Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Identify WorkPlace Tech Application Version (Detect if Created with WPT 3.2sp1 or Older)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Identify WorkPlace Tech Application Version (Detect if Created with WPT 3.2sp1 or Older)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • sesa116877
    sesa116877

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1343 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Identify WorkPlace Tech Application Version (Detect if Created with WPT 3.2sp1 or Older)

Product_Support
‎2018-09-07 01:57 AM

Last Updated: CraigEl Champion ‎2026-02-17 06:05 PM

Issue

Determine whether a WorkPlace Tech (WPT) application was created or edited using WorkPlace Tech 3.2sp1 or an earlier version, in order to know if it can be safely converted by WPT 4.x or WPT 5.x.

Product Line

TAC IA Series

Environment

WorkPlace Tech

Cause

The installed controllers may have been programmed using older versions of WorkPlace Tech. Applications created before WPT 3.2sp1 do not contain version metadata and should not be converted using WPT 4.x or 5.x without verification.

Resolution

⚠️ Critical Warning

Do not allow Visio or WorkPlace Tech to convert or update the application if prompted.
Selecting "Yes" may permanently modify the file and prevent correct identification or migration.


1. Open the Application in Visio

Visio is sufficient; WorkPlace Tech does not need to be installed.

2. Access the ShapeSheet

  1. Hold down the left Shift key.
  2. While still holding Shift, right‑click the background.
  3. Select Show ShapeSheet, keeping Shift held until the ShapeSheet opens.
    • If the ShapeSheet header does not show the file name followed by "", close it and repeat.

3. Check the User-defined Cells Section

Locate User-defined Cells.
Look for: User.wptVersion

4. Interpret Results

  • User.wptVersion is present
    The application was created/edited with WPT 3.2sp1 or newer and can be converted safely.

  • User.wptVersion or the entire User-defined Cells section is missing
    The application was created with WPT earlier than 3.2sp1 and must not be converted.

5. Close Without Saving

When exiting Visio, select No when asked to save.


Additional Notes for Visio 2010

To enable the Developer tab:
File → Options → Customize Ribbon → enable Developer

To open the ShapeSheet manually:
Developer → Shape Design → Show ShapeSheet (Shape, Page, or Document)Wptversion LL3336.jpg

Labels (1)
Labels:
  • TAC IA Series
Tags (2)
  • Find more articles tagged with:
  • 3336
  • CraigEllis26
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore