Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Installation Orientation Requirements for Power Supply, Automation Servers, and I/O Modules

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Installation Orientation Requirements for Power Supply, Automation Servers, and I/O Modules
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Siddharth_G
    Siddharth_G
  • DavidFisher
    DavidFisher
  • sesa139513
    sesa139513
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3336 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Installation Orientation Requirements for Power Supply, Automation Servers, and I/O Modules

Product_Support
‎2018-09-06 02:13 PM

Last Updated: Siddharth_G Contributor ‎2026-09-10 04:25 AM

Issue

Can the Power Supply (PS), Automation Server (AS/AS-P), and I/O module backplane assembly be installed vertically instead of horizontally when cabinet space is limited?

Product Line

  • EcoStruxure Building Operation

Environment

  • Power Supply (PS-24V)
  • Automation Server (AS-B, AS-P, AS-P-3)
  • Central I/O Modules
  • Hardware installation in control cabinets

Cause

Customers may prefer a vertical installation due to cabinet layout constraints or conduit routing.

Questions may also arise regarding whether more than one Automation Server can be connected to a single Power Supply.

Resolution

The system is designed, tested, and supported for horizontal mounting only.

Vertical installation is not a supported mounting method because it reduces the effectiveness of the modules' natural convective air cooling. Reduced ventilation can increase the internal operating temperature of the modules, which negatively impacts component lifetime.

Key considerations:

  • The system is specified to operate at temperatures up to 50°C (122°F) when mounted horizontally.
  • Increased internal temperature can significantly reduce the lifetime of electrical components.
  • The Automation Server (AS) is considered particularly sensitive because:
    • The CPU generates heat.
    • Critical power-retention components used during shutdown and restart are affected by elevated temperatures.
  • During normal operation, no immediate symptoms may be visible.
  • Long-term exposure to elevated temperatures can result in hardware reliability issues, including failure to restart after a power cycle.

Vertical Installation Considerations

  • Ambient temperature should not exceed 35°C (95°F).
  • Power supply loading should be reduced from 30 W to 25 W.
  • Convective air cooling relies on warm air rising through the module enclosure and being replaced by cooler air from below. Horizontal installation supports this airflow pattern and is therefore preferred.

Risk Mitigation

To minimize risk when cabinet constraints exist:

  • Always mount the Power Supply (PS) and Automation Server (AS) horizontally whenever possible.
  • I/O modules may be mounted separately and connected using an S-Cable.
  • If operating temperatures are near the maximum rated temperature, provide cabinet ventilation or external cooling in addition to mounting the PS and AS horizontally.

I/O Bus Backplane Requirements

  • More than one Automation Server cannot be connected to the same backplane because the backplane provides a communication path between connected units and Automation Servers cannot communicate on the backplane.
  • The I/O Bus supports 32 slots, including the Power Supply and Automation Server.
  • Empty backplane positions still consume a slot.

Additional Information

Refer to the SpaceLogic and EasyLogic Hardware Installation System Guide for complete installation, power budget, cooling, I/O bus, and wiring requirements.

Important installation requirements include:

  • Install the Power Supply, Automation Server, and Central I/O modules horizontally with the device label upright and reading left to right.
  • Install devices on a horizontal DIN rail to ensure proper airflow and cooling.
  • Vertical installation may exceed thermal specifications and reduce product lifespan.
  • The I/O bus supports a maximum of one Automation Server per I/O bus.
  • I/O bus device order must be maintained:
    • Position 1: Power Supply
    • Position 2: Automation Server
    • Position 3-32: Central I/O modules and additional power supplies as required
  • The I/O bus supports a maximum of 32 positions.
  • S-cables may be used to connect multiple DIN rail sections while maintaining I/O bus continuity.

Conclusion: Horizontal mounting is the only supported installation method. If vertical mounting is used, it is not a supported installation method and is performed at the installer's risk. Maintaining operating temperatures well below the maximum rated value is critical to reducing the risk of reduced product life and long-term reliability issues.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • 4435
  • SiddharthG26
Was this article helpful? Yes No
67% helpful (2/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore