Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SQL Server using high memory on Security Expert system

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SQL Server using high memory on Security Expert system
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AdamSteele
    AdamSteele

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
189 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SQL Server using high memory on Security Expert system

AdamSteele Champion
‎2026-06-15 07:53 PM

on ‎2026-06-15 07:53 PM

Issue

SQL Server is observed consuming almost all of the memory on a system configured with 64GB RAM, with memory utilization reaching around 85–94%. This appears high compared to the recommended 32GB baseline for Security Expert.

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert Client Server
  • SQL Server

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

Microsoft SQL Server is designed to aggressively consume available system memory to optimize performance when the max server memory limit is not explicitly configured. On Security Expert systems with higher RAM capacity, this behavior can appear abnormal when compared to minimum sizing guidance, even though it is expected SQL Server operation.

Resolution

This behavior is normal and expected.

  • SQL Server is designed to aggressively use available memory to maximize performance (for example, buffer pool and query plan cache). If the max server memory setting is not configured, SQL Server can consume approximately 80–95% of available RAM and will only release memory when the operating system is under pressure.
  • The 32GB RAM recommendation defined in the SX-SRVR Security Expert - Client Server - Installation Guide should be considered a minimum baseline, not a maximum limit. Larger systems with more controllers, events, integrations, and historical data may require significantly more memory.
  • If it is necessary to limit SQL Server memory usage (for example, to 70–80%), configure the max server memory setting accordingly. For example, on a 64GB server, setting the limit to approximately 48GB allows sufficient RAM for the operating system.
  • If performance degrades after applying a memory limit, this indicates that additional RAM may be required. In such cases, increasing total system memory and adjusting the SQL Server limit is recommended.
  • The max server memory setting can be configured in SQL Server Management Studio under server properties (Memory tab) or via T-SQL using sp_configure. Changes are applied immediately and do not require a restart. See Server memory configuration options Microsoft article for further details.
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • AdamSteele26
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore