Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

What to Validate After Upgrading EcoStruxure Building Operation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What to Validate After Upgrading EcoStruxure Building Operation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
215 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What to Validate After Upgrading EcoStruxure Building Operation

RobertAndriolo Champion
‎2026-06-14 09:19 PM

on ‎2026-06-14 09:19 PM

Issue

  • No standard test or performance validation procedure is available.
  • Each EcoStruxure Building Operation system requires a site-specific approach based on its configuration.
  • Guide on what to check after EBO / Windows updates

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation
  • Enterprise Central (EC)
  • Enterprise Server (ES)
  • Automation Server (AS)
  • WebStation
  • WorkStation
  • PostgreSQL / Timescale Database (if used)
  • SQL Server (if used)
  • External databases (if used)
  • Third-party interfaces (if used)

Cause

When validating system performance (for example, after an upgrade or Windows updates), a standard procedure may be expected; however, EcoStruxure Building Operation systems differ significantly in server roles, databases, and integrations, requiring a site-specific validation approach.

Resolution

Use the following structured approach to create and execute a site-specific performance validation procedure for EcoStruxure Building Operation systems.


1. Prepare Baseline (Before Changes)

Capture current system performance to enable comparison.

  • Record CPU usage (Enterprise Central / Enterprise Server)
  • Record memory usage (Enterprise Central / Enterprise Server)
  • Measure network latency between Enterprise Central / Enterprise Server and Automation Servers
  • Capture system load indicators:
    • Active alarms
    • Trend logs
    • Connected users
  • Measure user experience:
    • WebStation load times
    • WorkStation login times
    • Graphics load performance

2. Perform Immediate Post-Change Validation

Confirm the system is operational after updates or changes.

  • Confirm all servers are online
    • Expected result: No offline or red cross states
  • Verify licenses are valid
  • Confirm all required services are running
  • Validate communication between:
    • Enterprise Central
    • Enterprise Server
    • Automation Servers

3. Inspect Logs and System Health

Identify early warnings or failures.

  • Review Windows Event Viewer
  • Review EcoStruxure Building Operation logs
  • Check for:
    • Service failures
    • Certificate issues
    • Database warnings

4. Verify Core Functionality

Ensure key features are operating correctly.

  • Verify alarm generation and acknowledgment
  • Confirm trend data is being recorded
  • Validate graphics loading and bindings
  • Test access via:
    • WorkStation
    • WebStation
    • Mobile clients (if applicable)

5. Validate Performance

Assess system responsiveness and resource usage.

  • Validate WebStation responsiveness
    • Expected result: Acceptable page load and navigation times
  • Monitor CPU usage trends
  • Monitor memory usage trends
  • Check database performance
    • Trend retrieval speed
    • Alarm list loading
  • Verify network latency
  • Confirm communication stability
    • Expected result: No intermittent offline or red cross states

6. Perform Soak Testing (24–72 Hours)

Validate stability under normal operating conditions.

  • Operate the system under typical load
  • Monitor:
    • CPU stability
    • Memory trends
    • Communication reliability
  • Confirm no gradual performance degradation

7. Confirm Regression Checks

Ensure no functional or performance regression.

  • All servers remain online
  • No communication drops
  • WebStation operates reliably
  • Trends and alarms function correctly
  • Reports generate successfully

8. Define Rollback Plan

Prepare recovery actions if issues are identified.

  • Define rollback criteria:
    • Persistent communication issues
    • Sustained high resource usage
    • Performance degradation
    • Database latency issues
  • Define rollback method:
    • Restore from backup
    • Revert to the virtual machine snapshot

9. Document and Sign Off

Capture results and confirm validation completion.

  • Record system version and Windows update details
  • Document test results and identified issues
  • Obtain stakeholder or customer sign-off

Reference Materials

Use relevant documentation to support the validation approach:

 

  • EcoStruxure Building Management Overview
  • Architectural Guidelines 
  • Backup and Restore Overview
  • Information Technology System Planning Guide
  • Hardening Guidelines Overview
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo26
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore