Issue
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Automation Server (AS-B, AS-P)
- SpaceLogic Operator Display (HMIST6400SL)
Cause
Adding an Operator Display to AS-B or AS-P
Resolution
- Connect to the AS-B or AS-P with EBO Device Administrator version 3.0.1 or later.
- In the AS-B/AS-P configuration, navigate to Ethernet 2 Configuration and configure:
- Ethernet 2 Mode: Dual IP
- DHCP Mode: Server
-
Verify that the default IP address for Ethernet 2 is 10.110.210.1.
- Apply and save the configuration changes.
-
Connect the Operator Display to Ethernet Port 2 on the AS-B or AS-P.
-
Verify that the Operator Display establishes communication with the server by confirming that the three red Offline indicators at the top of the display are no longer shown.
-
Connect an Building Operation WorkStation to the AS-B or AS-P.
-
Create a BACnet Interface.
-
Create a second IP Network beneath the BACnet Interface.
-
Select the server in the System Tree and open the Device Discovery tab.
- Device Discovery and locate the Operator Display in the discovered devices list.
-
Drag and drop the Operator Display onto the second IP Network.
Validation
- The Operator Display appears in Device Discovery.
- The Operator Display can be added to the second IP Network.
- The display is online and communicating with the AS-B or AS-P.