Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Resolving Device Administrator Licensing Error "No EmbeddedLicensingRespone"

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Resolving Device Administrator Licensing Error "No EmbeddedLicensingRespone"
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
582 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Resolving Device Administrator Licensing Error "No EmbeddedLicensingRespone"

RobertAndriolo Champion
‎2026-03-29 10:37 PM

Issue

Attempts to assign or activate embedded or software licenses in Device Administrator fail when working with an Enterprise Server and Automation Servers running significantly older firmware versions (e.g., ES 3.2.x) than the DA version (DA 7.1.x) in use.

Licensing attempts fail, returning No EmbeddedLicensingResponse from the ES.


Sample messages from Device Administrator: "Detailed progress Dialogue box" 

  • Executing embedded operation: Activate ActivationID: ACT-xxxx-xxxx-xxxx
  • Failed to run script .\PythonActions\executelicensingcommand.py with arguments .\PythonActions\executelicensingcommand.py .... EmbeddedLicensingRespone returned from the server.
  • Embedded operation: Activate failed: No EmbeddedLicensingRespone returned from the server.

Product Line

EcoStruxure Building Operation 

Environment

  • EcoStruxure Building Operation Device Administrator (DA)
  • EcoStruxure Building Operation Enterprise Server (ES) 
  • EcoStruxure Building Operation Automation Servers (AS)
  • Upgrading from version 3.2x to v7.0 / v7.1 / v7.1.1.132 and above

Cause

Device Administrator 7.1 cannot activate licenses on an Enterprise Server running version 3.2.x because the two versions use different licensing systems. Over time, EcoStruxure Building Operation introduced major changes to how embedded licensing works (between versions 3.x and 7.x). As a result, an older ES cannot understand the licensing requests sent by the newer Device Administrator. This mismatch causes the server to return no response, resulting in the error “No EmbeddedLicensingResponse.”

Resolution

Upgrade target servers (ES/AS) to the desired Building Operation major version before attempting to activate the license using Device Administrator. 

Always use the latest supported Device Administrator version for the Building Operation version in use.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo26
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore