Issue
The Server Archive Status in Building Advisor may show statuses such as Out of Date or None Available.
These statuses can sometimes be interpreted as indicating a problem. However, the status reflects the availability and age of the server archive at the time of the archive upload and does not by itself indicate a connectivity issue.
This article clarifies what the displayed archive status means and when further investigation may be appropriate.
Product Line
EcoStruxure Building Advisor
Environment
- Building Advisor Portal
- EcoStruxure BMS
- Server Archive Status
Cause
Server archive files are periodically uploaded and the Server Archive Status reflects the archive information available at the time of the upload.
The following statuses describe the state presented in the UI:
- Out of Date indicates that the available server archive had not been updated before the latest archive upload.
- None Available indicates that no server archive was available for that server at the time of the upload.
An individual occurrence of either status does not necessarily indicate a problem. The status should therefore be interpreted in the context of subsequent archive updates.
Resolution
No corrective action is required solely because Out of Date or None Available is displayed.
First, check whether the status changes following subsequent archive updates.
Further investigation is appropriate when Out of Date or None Available continues to be reported across subsequent updates.
If the condition persists:
- Review the server associated with the reported status.
- Confirm that scheduled server backups are enabled.
- Confirm that the scheduled backups are completing successfully.
- Review the Last Upload information to determine whether newer archive information is being received.
- After a subsequent archive update, verify whether the Server Archive Status has returned to the expected state.
If None Available was associated with devices not being displayed in the Site Architecture tree, verify after the next successful archive update that the devices are displayed as expected.
For further information refer to the Server Archive States section of the BMS Connectivity - Ongoing Updates Webhelp topic.