Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Troubleshooting License Entitlement Assignment for AS-B and AS-P in EBO 2022 (4.0) and Later

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Troubleshooting License Entitlement Assignment for AS-B and AS-P in EBO 2022 (4.0) and Later
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
1116 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Troubleshooting License Entitlement Assignment for AS-B and AS-P in EBO 2022 (4.0) and Later

CraigEl Champion
‎2025-11-26 04:44 PM

Issue

Users encounter problems assigning entitlement licenses to AS-B and AS-P controllers in EcoStruxure Building Operation (EBO) 2022 (4.0) and later using Device Administrator.

Common symptoms include:

  • Entitlement assignment fails.
  • The assignment option is greyed out.
  • No license product appears after the entitlement is added.
  • "No valid license found" is displayed.
  • The entitlement is visible in Device Administrator but cannot be assigned to the controller.
  • A newly purchased license appears incompatible with the controller.

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation 2022 (4.x) to 2024 (6.x)
  • Device Administrator
  • Building Operation Automation Server
    • AS-P
    • AS-P-NL
    • AS-P-S
    • AS-P-NLS
    • AS-B
    • AS-B-P Family

Cause

Starting with EBO 2022 (4.0), Schneider Electric introduced a scalable licensing model that decouples hardware and software.

As a result, two different licensing models exist for AS-P and AS-B controllers:

  • Older controller hardware requires an Upgrade License.
  • Newer controller hardware requires a Bundle License.

If an Upgrade License is purchased for hardware that requires a Bundle License, or a Bundle License is purchased for hardware that requires an Upgrade License, Device Administrator will not allow the entitlement to be assigned to the controller.

This is the most common cause of entitlement assignment failures in EBO 2022 and later.

Resolution

Automation Server License Assignment Guide
I cannot assign my AS-P or AS-B license
Step 1
Find the Automation Server hardware part number from the controller properties or the controller label.
Do not rely only on the model name (AS-P or AS-B). The required license depends on the hardware part number.
↓
Match your hardware to the correct license
AS-P Upgrade

Hardware
  • SXWASPXXX10001
  • SXWASPXXX10002
  • SXWASPXXX1S001
Use an AS-P Upgrade License
  • SXWSWASPUPxxxx
AS-P Bundle

Hardware
  • SXWASPSBX10001
  • SXWASPSBX10002
  • SXWASPSBX1S002
Use an AS-P Bundle License
  • SXWSWXBUxxxxxx
AS-B Upgrade

Hardware
  • SXWASB24X10001
  • SXWASB24H10001
  • SXWASB36X10001
  • SXWASB36H10001
Use an AS-B Upgrade License
  • SXWSWASBUPxxxx
AS-B Bundle

Hardware
  • SXWASB24PX10001
  • SXWASB24HP10001
  • SXWASB36PX10001
  • SXWASB36HP10001
Use an AS-B Bundle License
  • SXWSWXBBUxxxxx
⚠ License Mismatch
If the purchased license does not match the Automation Server hardware, Device Administrator will not allow the entitlement to be assigned.
Purchased the wrong license?
If the entitlement has not been consumed or assigned, contact your local Schneider Electric Order Entry or Customer Care team to discuss returning the unused entitlement and purchasing the correct license.

AS-P Hardware Compatibility

Hardware Part Number Model Required License Type
SXWASPXXX10001 AS-P AS-P Upgrade License
SXWASPXXX10002 AS-P-NL AS-P Upgrade License
SXWASPXXX1S001 AS-P-SMK AS-P Upgrade License
SXWASPSBX10001 AS-P-S AS-P Bundle License
SXWASPSBX10002 AS-P-NLS AS-P Bundle License
SXWASPSBX1S002 AS-P-NLS-SMK AS-P Bundle License

Examples of AS-P Upgrade License Part Numbers

  • SXWSWASPUP30SA
  • SXWSWASPUP30SD
  • SXWSWASPUP30EN
  • SXWSWASPUP30FU
  • SXWSWASPUP40SA
  • SXWSWASPUP40SD
  • SXWSWASPUP40EN
  • SXWSWASPUP40FU

Examples of AS-P Bundle License Part Numbers

  • SXWSWXBU0000SA
  • SXWSWXBU0000SD
  • SXWSWXBU0000EN
  • SXWSWXBU0000FU

AS-B Hardware Compatibility

Hardware Part Number Model Required License Type
SXWASB24X10001 AS-B-24 AS-B Upgrade License
SXWASB24H10001 AS-B-24H AS-B Upgrade License
SXWASB36X10001 AS-B-36 AS-B Upgrade License
SXWASB36H10001 AS-B-36H AS-B Upgrade License
SXWASB24PX10001 AS-B-24-P AS-B Bundle License
SXWASB24HP10001 AS-B-24H-P AS-B Bundle License
SXWASB36PX10001 AS-B-36-P AS-B Bundle License
SXWASB36HP10001 AS-B-36H-P AS-B Bundle License

Examples of AS-B Upgrade License Part Numbers

  • SXWSWASBUP30SD
  • SXWSWASBUP30FU
  • SXWSWASBUP40SD
  • SXWSWASBUP40FU

Examples of AS-B Bundle License Part Numbers

  • SXWSWXBBU010SD
  • SXWSWXBBU050FU

Example License Mismatch

Controller Hardware:

SXWASB24X10001 (AS-B-24)

Correct License Type:

AS-B Upgrade License

Incorrect License Type:

SXWSWXBBU050FU (AS-B Bundle License)

Result:

The entitlement will be visible in Device Administrator but cannot be assigned to the controller.


Additional Information

  • Original AS-P and AS-B hardware models require Upgrade Licenses even when running EBO 2022, EBO 2023, EBO 2024, or EBO 6.x.
  • AS-P-S, AS-P-NLS, AS-P-NLS-SMK, and AS-B-P family hardware use the scalable licensing model and require Bundle Licenses.
  • Refer to the latest Part Number Summary and Hardware & Software Matrix when purchasing hardware or licenses.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • CraigEllis25
  • CraigEllis26
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore