Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

LON Communication Throttling in MNL‑800 Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • LON Communication Throttling in MNL‑800 Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2961 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

LON Communication Throttling in MNL‑800 Controllers

Product_Support
‎2018-09-06 02:39 PM

Last Updated: CraigEl Champion ‎2026-02-24 04:31 PM

Issue

Excessive LON network traffic can overload communication capacity, leading to LON communication delays or errors.

Product Line

TAC IA Series, EcoStruxure Building Operation

Environment

  • I/A Series MNL‑800 controllers
  • Building Operation Automation Server / ASP
  • LON networks
  • I/A Series R2, AX, and N4 JACE LON networks

Cause

Output (NVO) SNVT values are transmitted too frequently, often more frequently than operationally required.
Improper configuration of NCI timing objects (Send Heartbeat, Receive Heartbeat, Minimum Out Time, Minimum Propagation Time) can also lead to excessive traffic.

Resolution

 

Several NCI (configuration) objects control how the controller sends and receives LON data. Correct tuning prevents network saturation.

1. Send Heartbeat NCIs (nciSndHeartBeatA/B/C/D)

  • Each NVO is assigned to one Send Heartbeat group.
  • This value determines the periodic transmission interval for each bound output.

2. Receive Heartbeat NCIs (nciRcvHeartBeatA/B/C/D)

  • Each NVI is assigned to one Receive Heartbeat group.
  • If an NVI does not receive a value before the timeout, it reverts to its default value.

3. Minimum Output Time (nciMinOutTime)

  • Regulates how frequently consecutive NVO values are sent.
  • Critical rule:
    The number of bound NVOs × nciMinOutTime must be less than the shortest Send Heartbeat value.
    Example:
    • If Heartbeat = 120 seconds
    • NVOs bound = 60
      → nciMinOutTime must be < 2 seconds
  • Recommended guideline:
    nciMinOutTime = (Shortest Send Heartbeat) / (2 × Number of bound NVOs)

4. Minimum Propagation Time (nciMinPropTm)

  • Prevents rapidly changing NVOs (e.g., temperatures) from flooding the network.
  • Typical setting: 1–5 seconds

Additional Reference

More detail is available in WorkPlace Tech Tool 4.0 Engineering Guide (F‑27254), Chapter 6 (installed with Workplace Tech and also available in the WorkPlace Tech Software Package on mySchneider.)

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
Tags (3)
  • Find more articles tagged with:
  • 3366
  • CraigEllis26
  • RandyDavis22
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore