Users and User Groups Are Not Visible Across Server Tiers in a Multi-Server EcoStruxure BMS System
Building Automation Knowledge Base
Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
In a multi-server EcoStruxure BMS system, users and user groups created on higher-tier servers are not visible on lower-tier servers.
Examples include:
User groups or users created in Enterprise Central (EC) are not visible on Enterprise Servers (ES).
User groups or users created in Enterprise Servers are not visible on Automation Servers (AS).
Bound values, such as users and user groups, cannot be selected across domain boundaries.
Product Line
EcoStruxure Building Operation
Environment
Enterprise Central (EC)
Enterprise Server (ES)
Automation Server (AS)
Multi-server EcoStruxure Building Operation systems
Domain-based security architecture
Cause
This behavior is by design.
In EcoStruxure Building Operation, users and user groups are scoped to the domain in which they are created. Servers do not automatically expose user or group objects across domain boundaries, even when they are part of the same server hierarchy.
A field server is aware of the Enterprise Server to which it belongs, and an Enterprise Server is aware of its Enterprise Central and field servers. However, visibility of users and user groups remains limited to the applicable domain.
As a result:
Users and groups defined in an EC domain are not directly visible on an ES.
Users and groups defined in an ES domain are not directly visible on an AS.
User and group objects are not intended to be visible across server tiers.
Resolution
Manage domains, users, and user groups within the appropriate server tier and domain.
Recommended domain structure:
Add Enterprise Servers to the Enterprise Central domain.
Add field servers to the Enterprise Server domain.
Manage users and user groups within the domain where they are intended to be used.
Use domain membership consistently throughout the server hierarchy.
This architecture ensures that each server tier manages its own domain users and groups locally. Limited visibility of user and group objects between server tiers is expected behavior and does not indicate a communication or replication issue.