Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

WorkPlace Tech Editor Ribbon Fails to Load When Launching WorkStation or WorkPlace Tech

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • WorkPlace Tech Editor Ribbon Fails to Load When Launching WorkStation or WorkPlace Tech
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2031 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

WorkPlace Tech Editor Ribbon Fails to Load When Launching WorkStation or WorkPlace Tech

RandyDavis Champion
‎2022-06-23 12:23 PM

Last Updated: CraigEl Champion ‎2026-02-22 11:55 PM

Issue

When launching WorkPlace Tech or the WorkPlace Tech Editor inside EcoStruxure Building Operation (EBO), the WorkPlace Tech ribbon does not appear or displays an error indicating that the COM add‑in failed to execute.

Product Line

TAC IA Series, EcoStruxure Building Operation

Environment

  • Building Operation Workstation (Workplace Tech Editor)
  • I/A Series WorkPlace Tech

Cause

Smartware Studio 360 release 5.1.540 and later contains a 64-bit version of the Microsoft Access database.  It was modified to allow for installation with either Office 32-bit or 64-bit. 

Prior to EBO 7.0.2, WorkPlace Tech Editor required 32‑bit Visio, and Microsoft generally blocks mixed‑bit Office components on the same PC.
This mismatch could cause the WorkPlace Tech ribbon’s COM add‑in to fail to load at startup.

WorkPlace Tech 5.11 and EBO 7.0.2, WorkPlace Tech Editor now supports both 32‑bit and 64‑bit Visio. However:

  • Systems running WorkPlace Tech versions prior to 5.10 or EBO versions prior to 7.0.2 still require 32‑bit Visio
  • Installing or retaining a mismatched Access Database Engine can still cause COM add‑in load failures

Resolution

For EBO 7.0.2 and later

  1. Ensure your installed version of Visio (32‑bit or 64‑bit) is supported.
    • EBO 7.0.2 WorkPlace Tech Editor automatically detects bitness and configures accordingly.
  2. If the ribbon still fails to load:
    • Uninstall conflicting or leftover Microsoft Access Database Engine entries from Programs and Features

      AccessDB.gif

    • Reinstall the Access Database Engine bundled with Smartware Studio 360
  3. Restart WorkStation and verify the WPT Editor ribbon loads correctly.

For EBO versions prior to 7.0.2

  1. Confirm that 32‑bit Visio is installed.
    • 64‑bit Visio is not supported for older WPT Editor versions.
  2. Uninstall the 64‑bit Microsoft Access Database Engine if present.
  3. Reinstall Smartware Studio 360’s required components.
  4. Relaunch WorkPlace Tech or WorkStation.

Notes (Important from EBO 7.0.2 Release Notes)

  • EBO WorkPlace Tech Editor 7.0.2 now supports 64‑bit Visio, including Visio 2024.
  • Both standalone WorkPlace Tech 5.11 and EBO WorkPlace Tech Editor 7.0.2 can be upgraded to 64‑bit Visio.
  • Installation of WorkStation with WPT Editor will auto-detect whether Visio is 32‑bit or 64‑bit and adjust accordingly.
  • PCs requiring prior versions of EBO WorkPlace Tech Editor must continue using 32-bit Visio.
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • CraigEllis26
  • RandyDavis22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore