Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Suppressing or Managing “A Log Sample Was Missed” System Alarms in EcoStruxure Building Operation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Suppressing or Managing “A Log Sample Was Missed” System Alarms in EcoStruxure Building Operation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Siddharth_G
    Siddharth_G

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
1323 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Suppressing or Managing “A Log Sample Was Missed” System Alarms in EcoStruxure Building Operation

CraigEl Champion
‎2026-02-26 08:21 PM

Last Updated: RobertAndriolo Champion ‎2026-03-02 04:46 PM

Issue

Operators see excessive “A Log Sample Was Missed” system alarms in EcoStruxure Building Operation (EBO).
These alarms can flood the Alarm Viewer during device offline events, power outages, or heavy system load.
Users want to hide, filter, or suppress these alarms without losing visibility of higher‑priority alarms.

 

Product Line

EcoStruxure Building Operation

 

Environment

Building Operation WorkStation and Webstation

 

Cause

“A Log Sample Was Missed” alarms occur when:

  • A device or interface goes offline
  • The system is busy, impacting sample collection
  • The log configuration is too frequent or uses small COV thresholds
  • Power outages cause large numbers of logs to be missed simultaneously
  • Existing system alarms are not yet reprocessed after Alarm Decorations are applied

These alarms are system alarms and cannot be disabled at the log object itself.

 

Resolution

 

Option 1 — Disable Trend Log when Device is Offline 

To prevent the “Log Sample Was Missed” alarm entirely, configure the Activation variable property of the Trend Log.

Steps

  1. Open the Trend Log → Basic tab
  2. Find Activation
  3. Bind Activation to one of the following (in priority order)
  • DeviceChanged property of the device
  • Any property that reliably indicates online/offline
    Activation_Trend.png

Expected behavior:

  • When device goes offline → Activation = False
    Trend collection stops → No “log missed” alarms
  • When device comes online → Activation = True → Logging resumes

Note:

Trend log Activation does not accept certain binding types (e.g., Device Status) in some EBO versions. If a property is not accepted, use DeviceChanged instead.


Option 2 — Hide or Manage the Alarm Using Alarm Decorations 

Alarm Decorations can override default behavior for system alarms and automatically move these alarms to the Hidden Alarms section.

Steps (WorkStation):

  1. Open WorkStation and navigate to:
    System → Alarms → Alarm Decorations

    AlarmDecoration1.png

  2. Click the “+” icon to add a new Decoration Rule.

  3. Create a rule targeting the system alarm:

    • Field: System Alarm ID
    • Condition: Equals
    • Value: The ID for “Log Sample Missed”

      Filters.png

  4. Set Decoration Actions:

    • Auto-hide Override: True
    • Priority Override: (Optional) lower to non-operational priority
    • Category Override: (Optional) assign to a “System Alarms” category for filtering

      AutoHide.png

  5. Apply the rule.

  6. Important: Existing alarms will not move until they are reprocessed.
    Do one of the following:

    • Acknowledge existing alarms
    • Wait for the alarm to occur again naturally
    • Trigger a new test condition to generate a fresh sample-missed event

Expected result: New “Log Sample Missed” alarms appear in Hidden Alarms, not in the main alarm list.


Option 3 — Use Standard Alarm Filters (Works in both WorkStation and WebStation)

Some versions (e.g., EBO 4.0) may not show an Exclude option in Custom Alarm Views, but the standard alarm filter still supports filtering.

Steps (WorkStation)

  1. Open the standard alarm viewer.
  2. Right‑click inside the alarm list area.
  3. Select Add Filter.
  4. Choose Exclude for System Alarm ID.
  5. Enter the ID for “Log Sample Missed”.
  6. Apply and save.

    Alarm-Exclude.png

Webstation 

In WebStation’s filter dialog, if wanting to hide/ exclude alarms within a specific Priority range, select “Not between”.
Because,
“Between” = show only alarms inside the range
“Not between” = show only alarms outside the range (i.e., exclude that range)

alarm webstation.png
The above steps hides the alarms from this view without requiring Alarm Decorations.


Option 4 — Disable Individual Alarms Manually

  1. When the alarm appears, right‑click → Disable.
  2. The specific log’s alarm will no longer reappear.

Option 5 — Reduce Log Load to Prevent the Alarm Triggering

If alarms occur frequently for many logs:

  1. Reduce the log sampling frequency.
  2. Increase COV thresholds.
  3. Investigate field device communication issues.
  4. Check for overloaded AS or network issues.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • Siddharth_G26
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore