Issue
Product Line
TAC IA Series
Environment
- JACE‑8000
- Niagara 4.11 and newer
Cause
In Niagara versions prior to 4.11, the JACE‑8000 used a RAM disk to temporarily store alarm and history data. During a station save, this temporary data was copied from the RAM disk, zipped, and written to Flash.
In Niagara 4.11, the RAM disk has been fully removed. Data is now written directly to Flash, eliminating the need for temporary RAM disk storage. This change reallocates approximately 384 MB of RAM back into the system to improve performance and increase available memory for NRE (Niagara Runtime Environment) operations.
Resolution
Niagara 4.11 introduces a redesigned memory layout for the JACE‑8000, improving available system memory and performance. The RAM disk is no longer present and cannot be created. Memory categories have been adjusted as follows:
Previous NRE Defaults — Niagara 4.10 (MB)
- System Reserve: 0
- Heap Space: 360
- Metaspace: 56
- Code Cache: 16
- RAM Disk: 384
- Free Memory: ~16
Updated NRE Defaults — Niagara 4.11 (MB)
- System Reserve: 0
- Heap Space: 384
- Metaspace: 64
- Code Cache: 32
- RAM Disk: Not present
- Free Memory: ~352
Impact
- The change is transparent to most users.
- Approximately 384 MB of RAM is reclaimed.
- JACE‑8000 performance is moderately improved due to increased available system memory.
- The file system change requires no additional configuration from the user.