Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Using Digital Point Cards (DPC‑3‑1 / DPC‑3‑2) with a Network 8000 MicroZone II Controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using Digital Point Cards (DPC‑3‑1 / DPC‑3‑2) with a Network 8000 MicroZone II Controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2269 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using Digital Point Cards (DPC‑3‑1 / DPC‑3‑2) with a Network 8000 MicroZone II Controller

Product_Support
‎2018-09-07 04:19 AM

Last Updated: CraigEl Champion ‎2026-03-02 10:37 PM

Issue

Guidance on how to configure and use digital point cards with a Network 8000 MicroZone II controller.

Product Line

TAC IA Series

Environment

  • Network 8000 MicroZone II controller
  • Digital Point Card

Cause

MicroZone II controllers do not natively interpret the digital input signals from DPC‑3‑1 and DPC‑3‑2 cards. A custom application file is required for these cards to function correctly.

Resolution

To enable digital input support on a MicroZone II controller:

  1. Download and load the custom application file
    Use the attached application file 1‑DPC3.MZ2. This file enables the controller to correctly process signals from the DPC‑3‑1 and DPC‑3‑2 digital point cards.

  2. Refer to the attached technical bulletin
    The attached TB01‑26 document provides detailed information on:

    • Supported digital point card models
    • Hardware installation
    • Wiring considerations
    • Application behavior and configuration steps
  3. Compatibility note

    • DPC‑3‑1 and DPC‑3‑2 are the only digital point cards supported by the MicroZone II controller.
    • DPC‑5 series cards were designed for MNL and MNB controllers. They can be used with the DUI Expander Object, but not with standard MicroZone II applications.

(Note: The DPC-5 series cards were designed for the MNL and MNB controllers.  They are compatible with the DUI Expander Object available for both controller lines.)

Labels (1)
Labels:
  • TAC IA Series
Attachments
1-DPC3.zip
Tags (3)
  • Find more articles tagged with:
  • 3189
  • CraigEllis23
  • CraigEllis26
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore