Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Understanding the FILE Section in a LonWorks XIF File

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Understanding the FILE Section in a LonWorks XIF File
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4480 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Understanding the FILE Section in a LonWorks XIF File

Product_Support
‎2018-09-11 03:06 PM

Last Updated: CraigEl Champion ‎2026-03-01 08:09 PM

Issue

When troubleshooting LonWorks devices, configuration parameters (SCPTs and UCPTs) stored inside the FILE section of a XIF file can be difficult to interpret. The FILE template and value blocks contain encoded definitions that determine how device configuration data is stored and retrieved. Without understanding this structure, diagnosing NCI-related issues becomes challenging.
 

For information regarding NCI's that are not part of a FILE definition, refer to Understanding the NVVAL part of a XIF file

Product Line

EcoStruxure Building Operation, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC Vista

Environment

  • LonWorks Networks
  • XIF files containing FILE template and FILE value sections
  • Devices where configuration parameters (CPTs) are part of a FILE block rather than NVVAL

Cause

Certain configuration parameters (SCPT/UCPT values) are stored in the FILE section of a XIF file.

FILE template 0 2
"1.1;"
"2,23.24.25.26.27.28.29.30.31.32.33.34.35.36.37.41.42.43.45.46,0\x80,49,2;"
"1,1,0\x80,60,12;"
"1,1,0\x80,52,2;"
"2,0.2.3.5.6.7.8.9.10.16.17.18.19.20.21,0\x80,48,2;"
"1,0,0\x80,17,31;"
"1,1,0\x80,34,2;"
"1,1,0\x80,23,2;"
"1,1,0\xA4,169,1;"
"1,1,4\x80,3,8;"
"1,1,4\x80,5,17;"
"1,1,3\x80,1,2;"
"1,1,4\x80,4,9;"
"1,1,4\xA4,13,1;"
"1,1,4\xA4,14,1;"
"1,1,4\xA4,15,1;"
"1,1,4\xA4,16,1;"
"1,1,4\xA4,17,1;"
"1,1,4\x80,18,1;"
"1,1,0\x80,42,2;"
"1,1,0\x80,36,2;"
"1,1,0\x80,193,2;"
"1,1,4\x80,8,2;"
"1,0,3\x80,2,2;"
"1,0,0\x84,165,1;"
"1,0,0\xA4,166,1;"
"1,1,6\xA4,2,8;"

FILE value 1 1 116
0x0B, 0xB8, 0x09, 0x1D, 0x09, 0xFB, 0x0B, 0x80, 0x08, 0x77, 0x07, 0x98, 0x06, 0x13, 0x00, 0x02,
0x23, 0x28, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00,
0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00,
0x00, 0x00, 0x78, 0x7F, 0xFF, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00,
0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00,
0x00, 0x80, 0x80, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x00, 0x01, 0x00, 0x00, 0x00, 0x00, 0x00,
0xFF, 0xFF, 0x7F, 0xFF, 0x7F, 0xFF, 0x13, 0x88, 0x00, 0x00, 0x02, 0x0B, 0x00, 0x00, 0x00, 0x00,
0x00, 0x00, 0x00, 0x00

This section can appear cryptic because:

  • CPT definitions use multi-field encodings.
  • Flags (e.g. device-specific, read-only, manufacturing-only) are encoded as hex.
  • Byte offsets and lengths are defined indirectly via the template.
  • Vector lengths must be interpreted via combined fields.
  • The value block is a raw byte array that must be decoded using the template.

These factors make interpreting configuration values difficult without a breakdown of the template format.

Resolution

The FILE section contains two parts that work together: FILE template and FILE value.


1. FILE Template (Structure Definition)

The FILE template defines how each CPT is stored.

Example:

"1,1,0\x80,60,12;"

Each entry follows the format:

"A,B,C\xDD,E,F,G;"

Field meanings

  • A – Ownership
    • 0 device
    • 1 function block
    • 2 network variable
  • B – Function block or variable index
  • C – Type selector
    • 0 SCPT
    • 3,4,5,6 UCPT
  • DD – Handling flags (bitfield)
    • a: Always 1
    • c: Device-specific
    • d: Manufacturing-only
    • e: Reset required after change
    • f: Read-only
    • g: Device must be offline to write
    • h: FB must be disabled to write
  • E – CPT index
  • F – CPT byte length
  • G – Optional vector multiplier

Example interpretation:

"1,1,0\x80,60,12;"
  • CPT belongs to FB 1
  • Standard CPT (SCPT)
  • No special flags set (0x80)
  • Index 60 → SCPTsetPnts (based on SNVT_temp_setpt)
  • Length 12 bytes

2. FILE Value (Encoded Data Block)

The FILE value section contains the raw bytes for all CPTs defined in the template.

Example:

FILE value 1 1 116
0x0B, 0xB8, 0x09, 0x1D, ...
  • First two numbers identify a value section.
  • The optional length (116 bytes) should match total CPT byte requirements.

Each CPT’s data must be decoded using:

  • Its offset (from template sequence)
  • Length (field F × optional G)
  • SNVT/SCPT resolution rules

Example decoding:

CPT entry:

"2,23.24...45.46,0\x80,49,2;"

Refers to SNVT_time_sec (index 49).
First two bytes:

  • 0x0B 0xB8 = 101110111000 (binary) = 3000 decimal → 300.0 seconds.

Example: SCPTsetPnts (12 bytes)

"1,1,0\x80,60,12;"

SNVT_temp_setpt values decoded:

Bytes Decimal Adjusted Member
09 1D 2333 23.33 occupied_cool
09 FB 2555 25.55 standby_cool
0B 80 2944 29.44 unoccupied_cool
08 77 2167 21.67 occupied_heat
07 98 1944 19.44 standby_heat
06 13 1555 15.55 unoccupied_heat

Troubleshooting Tips

  • Verify the total byte length in FILE value matches all template-defined CPT lengths.
  • Confirm SCPT/UCPT index maps to correct SNVT type.
  • If TAC Vista cannot import CPTs linked to NVs, update entries:
    "2,..." → "1,1,..."
Labels (5)
Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC Vista
Attachments
Tags (3)
  • Find more articles tagged with:
  • 16923
  • CraigEllis26
  • Peter Larsen20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore