Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Security Expert – Allegion Integration and Dynamic Authority Control Support

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Security Expert – Allegion Integration and Dynamic Authority Control Support
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
129 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Security Expert – Allegion Integration and Dynamic Authority Control Support

Alan_Wood Leader
‎2026-02-26 02:38 PM

Issue

Dynamic Authority Control is available on Allegion Engage LE wireless locks, but this feature is not supported when the locks are integrated with EcoStruxure Security Expert. This leads to confusion about access behavior during communication loss.

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert
  • Allegion Engage LE Wireless Locks
  • Allegion Engage Gateway (GWE)

Cause

Allegion Engage LE locks include a built‑in mechanism for storing Users and Access Levels locally. However, the current Security Expert integration does not utilize or support Allegion's Dynamic Authority Control.
Instead, the integration treats Engage LE locks as smart readers, with all authentication, access logic, and user database management performed entirely by the Security Expert SP‑C controller.

Because local credential storage is not used in this mode, the locks cannot make independent access decisions when communication with the SP‑C is lost.

Resolution

Per Application Notes 182 and 272, Dynamic Authority Control is not supported when using Allegion Engage LE locks with the Security Expert integration.

When integrated, the system operates as follows:

Normal Operation

  • Engage LE locks act as smart readers
  • All access control logic resides on the SP‑C controller
  • Cardholder data is stored centrally on the SP‑C

Event Behavior

  • An “Allegion 485 Reader Offline” event is generated when communication is lost
  • No door events are generated or cached while the Allegion interface module is offline

Communication Loss Scenarios

Condition Result
SP‑C loses communication with the server Card access continues. The SP‑C uses its local cache and maintains control.
GWE loses communication with the SP‑C Card access fails. The lock cannot authenticate because it does not store credentials in this integration mode.

 

Note: Ensure that the mobile app is disconnected from the lock before connecting to the SPC.
The mobile app and the SPC cannot be connected at the same time.

Because Dynamic Authority Control is not supported, there is no configuration option in Security Expert to store credentials locally on the Engage LE locks.

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • AlanWood26
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore