Issue
When installing a Niagara station .bog file, the following error appears:
Transfer failed. com.tridium.platform.daemon.DaemonResponseException: bad return code to commit file instance
This typically occurs during station transfer to an Enterprise Server or JACE device.
Product Line
TAC IA Series
Environment
- I/A Series N4 Enterprise Server
- I/A Series N4 Jace
Warning
Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.
Cause
The error occurs when:
- The .bog file is not located in the proper User Home → Stations directory before transfer, or
- The passphrase used to protect the .bog file is unknown or incorrect
As a result, Workbench cannot validate or unpack the station archive.
Resolution
-
Always use the Station Copier
- Install the station .bog from the designated User Home → Stations folder.
-
If the error occurs:
- Open Workbench
- Navigate to User Home → Stations
- Expand the station folder
- Double‑click the .bog file to open it
-
Force Start the Station
- In the .bog file view, select the Bog File Protection icon
- Choose “Force the file to start…”
- Click Update
Note: This operation may affect stored passphrases or security settings inside the .bog.
- In the .bog file view, select the Bog File Protection icon
-
If “Cannot display page” appears when opening the .bog:
- Open Details
- Look for missing module messages such as:
Cannot load module 'xxxx=version'. - Ensure all required modules are installed on the JACE or ES before retrying the force start.