Unable to Download Controller Operating Files (e.g., pntfle.rec, lookup.rec) into a BAS Outstation
  • Unable to Download Controller Operating Files (e.g., pntfle.rec, lookup.rec) into a BAS Outstation
  • CraigEl
    CraigEl
  • MaximeLaudren
    MaximeLaudren
  • DavidChild
    DavidChild
‎2021-01-31 08:35 PM
Last Updated: Administrator CraigEl Administrator ‎2025-11-02 11:40 PM
Attempts to download controller operating files into a BAS outstation fail when using a terminal connected to Port 2 (e.g., an engineer’s laptop).
Satchwell BAS & Sigma
  • Satchwell BAS2000
  • Satchwell BAS2800
  • Satchwell BAS2800+
The failure occurs because the terminal number configured in the BAS setup does not match the terminal number assigned to Port 2 of the outstation. This mismatch prevents successful communication and file transfer.
  1. Verify Terminal Configuration:
    • Perform a Commstats (F3) on the node to display a list of devices and their assigned numbers per port.
    • Alternatively, check the site node file to identify the terminal number configured for Port 2 of the outstation.
  2. Identify Terminal Assignment:
    • Look for entries with the letter “T” followed by a device number. This indicates a terminal has been assigned.
  3. Update BAS Setup:
    • In the BAS setup page, update the terminal number to match the one identified in step 1.
    • Save and exit the BAS setup.
  4. Retry File Download:
    • Reopen BAS and attempt to download the controller operating files again.
Additional Notes
  • This issue only affects outstation files, not node files.