Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

N4 ASD (tacAsd) Driver Configuration Basics

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • N4 ASD (tacAsd) Driver Configuration Basics
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • RandyDavis
    RandyDavis
  • WaynePeters
    WaynePeters
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2642 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

N4 ASD (tacAsd) Driver Configuration Basics

Product_Support
‎2018-09-06 02:00 PM

Last Updated: CraigEl Champion ‎2026-02-26 05:40 PM

Issue

Additional setup guidance is required to properly configure the ASD (tacAsd) driver in Niagara N4 for reliable communication with ASD devices.

Product Line

TAC IA Series

Environment

  • I/A Series N4 Jace 8000/9000
  • I/A Series N4 ASD driver

Cause

ASD networks require specific driver parameters to ensure proper baud‑rate synchronization, polling, and communication stability. Incorrect settings may result in devices not being discovered, long scan times, or devices reporting as down.

Resolution

Follow the configuration guidelines below to ensure correct operation of the N4 ASD (tacAsd) driver.


Monitor Properties

Property Recommended Setting Notes
Ping Enabled true Ensures devices are periodically checked for connectivity
Ping Frequency 1 minute Default is 5m
Alarm On Failure true Alerts if communication failures occur
Startup Alarm Delay 5 minutes Prevents false alarms during system start

Baud‑Rate Synchronization

ASD devices always initialize at 1200 baud at power‑up. The driver must then synchronize and set the network to the correct operational baud rate.

Parameter Value Notes
Baud Rate Sync Time 1 minute Time between sync attempts
Baud Rate Set Timeout 0.2 seconds Timeout when applying baud change
Baud Rate Set Repeat 1 Number of retry attempts
Baud Rate Change Millis 800 ms Time required for device baud transition

Important:
These values come from the ASD protocol specification and must not be modified.


Device Statistics

  • Total Devices – Number of active devices
  • Total Down – Number of devices failing communication
  • Scan Time – Time required to poll all devices
    • Example: 33 devices = approx. 6.9 seconds total, or 4.5 devices/second
  • ASD protocol exchanges most data in a single transaction, improving efficiency

Tuning Policies (Default)

Leave all tuning policy values at default unless directed by support.

Parameter Recommended Setting
Min Write Time 0
Max Write Time 0
Write On Start false
Write On Up false
Write On Enabled false
Stale Time 0

Note:
Stale time relates only to proxy point behavior. Polling and internal data updates continue normally regardless of stale settings.


Poll Scheduler

Parameter Recommended Setting Notes
Poll Enabled true Enables scheduled polling
Fast Rate 5 seconds Default: 1s
Normal Rate Use formula (devices / 3.5) Example: 33 devices = 10s
Slow Rate 30 seconds Default value is acceptable

Niagara N4 automatically and continuously optimizes polling order using its dynamic polling engine.


Retry and Timing Settings

Parameter Recommended Setting Notes
Retry Count 1 (max 3) Increase only if occasional missed responses occur
Response Timeout 2 seconds Do not change
Inter Message Delay 0.020 seconds Increase to 0.050–0.075s when using ASD repeaters
Labels (1)
Labels:
  • TAC IA Series
Tags (3)
  • Find more articles tagged with:
  • 4820
  • CraigEllis26
  • RandyDavis25
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore