Issue
SpaceLogic MS/TP controllers connected through a BACnet/IP to MS/TP router are discovered by the EcoStruxure Building Operation server, but cannot be hosted directly under the BACnet/IP Network. Attempting to host a controller reports
Invalid operation - Operation failed, the target container cannot contain this object.Product Line
EcoStruxure Building Operation
Environment
- Building Operation Automation Server Premium (AS-P)
- SpaceLogic RP-C controller
- BACnet/IP to MS/TP router
Cause
MS/TP controllers located behind a BACnet/IP to MS/TP router cannot be hosted directly under the BACnet/IP Network. The remote MS/TP network must first be represented in the EcoStruxure Building Operation BACnet database.
Resolution
- Add the BACnet/IP to MS/TP router as a BACnet device.
- Under the router, add a Remote Network.
- Configure the Remote Network with the BACnet network number used by the router's MS/TP network.
- Add the MS/TP controllers under the Remote Network.
Confirm that the controllers come online under the Remote Network.