Issue
Product Line
TAC IA SeriesEnvironment
- MNB‑70
- MNB‑300
- MNB‑1000
- MNB‑V1 / MNB‑V2
Cause
Firmware for I/A Series Micronet BACnet (MNB) controllers is difficult to locate within mySchneider.
Resolution
- Log in to mySchneider.
- In the search bar, enter "MNB firmware".
- Download the firmware package that corresponds to the specific controller model:
- MNB‑ASC Series (MNB‑70, MNB‑300, MNB‑V controllers)
- MNB‑1000
- Before applying the firmware:
- Ensure full controller and database backups.
- Confirm the firmware package matches the exact controller model and hardware type.
- Apply the firmware using the approved I/A Series engineering tools following the directions in the firmware release note.
- After upgrade:
- Verify controller communication
- Confirm BACnet device and point integrity
- Validate proper operation of all applications