Obsolescence of Satchwell AR Series 7 Rotary Actuators Resolution Replace Satchwell AR Series 7 Rotary Actuators with appropriate Schneider Electric MD Series Rotary Actuators and wire as follows :- Satchwell AR Series 7 Rotary Actuators installed on Air Dampers. ARE ARE Series 7 Wire Number 2 = MD20A-24 Wire Number 2 ARE Series 7 Wire Number 3 = MD20A-24 Wire Number 3 ARE Series 7 Wire Number 1 = MD20A-24 Wire Number 1 ARE Series 7 Wire Number 5 = MD20A-24 Wire Number 5 ARX ARX Series 7 Wire Number 3 = MD20B-24 Wire Number 3 ARX Series 7 Wire Number 2 = MD20B-24 Wire Number 2 ARX Series 7 Wire Number 1 = MD20B-24 Wire Number 1 ARM ARM Series 7 Wire Number 3 = MD20B-230 Wire Number 3 ARM Series 7 Wire Number 2 = MD20B-230 Wire Number 2 ARM Series 7 Wire Number 1 = MD20B-230 Wire Number 1 ARM Series 7 Wire EARTH = MD20B-230 NO EARTH REQUIRED N.B. Should the Satchwell AR Series 7 Actuator include a wired Auxiliary Switch then the following Accessory should also be wired on the Schneider Electric MD Actuator as follows :- MD – S1 One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch AR COMMON Wire Number S1 = MD-S1 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S1 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S1 N/C contact Wire Number S2 MD – S2 Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches AR COMMON Wire Number S1 = MD-S2 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S2 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S2 N/C contact Wire Number S2 AR COMMON Wire Number S4 = MD-S2 COMMON Wire Number S4 AR N/O contact Wire Number S6 = MD-S2 N/O contact Wire Number S6 AR N/C contact Wire Number S5 = MD-S2 N/C contact Wire Number S5   Satchwell AR Series 7 Rotary Actuators installed on Satchwell MB Series Screwed Rotary Shoe Valve Bodies. ARE ARE Series 7 Wire Number 2 = MD10A-24 Wire Number 2 ARE Series 7 Wire Number 3 = MD10A-24 Wire Number 3 ARE Series 7 Wire Number 1 = MD10A-24 Wire Number 1 ARE Series 7 Wire Number 5 = MD10A-24 Wire Number 5 ARX ARX Series 7 Wire Number 3 = MD10B-24 Wire Number 3 ARX Series 7 Wire Number 2 = MD10B-24 Wire Number 2 ARX Series 7 Wire Number 1 = MD10B-24 Wire Number 1 ARM ARM Series 7 Wire Number 3 = MD10B-230 Wire Number 3 ARM Series 7 Wire Number 2 = MD10B-230 Wire Number 2 ARM Series 7 Wire Number 1 = MD10B-230 Wire Number 1 ARM Series 7 Wire EARTH = MD10B-230 NO EARTH REQUIRED N.B. Should the Satchwell AR 7 Series Actuator include a wired Auxiliary Switch then the following Accessory should also be wired on the Schneider Electric MD Actuator as follows :- MD – S1 One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch AR COMMON Wire Number S1 = MD-S1 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S1 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S1 N/C contact Wire Number S2 MD – S2 Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches AR COMMON Wire Number S1 = MD-S2 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S2 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S2 N/C contact Wire Number S2 AR COMMON Wire Number S4 = MD-S2 COMMON Wire Number S4 AR N/O contact Wire Number S6 = MD-S2 N/O contact Wire Number S6 AR N/C contact Wire Number S5 = MD-S2 N/C contact Wire Number S5   Satchwell AR Series 7 Rotary Actuators installed on Satchwell MBF Series Flanged Rotary Shoe Valve Bodies ARE ARE Series 7 Wire Number 2 = MD20A-24 Wire Number 2 ARE Series 7 Wire Number 3 = MD20A-24 Wire Number 3 ARE Series 7 Wire Number 1 = MD20A-24 Wire Number 1 ARE Series 7 Wire Number 5 = MD20A-24 Wire Number 5 ARX ARX Series 7 Wire Number 3 = MD20B-24 Wire Number 3 ARX Series 7 Wire Number 2 = MD20B-24 Wire Number 2 ARX Series 7 Wire Number 1 = MD20B-24 Wire Number 1 ARM ARM Series 7 Wire Number 3 = MD20B-230 Wire Number 3 ARM Series 7 Wire Number 2 = MD20B-230 Wire Number 2 ARM Series 7 Wire Number 1 = MD20B-230 Wire Number 1 ARM Series 7 Wire EARTH = MD20B-230 NO EARTH REQUIRED N.B. Should the Satchwell AR Series 7 Actuator include a wired Auxiliary Switch then the following Accessory should also be wired on the Schneider Electric MD Actuator as follows :- MD – S1 One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch AR COMMON Wire Number S1 = MD-S1 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S1 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S1 N/C contact Wire Number S2 MD – S2 Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches AR COMMON Wire Number S1 = MD-S2 COMMON Wire Number S1 AR N/O contact Wire Number S3 = MD-S2 N/O contact Wire Number S3 AR N/C contact Wire Number S2 = MD-S2 N/C contact Wire Number S2 AR COMMON Wire Number S4 = MD-S2 COMMON Wire Number S4 AR N/O contact Wire Number S6 = MD-S2 N/O contact Wire Number S6 AR N/C contact Wire Number S5 = MD-S2 N/C contact Wire Number S5   Product Information. For details of AR Series 7 please see here For details of MD10A please see here For details of MD10B please see here For details of MD20A please see here For details of MD20B please see here For details of MD-S1 please see here For details of MD-S2 please see here
View full article
Picard Product_Support
‎2018-09-10 12:23 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-22 07:50 PM

Labels:
  • Field Devices
1988 Views
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 36
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc