Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Building Automation Knowledge Base

Access this self-service resource 24/7 and post your questions or scroll through forums for answers on building automation.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Field Devices
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,192
  • TAC Vista 2,049
  • TAC IA Series 1,805
  • EcoStruxure Building Operation 1,715
  • TAC INET 1,461
  • Field Devices 712
  • Satchwell BAS & Sigma 475
  • EcoStruxure Security Expert 284
  • Satchwell MicroNet 254
  • EcoStruxure Building Expert 227
  • EcoStruxure Access Expert 124
  • CCTV 53
  • Project Configuration Tool 30
  • EcoStruxure Building Advisor 7
  • Automated Engineering Tool 4
  • EcoStruxure Workplace Advisor 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
3

Related Forums

  • Field Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "field devices"

View in: "Building Automation Knowledge Base" | Community

712 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • 2
    • 3
    • 4
    • …
    • 36
  • Next »
Label: "Field Devices" Show all articles

STR800 Series Wall Module wiring details

Issue Not generally available Product Line Field Devices Environment I/A series Field device Cause Information not provided with the documentation supplied. Resolution The STR800 Series User manual can be downloaded by selecting this link. The STR800 Temperature Sensor RoHS Certificate can be downloaded by selecting this link. The STR800 Wall Module Specification Sheet can be downloaded by selecting this link. Other STR800 documentation is available on the Schneider Download Center.
View full article
Picard Product_Support
‎2018-09-10 12:51 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:39 PM

Labels:
  • Field Devices
  • TAC IA Series
867 Views

Replacement of Satchwell CZU Mk 2 Zonemaster Controller by S-E Satchwell CZU Mk 4 Zonemaster Controller due to obsolescence.

Issue Satchwell CZU Mk2 Zonemaster Controller requires replacement. Product Line Field Devices Environment Stand alone Fan Coil Unit Temperature Controller. Satchwell CZU Mk 2 Zonemaster Controller. CZU 2201 CZU 2202 CZU 2203 Cause Obsolescence of Satchwell CZU Mk 2 Zonemaster Controller. Resolution Replacement of Satchwell CZU Mk 2 Zonemaster Controller with S-E Satchwell CZU Mk 4 Zonemaster Controller. The CZU 4201 may be used to replace the following CZU Mk 2 Controllers :- CZU 2201, CZU 2202, CZU 2203 N. B. CZU 2201 Controllers provided an additional -9 to +9 V d.c. output enabling connection to peripherals such as the Satchwell NSU 1401 Night Set-back Override Unit, TSU 1402 Two Step Auxiliary Unit and SSU 1403 Signal Selector Unit. CZU 2202 and CZU 2203 Controllers provided an additional -0.5 to +9 or -9 to +0.5 V d.c. output enabling connection to the Satchwell NSU 1401 Night Set-back Override Unit.  Additional outputs are not provided on the CZU 4201 Controller and in those applications where these are required then it will be necessary to consider an alternative Controller to the CZU 4201. Details of the CZU 4201 may be viewed here. A remote Satchwell Adjustable Room Temperature Sensor such as the DRT 3451, or a remote Satchwell Duct Temperature Sensor from the DDU range of Sensors may have been installed and connected to the Controller. Any existing remote Satchwell Temperature Sensors may be retained for connection to the CZU 4201. Should the remote Satchwell Adjustable Room Temperature Sensor require replacement then this may be replaced by an S E STR 612 Adjustable Room Temperature Sensor. Details of the STR 612 may be viewed here. Should the remote Satchwell Duct Temperature Sensor require replacement then this may be replaced by an S E STD 670 Duct Temperature Sensor. Details of the STD 670 may be viewed here
View full article
Picard Product_Support
‎2018-09-10 03:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:19 PM

Labels:
  • Field Devices
1074 Views

Replacement of Satchwell CD2401 Proportional Controller-Actuator by Schneider Electric Satchwell CZT Proportional Controller due to obsolescence.

Issue Satchwell CD2401 Proportional Controller-Actuator requires replacement. Product Line Field Devices Environment Stand alone discreet Satchwell CD2401 Proportional Controller-Actuator Cause Obsolescence of Satchwell CD2401 Proportional Controller-Actuator Resolution Replace Satchwell CD2401 Proportional Controller-Actuator with Schneider Electric Satchwell CZT5305 Proportional Controller, compatible Temperature Sensor and MD Series Actuator and Linkage Kit. Replace Satchwell CD2401 Proportional Controller-Actuator with Schneider Electric Satchwell CZT5305 Proportional Controller. Details of the Schneider Electric Satchwell CZT 5305 Proportional Controller may be viewed here. Replacement of Temperature Sensor It should be noted that although the existing Satchwell Temperature Sensor associated with the CD2401 Proportional Controller–Actuator is obsolete, it is compatible with the CZT Proportional Controller and may be retained. Should it be decide to install a replacement Temperature Sensor however, then the following may be considered. Room Temperature Sensor STR600 series details of which appear here. Duct Temperature Sensor STD660 details of which appear here. Immersion Temperature Sensor STP660 details of which appear here. NB In order to utilize the existing Pocket a Pocket Adaptor DWA0001 will also be required. Pocket Adaptor DWA0001 details of which appear here. OR Surface mounting Temperature Sensor STC600 details of which appearhere. Replacement of Actuator. Whilst the existing Satchwell MB Valve Body may also be retained, a new Schneider Electric Actuator and Linkage Kit will need to be installed on the MB Valve Body in order to permit control from the CZT Proportional Controller. Details of the Schneider Electric MD10A-24 Actuator may be viewed here. Details of the Schneider Electric LMD/AR-MB Linkage Kit may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 12:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 09:17 PM

Labels:
  • Field Devices
1064 Views

Replacement of Satchwell "MM" combined Actuator & 3-port Valve Body assembly due to obsolescence.

Issue Satchwell “MM” combined Actuator & 3-port Valve Body assembly requires replacement. Product Line Field Devices Environment Stand alone Satchwell “MM” combined Actuator & 3-port Valve Body assembly. MM Actuator 3-port Valve Body Cause Obsolescence of Satchwell “MM” combined Actuator & 3-port Valve Body assembly. Resolution Replace Satchwell “MM” combined Actuator & 3-port Valve Body assembly with Schneider Electric MD10B Actuator, LMD-MB Linkage Kit and Satchwell MB series 3-port Valve Body of appropriate size. Details of the original Satchwell “MM” combined Actuator & 3-port Valve Body assembly may be viewed here. Details of the replacement Schneider Electric MD10B Actuator may be viewed here. Details of the replacement Schneider Electric LMD-MB Linkage Kit may be viewed here. Details of the replacement Satchwell MB 3-port Valve Body may be viewed here. N.B. It is possible that the "MM" Actuator may have been fitted with an Auxiliary Switch. If so then an MD-S1 Auxiliary Switch may be fitted to the MD10B Actuator if required. Details of the MD-S1 Auxiliary Switch may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 04:55 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 08:55 PM

Labels:
  • Field Devices
1015 Views

What is the replacement for a Drayton Theta YBL1A Valve Body / Actuator assembly?

Issue The Drayton Theta YBL1A Valve Body / Actuator assembly is to be replaced. Product Line Field Devices Environment Replacement Drayton Actuator Valve YBL1A Cause The Drayton Theta YBL1A Valve Body / Actuator assembly is obsolete. Resolution OVERVIEW The Drayton Theta YBL1A Valve Body / Actuator assembly is obsolete, and there is no purpose built replacement. The Valve Body was available in 1.1/4", 1.1/2" and 2" B.S.P. sizes and was normally installed as a mixing valve in variable temperature, constant volume, compensated heating circuits. No Valve Body / Actuator assemblies are currently available in these sizes. Details of the YB Valve Body may be viewed here.   VALVE BODY REPLACEMENT To replace the YBL1A Valve Body the following is required:- S-E SatchwellMB Valve Body of appropriate size - MB1552 (1.1/4"), MB1602 (1.1/2"), MB1652 (2") Details of the MB Valve Body may be viewed here.   ACTUATOR REPLACEMENT (6-WIRE INSTALLATION) The YBL1A Actuator normally comprised a 6-wire electrical connection enabling it to be operated by a Theta Potentiometric Controller as follows :-  Terminal M1 – Open signal Terminal M2 – Close signal Terminal M3 – Common  Terminal M4 – 135 ohm Feedback Potentiometer – winding Terminal M5 – 135 ohm Feedback Potentiometer – wiper Terminal M6 – 135 ohm Feedback Potentiometer – winding Where 6 wires are connected to the YBL1A Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here Details of the MD20B-24 Actuator may be viewed here. N.B. The YBL1A Actuator also included an additional 3-wire electrical connection associated with an integral S.P.C.O. Auxiliary Switch wired as follows :-  Terminal S1 – Normally Closed Contact Terminal S2 – Common Terminal S3 – Normally Open Contact Where external wiring is connected to the YBL1A Actuator Auxiliary Switch then an Auxiliary Switch Kit containing a S.P.C.O. Auxiliary Switch should be installed on the MD Actuator. Auxiliary Switch Kit MD-S1 (914-1060-000) Details of the MD-S1 Auxiliary Switch Kit may be viewed here. The MD-S1 Auxiliary Switch Kit should be wired as follows :-. Terminal S1 – Common Terminal S2 – Normally Closed Contact Terminal S3 – Normally Open Contact   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here   IMPORTANT NOTE In such 6-wire installations not only will the YBL1A Valve / Actuator assembly need to be replaced but the associated Theta Potentiometric Controller and its Sensors will also need to be replaced.   CONTROLLER REPLACEMENT The Theta Potentiometric Controller may be replaced by the S-E Satchwell CSC5252 or the CSC5352 Compensator Controller. Details of the CSC Controllers may be viewed here.   SENSOR REPLACEMENT Theta 3-wire Temperature Sensors may be replaced by S-E Satchwell 2-wire Temperature Sensors compatible with the S-E Satchwell CSC 5252 or CSC5352 Compensator Controllers selected from the following as appropriate. Outside Air Temperature Sensor (STO 600) Contact Temperature Sensor (STC 600), or alternatively :- Immersion Temperature Sensor (STP 660) + Sensor Pocket Adaptor (DWA 0001) Room Temperature Sensor (STR 600) – OPTIONAL ONLY Details of the STO 600 Outside Air Temperature Sensor may be viewed here. Details of the STC 600 Contact Temperature Sensor may be viewed here. Details of the STP 660 Water Temperature Sensor may be viewed here. Details of the DWA 0001 Sensor Pocket Adaptor may be viewed here. Details of the STR 600 Room Temperature Sensor may be viewed here.   N.B. ACTUATOR REPLACEMENT (3-WIRE INSTALLATION) Should only 3 wires be connected to a YBL1A Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here. Details of the MD20B-24 Actuator may be viewed here. N.B. The YBL1A Actuator also included an additional 3-wire electrical connection associated with an integral S.P.C.O. Auxiliary Switch wired as follows :-  Terminal S1 – Normally Closed Contact Terminal S2 – Common Terminal S3 – Normally Open Contact Where external wiring is connected to the YBL1A Actuator Auxiliary Switch then an Auxiliary Switch Kit containing a S.P.C.O. Auxiliary Switch should be installed on the MD Actuator. Auxiliary Switch Kit MD-S1 (914-1060-000) Details of the MD-S1 Auxiliary Switch Kit may be viewed here. The MD-S1 Auxiliary Switch Kit should be wired as follows :-. Terminal S1 – Common Terminal S2 – Normally Closed Contact Terminal S3 – Normally Open Contact   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here In such 3-wire installations the YBL1A Valve / Actuator assembly only will need to be replaced, while any associated Controller and Sensors may be retained.
View full article
Picard Product_Support
‎2018-09-10 12:17 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 06:45 PM

Labels:
  • Field Devices
1041 Views

SED-T Temperature sensor Integration Tips

Issue Having difficulties integrating an SED-T stat with the MPM (Stat not being "learned" by the MPM) Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Multi-Purpose Manager SED-T00 SED-TS0 SED-TH0 SED-THS Cause Installation manual does not provide enough information Resolution Commissioning tips and recommendations   Dip Switches: SED-T series stats come directly from production with all dip switches set to 0. The dip switches settings must be changed otherwise the device will not send any telegrams. Tip: When pairing an EnOcean Temperature Sensor with the MPM, always set at least one pin of the DIP switch to the ON position before learning it in. Otherwise the MPM will not display any readings regardless of dip switch configuration even if the Enocean ID had been populated in the EODC object. The workaround at this point would be to click on the learn button again, the device will be learned successfully when the “RSSI” value and a “Last Communication” time stamp are displayed.   Example on how to use the dip switches: If the dip switches are set to 1= OFF, 2 = ON, 3 = ON, 4 = OFF, the stat would wake up every 10 seconds and take a look at the values. if they changed, the stat will send a new telegram with the new value. if the value did not change however, the stat will go back to sleep until the next 10 seconds elapse (first iteration). If the value did still did not change before the 7th iteration, then the stat will randomly send a telegram with the unchanged value at any time between the 7th and the 14th iteration. that is a minimum of 10*7 = 70 seconds and maximum of 10*14 = 140 seconds.   Solar cell: When removing the unit from the box for the first time, its energy banks (super capacitor) need to be charged using one of the methods below in order to be able to learn the device. A minimum of 2.1VDC is required before the stat can wake up and send a telegram and Ideally, the Super cap voltage should be between 4 to 5Volts. Method 1: Power the sensor with 24VAC for 1 hour (3volts/hour) Method 2: expose the solar cell to light for x amount of time depending on the light source: 1- Room with LED panels: 24hr minimum charging time (0.1Volts/hour) 2- Lit room with day light: 3-4 hours minimum charging time (0.7Volts/hour) 3- Direct sunlight: 1/2 hour minimum charging time (3.5Volts/hour)   Battery: The 20mm coin cell battery does not charge the super capacitor, however it slows down the depletion of super capacitor once its charge drops below 2.1Volts.
View full article
Picard Product_Support
‎2018-09-11 08:22 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 06:28 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
1093 Views

What replaces the Satchwell CXC controller.

Issue Controller replacement Product Line Field Devices Environment Field   Cause Controller Replacement Resolution The CXC controller provided compensated control. The CSC 5252 or CSC 5253 (With time clock) is the current replacement. Downloads The CXC data sheet can be downloaded here. The CSC data sheet can be downloaded here. The CSC User guide can be downloaded here.   Please be aware: since July 2016 the CSC compensator and other descrete controllers were withdrawn from service. To see "PA-00479 - Discrete Controllers - Notice of Withdrawal - Satchwell" click here.
View full article
Picard Product_Support
‎2018-09-10 11:36 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 11:54 PM

Labels:
  • Field Devices
1206 Views

Replacement of Satchwell CZU Mk 3 Zonemaster Controller by S-E Satchwell CZU Mk 4 Zonemaster Controller due to obsolescence.

Issue Satchwell CZU Mk3 Zonemaster Controller requires replacement. Product Line Field Devices Environment Stand alone Fan Coil Unit Temperature Controller. Satchwell CZU Mk 3 Zonemaster Controller. CZU 3201 CZU 3202 CZU 3203 Cause Obsolescence of Satchwell CZU Mk3 Zonemaster Controller. Resolution Replacement of Satchwell CZU Mk 3 Zonemaster Controller with S-E Satchwell CZU Mk 4 Zonemaster Controller. The CZU 4201 may be used to replace the following CZU Mk 3 Controllers :- CZU 3201, CZU 3202, CZU 3203 N. B. CZU 3201 Controllers provided an additional -9 to +9 V d.c. output enabling connection to peripherals such as the Satchwell NSU 1401 Night Set-back Override Unit, TSU 1402 Two Step Auxiliary Unit and SSU 1403 Signal Selector Unit. CZU 3202 and CZU 3203 Controllers provided an additional -0.5 to +9 or -9 to +0.5 V d.c. output enabling connection to the Satchwell NSU 1401 Night Set-back Override Unit. Additional outputs are not provided on the CZU 4201 Controller and in those applications where these are required then it will be necessary to consider an alternative Controller to the CZU 4201. Details of the CZU 4201 may be viewed  here. A remote Satchwell Adjustable Room Temperature Sensor such as the DRT 3451, or a remote Satchwell Duct Temperature Sensor from the DDU range of Sensors may have been installed and connected to the Controller. Any existing remote Satchwell Temperature Sensor may be retained for connection to the CZU 4201. Should the remote Satchwell Adjustable Room Temperature Sensor require replacement then this may be replaced by an S E STR 612 Adjustable Room Temperature Sensor. Details of the STR 612 may be viewed here. Should the remote Satchwell Duct Temperature Sensor require replacement then this may be replaced by an S E STD 670 Duct Temperature Sensor. Details of the STD 670 may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 01:37 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 10:19 PM

Labels:
  • Field Devices
1190 Views

Operation of multiple Satchwell CZU Fan Coil Unit Controllers from a common Temperature Sensor.

Issue Operation of multiple Satchwell CZU Fan Coil Unit Controllers from a common Temperature Sensor. Product Line Field Devices Environment Fan Coil Unit installations comprising multiple Satchwell CZU Fan Coil Unit Controllers. Stand alone discreet Satchwell CZU Mk 1, Mk2, Mk3 and Mk4 Zonemaster Controllers CZU1201 CZU1202 CZU1203 CZU2201 CZU2202 CZU2203 CZU3201 CZU3202 CZU3203 CZU4201 Cause From time to time the need arises for office partition layouts within a building to be revised in order to reflect changes in occupancy requirements. This can result in the combination of numerous individual controlled spaces into a common controlled space. This in turn may result in the need to revise associated Fan Coil Unit control systems installed in the controlled spaces affected. Such revisions may require multiple Fan Coil Unit control systems to be controlled from a common Temperature Sensor installed in the common controlled space. This form of control may be achieved by adopting the installation method described in the Resolution. Should the common controlled space be of such a size as to benefit from the installation of averaging Temperature Sensors then this may be achieved by installing 4 non-adjustable Temperature Sensors.  The 4 non-adjustable Temperature Sensors should be wired in a series-parallel configuration in order to ensure compatibility with the associated Satchwell CZU Fan Coil Unit Controller. The series-parallel wiring configuration may be achieved by adopting the installation method described in the Resolution. Resolution 1.  Operation of multiple Satchwell CZU Fan Coil Unit Controllers from a common Temperature Sensor.  Multiple Satchwell CZU Fan Coil Unit Controllers should not be connected directly to a common Temperature Sensor. Instead the common Temperature Sensor should be connected to a single Satchwell CZU Fan Coil Unit Controller. The single Satchwell CZU Fan Coil Unit Controller should then be connected to the associated Fan Coil Unit Heating Coil Control Valve Actuators and / or Cooling Coil Control Valve Actuators. Up to 7 Heating and / or 7 Cooling Control Valve Actuators may be wired to a single Satchwell CZU Fan Coil Unit Controller in accordance with the method shown here 2.  Averaging Temperature Sensor control. Should the controlled space be of such a size as to benefit from the installation of averaging Temperature Sensors then 4 non-adjustable Temperature Sensors may be wired in series-parallel configuration in order to ensure connection compatibility with the associated Satchwell CZU Fan Coil Unit Controller. The 4 non-adjustable Temperature Sensors may be wired in series-parallel configuration to a common Satchwell CZU Fan Coil Unit Controller in accordance with the method shown here
View full article
Picard Product_Support
‎2018-09-10 02:31 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 10:17 PM

Labels:
  • Field Devices
1212 Views

Replacement of Satchwell "M 1301" Actuator forming part of combined Actuator / 3-port Valve Body assembly due to obsolescence.

Issue Satchwell "M 1301" Actuator forming part of combined Actuator / 3-port Valve Body assembly requires replacement. Product Line Field Devices Environment Stand alone Satchwell “M 1301” Actuator forming part of combined Actuator / 3-port Valve Body assembly M 1301 Actuator 3-port Valve Body Cause Obsolescence of Satchwell "M 1301" forming part of combined Actuator / 3-port Valve Body assembly. Resolution There is no direct replacement for the "M 1301" Actuator and as a result both the "M 1301" Actuator and the 3-port Valve Body to which it is connected will also require replacement.  Replace Satchwell “M 1301” combined Actuator & 3-port Valve Body assembly with Schneider Electric MD10B-230 Actuator, LMD-MB Linkage Kit and Satchwell MB series 3-port Valve Body of appropriate size. Details of the original Satchwell “M 1301” combined Actuator & 3-port Valve Body assembly may be viewed here. Details of the replacement Schneider Electric MD10B-230 Actuator may be viewed here. Details of the replacement Schneider Electric LMD-MB Linkage Kit may be viewed here. Details of the replacement Satchwell MB 3-port Valve Body may be viewed here. N.B. It is possible that the "M 1301" Actuator may have been fitted with an Auxiliary Switch. If so then an MD-S1 Auxiliary Switch may be fitted to the MD10B-230 Actuator if required. Details of the MD-S1 Auxiliary Switch may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 05:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 10:00 PM

Labels:
  • Field Devices
1290 Views

Sensor Calibration certificate, Veris portfolio

Issue   A calibration certificate is sometimes requested by the end customer Product Line Field Devices Environment Veris sensors Cause   To ensure that a sensor is keeping measurement values within specification, a certificate is sometimes requested by the end customer. Resolution Calibration certificates are available for some Veris models and must be requested at the time of ordering by selecting  “N” in NIST block for 1% and 2% humidity transmitters. Temperature transmitters can be ordered with 1 or 2 point calibration certificates by selecting 1 or 2 in the in the Temp Cert Block. The following example shows how the model numbers are built up: As can be seen in the second example above the model HD2NVCTC2 has a 2% accuracy RH element with a NIST traceable certificate, it also has a 1K platinum RTD with a 2 point  calibration certificate. For information on NIST traceability see the National Institute of Standards and Technology website
View full article
Picard Product_Support
‎2018-09-11 02:48 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 09:39 PM

Labels:
  • Field Devices
1175 Views

SEC-TE/SED-0 does not join the MPM’s ZigBee network and does not go online

Issue SEC-TE (TE2) smart terminal controller / SED-0 (DA2) smart wireless actuator will not come online in an MPM controller. Product Line EcoStruxure Building Expert, Field Devices Environment SmartStruxure Lite Multi-Purpose Manager Smart Controllers Cause The Zigbee network configuration parameters in the MPM have been entered incorrectly. Resolution The application version of the SEC-TE/SED-0 must be determined before proceeding forward. Sticker on device should read V13 or V14. To check/modify the current settings, navigate to the "ZigBee Configuration" object (ZBC) under the MPM. For Application Version 13: Stack profile should be set to "Custom" and Security profile should be set to "None." For Application Version 14: Stack profile should be set to "ZigBee Pro" and Security profile should be set to "Home Automation."
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 08:18 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
1323 Views

SER8000 series room controllers communications options

Issue SER8000 series room controllers communications options Environment SER8000 series room controllers Cause Integration to SER8000 room controllers via Modbus is required.  Resolution Currently, the SER8000 series room controllers communications options are Zigbee Pro or BACnet MS/TP. Refer to the SER8300 datasheet.  To communicate on Modbus RS-485, an option would be to use the multi purpose manager (MPM-UN) as a gateway device.    * Updated July 2015 As per Product Annoucement PA-00428, the SE8000 with firmware 1.3 can now act as a Modbus slave using the RS-485 port. 
View full article
Picard Product_Support
‎2018-09-11 06:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:49 PM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
1537 Views

What is the replacement for a Drayton Theta YBL3 Valve Body / Actuator assembly?

Issue The Drayton Theta YBL3 Valve Body / Actuator assembly is to be replaced. Environment Replacement Drayton Actuator Valve YBL3 Cause The Drayton Theta YBL3 Valve Body / Actuator assembly is obsolete. Resolution OVERVIEW The Drayton Theta YBL3 Valve Body / Actuator assembly is obsolete, and there is no purpose built replacement. The Valve Body was available in 1.1/4", 1.1/2" and 2" B.S.P. sizes and was normally installed as a mixing valve in variable temperature, constant volume, compensated heating circuits. No Valve Body / Actuator assemblies are currently available in these sizes. Details of the YB Valve Body may be viewed here.   VALVE BODY REPLACEMENT To replace the YBL3 Valve Body the following is required:- S-E Satchwell MB Valve Body of appropriate size - MB1552 (1.1/4"), MB1602 (1.1/2"), MB1652 (2") Details of the MB Valve Body may be viewed here.   ACTUATOR REPLACEMENT (6-WIRE INSTALLATION) The YBL3 Actuator normally comprised a 6-wire electrical connection enabling it to be operated by a Theta Potentiometric Controller as follows :-  Terminal M1 – Open signal Terminal M2 – Close signal Terminal M3 – Common  Terminal M4 – 135 ohm Feedback Potentiometer – winding Terminal M5 – 135 ohm Feedback Potentiometer – wiper Terminal M6 – 135 ohm Feedback Potentiometer – winding Where 6 wires are connected to the YBL3 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here Details of the MD20B-24 Actuator may be viewed here. N.B. The YBL3 Actuator may also have included an additional 2-wire electrical connection associated with integral Transfer Switches wired as follows :-  Terminal M7 – M1 made to M7 when YBL3 Fully Closed (24Vac) Terminal M8 – M2 made to M8 when YBL3 Fully Open (24Vac) Where external wiring is connected to YBL3 Transfer Switch Terminals M7 or M8 then an Auxiliary Switch Kit containing two S.P.C.O. Auxiliary Switches should be installed on the MD Actuator. Auxiliary Switch Kit MD-S2 (914-1061-000) Details of the MD-S2 Auxiliary Switch Kit may be viewed here. Where external wiring is connected to YBL3 Terminal M7 then the MD-S2 Auxiliary Switch Kit should be wired as follows :- Terminal S1 (Common) - connect to 24Vac power source Terminal S2 (Normally Closed) - connect to 24Vac device previously connected to YBL3 Terminal M7 Terminal S3 (Normally Open) - no connection necessary Where external wiring is connected to YBL3 Terminal M8 then the MD-S2 Auxiliary Switch Kit should be wired as follows :- Terminal S4 (Common) - connect to independent 24Vac supply Terminal S5 (Normally Closed) - no connection necessary Terminal S6 (Normally Open) - connect to 24Vac device previously connected to YBL3 Terminal M8   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here   IMPORTANT NOTE In such 6-wire installations not only will the YBL3 Valve / Actuator assembly need to be replaced but the associated Theta Potentiometric Controller and its Sensors will also need to be replaced.   CONTROLLER REPLACEMENT The Theta Potentiometric Controller may be replaced by the S-E Satchwell CSC5252 or the CSC5352 Compensator Controller. Details of the CSC Controllers may be viewed here.   SENSOR REPLACEMENT Theta 3-wire Temperature Sensors may be replaced by S-E Satchwell 2-wire Temperature Sensors compatible with the S-E Satchwell CSC 5252 or CSC5352 Compensator Controllers selected from the following as appropriate. Outside Air Temperature Sensor (STO 600) Contact Temperature Sensor (STC 600), or alternatively :- Immersion Temperature Sensor (STP 660) + Sensor Pocket Adaptor (DWA 0001) Room Temperature Sensor (STR 600) – OPTIONAL ONLY Details of the STO 600 Outside Air Temperature Sensor may be viewed here Details of the STC 600 Contact Temperature Sensor may be viewed here. Details of the STP 660 Water Temperature Sensor may be viewed here. Details of the DWA 0001 Sensor Pocket Adaptor may be viewed here. Details of the STR 600 Room Temperature Sensor may be viewed here.   ACTUATOR REPLACEMENT (3-WIRE INSTALLATION) Should only 3 wires be connected to a YBL3 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here. Details of the MD20B-24 Actuator may be viewed here. N.B. The YBL3 Actuator may also have included an additional 2-wire electrical connection associated with integral Transfer Switches wired as follows :-  Terminal M7 – M1 made to M7 when YBL3 Fully Closed (24Vac) Terminal M8 – M2 made to M8 when YBL3 Fully Open (24Vac) Where external wiring is connected to YBL3 Transfer Switch Terminals M7 or M8 then an Auxiliary Switch Kit containing two S.P.C.O. Auxiliary Switches should be installed on the MD Actuator. Auxiliary Switch Kit MD-S2 (914-1061-000) Details of the MD-S2 Auxiliary Switch Kit may be viewed here Where external wiring is connected to YBL3 Terminal M7 then the MD-S2 Auxiliary Switch Kit should be wired as follows :- Terminal S1 (Common) - connect to 24Vac power source Terminal S2 (Normally Closed) - connect to 24Vac device previously connected to YBL3 Terminal M7 Terminal S3 (Normally Open) - no connection necessary Where external wiring is connected to YBL3 Terminal M8 then the MD-S2 Auxiliary Switch Kit should be wired as follows :- Terminal S4 (Common) - connect to independent 24Vac supply Terminal S5 (Normally Closed) - no connection necessary Terminal S6 (Normally Open) - connect to 24Vac device previously connected to YBL3 Terminal M8   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here In such 3-wire installations the YBL3 Valve / Actuator assembly only will need to be replaced, while any associated Controller and Sensors may be retained.
View full article
Picard Product_Support
‎2018-09-10 03:02 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 06:27 PM

Labels:
  • Field Devices
1729 Views

What is the replacement for a Drayton Theta YBL1 Valve Body / Actuator assembly?

Issue The Drayton Theta YBL1 Valve Body / Actuator assembly is to be replaced. Environment Replacement Drayton Actuator Valve YBL1 Cause The Drayton Theta YBL1 Valve Body / Actuator assembly is obsolete. Resolution OVERVIEW The Drayton Theta YBL1 Valve Body / Actuator assembly is obsolete, and there is no purpose built replacement. The Valve Body was available in 1.1/4", 1.1/2" and 2" B.S.P. sizes and was normally installed as a mixing valve in variable temperature, constant volume, compensated heating circuits. No Valve Body / Actuator assemblies are currently available in these sizes. Details of the YB Valve Body may be viewed here.   VALVE BODY REPLACEMENT To replace the YBL1 Valve Body the following is required:- S-E SatchwellMB Valve Body of appropriate size - MB1552 (1.1/4"), MB1602 (1.1/2"), MB1652 (2") Details of the MB Valve Body may be viewed here.   ACTUATOR REPLACEMENT (6-WIRE INSTALLATION) The YBL1 Actuator normally comprised a 6-wire electrical connection enabling it to be operated by a Theta Potentiometric Controller as follows :-  Terminal M1 – Open signal Terminal M2 – Close signal Terminal M3 – Common  Terminal M4 – 135 ohm Feedback Potentiometer – winding Terminal M5 – 135 ohm Feedback Potentiometer – wiper Terminal M6 – 135 ohm Feedback Potentiometer – winding Where 6 wires are connected to the YBL1 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here. Details of the MD20B-24 Actuator may be viewed here.   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here   IMPORTANT NOTE In such 6-wire installations not only will the YBL1 Valve / Actuator assembly need to be replaced but the associated Theta Potentiometric Controller and its Sensors will also need to be replaced.   CONTROLLER REPLACEMENT The Theta Potentiometric Controller may be replaced by the S-E Satchwell CSC5252 or the CSC5352 Compensator Controller. Details of the CSC Controllers may be viewed here.   SENSOR REPLACEMENT Theta 3-wire Temperature Sensors may be replaced by S-E Satchwell 2-wire Temperature Sensors compatible with the S-E Satchwell CSC 5252 or CSC5352 Compensator Controllers selected from the following as appropriate. Outside Air Temperature Sensor (STO 600) Contact Temperature Sensor (STC 600), or alternatively :- Immersion Temperature Sensor (STP 660) + Sensor Pocket Adaptor (DWA 0001) Room Temperature Sensor (STR 600) – OPTIONAL ONLY Details of the STO 600 Outside Air Temperature Sensor may be viewed here. Details of the STC 600 Contact Temperature Sensor may be viewed here. Details of the STP 660 Water Temperature Sensor may be viewed here. Details of the DWA 0001 Sensor Pocket Adaptor may be viewed here. Details of the STR 600 Room Temperature Sensor may be viewed here.   N.B. ACTUATOR REPLACEMENT (3-WIRE INSTALLATION) Should only 3 wires be connected to a YBL1 Actuator then the Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-24 MD20B-24 (if MD10B-24 not available) Details of the MD10B-24 Actuator may be viewed here. Details of the MD20B-24 Actuator may be viewed here.   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here In such 3-wire installations the YBL1 Valve / Actuator assembly only will need to be replaced, while any associated Controller and Sensors may be retained.
View full article
Picard Product_Support
‎2018-09-10 12:13 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 02:17 AM

Labels:
  • Field Devices
1745 Views

Changing the BACnet MAC address of the Multical meters

Issue Changing the BACnet MAC address of the Multical meters Product Line Field Devices Environment Multical 601/602 with BACnet MS/TP module Cause The default BACnet MAC address of the BACnet MS/TP module has to be changed for BACnet integration to a BMS system Resolution Requires the USB Optical Eye tool (part number: MAOPTICUSB) and the software tools of the METERTOOL HCW or the Module Programmer. Both the METERTOOL HCW and the Module Programmer can be used to change the BACnet MAC address. The METERTOOL HCW is a program that installs SQL Server whilst the Module Programmer is a simple and lite program with limited functionality. So for the purpose of changing the BACnet MAC address, the procedure to change the BACnet MAC address using the Module Programmer is shown in this article.  Install the USB drivers for the USB Optical Eye tool before connecting the tool to the laptop for the first time. The Module Programmer software must be installed after the Optical Eye hardware has been recognised by the computer. Remove the protective magnet from the Optical Eye and place on the front of the meter that we want to change. The Optical Eye sits over the bottom left corner where the small window is, resting on the 2 nipples, magnetically held. Launch the Module Programmer software. If not already shown, select the Com port which says Kamstrup USB Controller. Press the Read button, this should return the Meter Type and Module Placement. If you are using the MULTICAL 602 and have fitted the module into the base of the meter Select the correct Module Type from the drop down list. Here you must select BACnet because this is what you have. Press the same Read button again, it will read out the current setting. This is the MAC address of the meter for the BACnet MS/TP network. If you are using the Schneider Electric AS/AS-P, the number must be less than 127. Use the UP/DOWN arrows to change address value or enter the number in this field manually. Press the Write button to send the new MAC address to the meter. It is best to power cycle the meter after changing any settings with this programmer tool. You can press Reset and prepare for new meter button and repeat the above steps. Read the address to verify that the new setting has been successfully written to the meter. * Contact Product Support for the software and drivers.
View full article
Picard Product_Support
‎2018-09-11 07:09 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 12:51 AM

Labels:
  • Field Devices
1706 Views

Replacement of Satchwell "AMS" series Spring Return Rotary Actuator

Issue Satchwell "AMS" series Spring Return Rotary Actuator requires replacement by S-E M700 Spring Return Linear Actuator due to obsolescence. (Actuator Wiring) Product Line Field Devices Environment Satchwell “AMS” series Spring Return Rotary Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF series Plug and Seat Valve Body.  N.B. Where a Satchwell "AMS" series Spring Return Rotary Actuator is installed on a Satchwell VV Butterfly Valve Body then NO simple Actuator replacement is available. Please refer to Replacement of Satchwell "AMS" or "AMSH" (high torque) series Spring Return Rotary Actuator Cause Obsolescence of Satchwell "AMS" series Spring Return Rotary Actuator. Resolution Replace Satchwell AMS Actuator with S-E M700 Actuator. The S-E M700 Actuator may be used to replace an existing Satchwell AMS Actuator. It should be noted however that the S-E M700 Actuator is suitable for use with 24 volt power supplies only, while the Satchwell AMS Actuator is a mains voltage device. The S-E M700 Actuator has an average power consumption of 30 VA and the use of an independent 230 / 24 volt Transformer rated 50 VA is recommended. S-E Transformer Type TR60 (341-3060-000) Please check the latest catalog for current equipment.
View full article
Picard Product_Support
‎2018-09-10 12:05 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 05:53 PM

Labels:
  • Field Devices
789 Views

TAC 200 OTP Controller replacement battery

Issue TAC 200 OTP Controller replacement battery information Product Line Field Devices, TAC Vista Environment Site with TAC 200 OTP Controller  Cause On-board battery is in need of replacement, Part number - 200-1005-000. Here is additional information: TAC 200 OTP compensator and optimiser TAC 200 OTP is a compensator and an optimiser. It controls the heating via a boiler output and a mixing valve or via two stages of gas boilers. TAC 200 OTP can be operated with or without a room sensor. The controller has an easy-to-use operator's panel and needs virtually no maintenance. TAC 200 OTP is also described in the following documents, all available in English: Data sheet TAC 200 OTP C-10-31 The data sheet contains a comprehensive specification of the controller and should be read together with the handbook (part number 0-003-1148). A brief instruction A small leaflet normally placed in a slot in the operator's panel (part number 0FL-3564). User's manual TAC 200 OTP The user's manual (part number 0FL-3563) is a description for installation and start-up, packed together with the unit. The contents are a condensed version of chapter 2 in this manual and a mounting instruction. Manuals are available in TAC 200 OTP User Guide, TAC 239W DHW User Guide. Resolution Replacement battery is 342200360 CAP, .22 F 5.5V RM5 
View full article
Picard Product_Support
‎2018-09-11 07:02 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 05:43 PM

Labels:
  • Field Devices
  • TAC Vista
896 Views

Drayton Theta YB Actuators variations

Issue What voltage do the following Drayton Theta YB Actuator variations work with and what features do they have? Environment YBL1 YBL1A YBM2 YBM2A YBL3 YBM3 Cause What voltage do the following actuators work at? What does each actuator have?  Resolution YBL1 = 24vac + Potentiometer YBL1A = 24vac + 1 Auxiliary Switch + Potentiometer YBM2 = 230Vac YBM2A = 230Vac + 1 Auxiliary Switch YBL3 = 24vac + Changeover Limit Switches (Transfer Switch) YBM3 = 230vac + Changeover Limit Switches (Transfer Switch) Note: see diagram for difference between Changeover Limit Switches and Auxiliary Switch. For the Drayton Datasheet and YBM2 and YBM2A actuator, all valve replacements and valve to actuator linkage kit part numbers, see What is the replacement for a Drayton Theta YBM2A Valve Body / Actuator assembly? For the other actuators ensure the correct voltage actuator is selected: YBL1 = MD10B-24 or MD20B-24 YBL1A = MD10B-24 or MD20B-24 YBL3 = MD10B-24 or MD20B-24 YBM3 = MD10B-230 or MD20B-230 The switch and potentiometer combinations can be replaced by the following: Changeover Limit Switches - MD-S2 Auxiliary Switch - MD-S1 Potentiometer - Belimo P140A (not a Schneider Electric part number)
View full article
Picard Product_Support
‎2018-09-10 05:11 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:21 AM

Labels:
  • Field Devices
877 Views

Replacement of Satchwell "AMS" or "AMSH" (high torque) series Spring Return Rotary Actuator

Issue Satchwell "AMS" and "AMSH" series Spring Return Rotary Actuator requires replacement by S-E M700 Spring Return Linear Actuator due to obsolescence. Product Line Field Devices Environment Satchwell "AMS" series Spring Return Rotary Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF series Plug and Seat Valve Body. Satchwell "AMSH" series Spring Return Rotary Actuator installed on Satchwell MZF or VZF series 125mm and 150mm Plug and Seat Valve Body. N.B. Where a Satchwell "AMS" series Spring Return Rotary Actuator is installed on a Satchwell VV Butterfly Valve Body then NO simple Actuator replacement is available. See Replacement of Satchwell V V series Butterfly Valve Body Cause Obsolescence of Satchwell AMS and AMSH series Spring Return Rotary Actuator. Resolution The new actuator is 24Vac and the control signal will need to be converted from 230Vac to 24Vac, this could be achieved by a transformer and 2 off 230Vac relays. The old signals switch the coils of the relays. The relay contacts switch 24Vac to the new actuator. Replace Satchwell AMS or AMSH series Spring Return Rotary Actuator with S-E M700 Spring Return Linear Actuator and Linkage Kit: AMS = M700 + L7SV (880-0126-000) Linkage Kit. N.B. M700 is available with two different spring return actions M700 - SRSU (880-0430-000) = Spring Return Spring Up          ( M700 - SRSU will CLOSE a Satchwell Valve.) M700 - SRSD (880-0440-000) = Spring Return Spring Down     ( M700 - SRSD will OPEN a Satchwell Valve.) Should the Satchwell AMS series Actuator include a wired Auxiliary Switch then the following S-E M700 Actuator specifications which include 2 independent 24 volt 4 amp AC-1 rated SPDT Auxiliary End Point Switches should be considered as appropriate: M700 - S2 - SRSU (880-0431-000) M700 - S2 - SRSD (880-0441-000) Alternatively Auxiliary Switch Pack S2 (880-0104-000) - Two independent 24 volt 4 amp AC-1 rated SPDT Auxiliary End Point Switches may be purchased separately permitting local installation. Particular care should be taken when selecting a TAC Forta M700 Spring Return Actuator to replace an existing Satchwell AMS Spring Return Actuator. Please refer to Replacement of Satchwell "AL..S" series Spring Return Linear Actuator. Please check the latest catalog for current equipment.
View full article
Picard Product_Support
‎2018-09-10 12:04 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:03 AM

Labels:
  • Field Devices
999 Views
  • « Previous
    • 1
    • 2
    • 3
    • 4
    • …
    • 36
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc