Issue
When running I/NET Seven rev. 2.15, in the I/O Server editor, the "CCTV" button is Grayed out
Environment
- I/NET
- DVR
- CCTV
Cause
Errors occurred during installation
Resolution
CCTV new DLL file Install Process from I/NET Seven CD (Rev 2.14 and above)
-
Load the I/NET Seven CD in the CD drive unit (D:\). The CD will try to auto-load, cancel that install. Then go to this location on the CD
D:\Support\RVCTL_DLL\Rev 3.6.0.1 - Copy the three DLL files (ijl15.dll, rvctl.dll & rview.dll) from the CD. Then paste them into this location C:\Program Files\INET Seven
-
You must register one of the copied DLL files into the Windows Registry. Please follow these steps:
- Open a “CMD” prompt. Use Start>Run, type cmd and select OK
-
Type the following:
Cd\
Cd \Program Files\INET Seven
Regsvr32 rvctl.dll -
You will see a message box with the message “DllRegisterServer in rvctl.dll succeeded” - The CCTV Button in the I/O Server is now available to be used for integral DVR’s