Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Importing large Enterprise Server (ES) backups

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Importing large Enterprise Server (ES) backups
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
533 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Importing large Enterprise Server (ES) backups

RobertAndriolo Champion
‎2026-02-15 07:37 PM

Issue

Importing a very large Enterprise Server (ES) backup in WorkStation appears to hang with no visible progress, and the subsequent restore on a new ES seems stalled during validation. In some cases, a message such as “Unable to validate checksum” is shown even when the backup is healthy.

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation Enterprise Server (large ES backups > ~50 GB with extensive trends/events)
  • EcoStruxure Building Operation WorkStation
  • Restore the full backup to the new hardware after the Enterprise Server host failure
  • Local backup directory, e.g.: C:\ProgramData\Schneider Electric EcoStruxure\Building Operation <version>\Enterprise Server\db_backup\LocalBackup

Warning

Potential for Data Loss: The steps below involve backup and restore operations. Ensure you have verified backups and adequate free disk space before proceeding. If unsure, contact your local support for assistance.

Cause

For very large ES backups, the WorkStation “Import” provides minimal progress feedback and performs additional background processing, which can take a long time and appear unresponsive.

 

During restore to a new ES, the system performs a validation phase that may take several minutes before any prompt appears; if the confirmation is not accepted in time, the restore can abort. The “Unable to validate checksum” message can be expected when restoring a backup created on a different machine and does not necessarily indicate corruption.

Resolution

  1. Bypass the slow WorkStation import for large backups (>40-50 GB): Manually copy the ES backup file into the local backup directory (e.g., ...\db_backup\LocalBackup). This allows WorkStation to detect the backup without relying on the long-running import dialog.  See the following article for instructions on how to perform this: Failed to import backup set file.
  2. Run the restore and watch for the confirmation prompt: Start the restore from WorkStation and allow time for the validation phase. The confirmation dialog may take ~10–11 minutes to appear on SSD-based systems and may surface behind other windows. Accept the prompt as soon as it appears so the restore can proceed;  WorkStation will log out automatically, and the ES service will continue the process.
  3. Allow additional time for restore startup feedback: After confirmation, it may take another ~10–11 minutes for visible restore progress to appear. Monitoring disk activity can help confirm ongoing work.
    1. Zero disk activity during Import indicates completion of Import as seen below:
      Import-Disk.png
    2. After the import is complete, monitor the EcoStruxure BuildingOperation process for excessive disk activity, which indicates the restore is still in progress.  
      EBO - Process.png
    3. An alternative method, but with minimal feedback, you can view the Building Operation Software Administrator Server status
      1. Starting - means the service is starting, but not yet running.  Server will not accept any login commands.
        ES-ServerStarting.png
      2.  Running - server is now running.  Users can now login. 
        ES-ServerRunning.png
  4. Ensure sufficient free disk space: Keep roughly 2× the backup size free (e.g., ~120 GB for a 50 GB backup) to accommodate validation and temporary files.
  5. Optimize for future reliability and speed: Recommend using SSD storage for the ES and backups; using non-SSD drives in these instances will increase delays from 15-30 minutes to 1-2 hours. 
    Reduce database size by enabling External Log Storage where appropriate, and after a successful recovery on the new machine, take a fresh full backup (this can avoid validation delays on subsequent restores to the same system).
  6. Note on checksum validation message: Seeing “Unable to validate checksum” when restoring a backup created on a different system can be expected and is not, by itself, evidence of backup tampering.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo26
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.