WPT BACnet IP Tool Cannot Discover MNB MS/TP Devices Behind ENC
  • WPT BACnet IP Tool Cannot Discover MNB MS/TP Devices Behind ENC
  • CraigEl
    CraigEl
  • RyanSuar
    RyanSuar
‎2018-09-06 09:00 AM
Last Updated: CraigEl Champion ‎2026-01-15 03:55 PM
WorkPlace Commissioning Tool (WPT) configured for BACnet IP cannot discover MNB MS/TP field devices that are connected through an I/A Series G3 Enterprise Network Controller (ENC).
TAC IA Series
  • I/A Series G3 ENC
  • BACnet Integration (BACnet IP to BACnet MS/TP)
  • MNB Series Controllers connected via MS/TP
BACnet routing within the ENC station is not enabled. When routing is disabled, the ENC does not pass BACnet MS/TP device information to BACnet IP, preventing WPT from discovering downstream MNB controllers.
  1. Open the ENC station in Workbench.
  2. Navigate to:
    BacnetNetwork > Bacnet Comm > Network
  3. Set Routing Enabled = true.
  4. Save changes and allow the station to restart communication.
  5. Re-run BACnet device discovery in WPT.
    The MS/TP-connected MNB devices should now be discoverable over BACnet IP.