Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Otis destination dispatch controllers repeatedly go offline or DEC devices cycle offline and online

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Otis destination dispatch controllers repeatedly go offline or DEC devices cycle offline and online
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
196 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Otis destination dispatch controllers repeatedly go offline or DEC devices cycle offline and online

Alan_Wood Leader
‎2026-06-17 04:53 PM

on ‎2026-06-17 04:53 PM

Issue

Otis Destination Dispatch integration with controller models MP4502 and LP4502 experiences instability where Destination Entry Controllers (DECs) repeatedly cycle online and offline, and elevator access control intermittently stops working. In some cases, controllers remain online locally but appear offline in the system, and elevators either do not respond to badges or allow free access. Temporary workarounds such as rebooting the controller, modifying IP settings, or adding/removing a reader restore operation for a limited time before the issue reoccurs.

Product Line

EcoStruxure Access Expert

Environment

  • Mercury MP4502 controllers (firmware 2.7.x, 2.9, 2.10)
  • Mercury LP4502 controllers (firmware 1.29.x, 1.30.x)
  • Otis Destination Dispatch integration
  • Otis Compass 360 system

Warning

Potential for Data Loss: Ensure all important data is backed up before proceeding.

Cause

Instability occurs when using Mercury MP4502 controllers with Otis Compass 360 Destination Dispatch systems, resulting in intermittent loss of communication between the controller and Destination Entry Controllers (DECs).

 

Mercury MP4502 firmware has been validated with earlier Otis Compass integrations, but not explicitly with Compass 360. In this scenario, MP4502 firmware versions (2.7.x through 2.10) establish communication over TCP port 3001, however, sessions do not remain stable, leading to repeated disconnect and reconnect behavior.

 

The issue does not occur when using Mercury LP4502 controllers running firmware 1.30.2, indicating a compatibility limitation between MP4502 firmware and the Compass 360 integration in this configuration.

Resolution

Stability was achieved by replacing the MP4502 controller with an LP4502 controller running firmware version 1.30.2. After this change, DEC devices no longer exhibited online/offline cycling and the integration remained stable during operation.

Additional actions taken during troubleshooting included:

  • Upgrading MP4502 firmware to version 2.9, which did not resolve the instability
  • Attempting firmware downgrade, which was unsuccessful
  • Performing multiple temporary workarounds (controller reboot, IP refresh, configuration changes) that restored functionality only temporarily

The validated outcome is that LP4502 firmware in the 1.x branch provided stable operation for the integration, whereas MP4502 firmware versions tested did not consistently resolve the issue. Continued coordination with vendors is required for a fully supported and validated solution for Compass 360 with newer hardware.

Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (1)
  • Find more articles tagged with:
  • AlanWood26
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore