Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to Change an Existing Enterprise Download Server Deployment from Typical to Large

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to Change an Existing Enterprise Download Server Deployment from Typical to Large
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AndreasP
    AndreasP

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
33 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to Change an Existing Enterprise Download Server Deployment from Typical to Large

AndreasP Contributor
‎2026-11-04 02:51 PM

on ‎2026-11-04 02:51 PM

Issue

An existing Security Expert Enterprise Download Server is deployed using the Typical deployment size and needs to be changed to the Large deployment size.

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert Server
  • Security Expert Enterprise Download Server

Cause

The deployment size of an existing Enterprise Download Server cannot be changed in place.

  • A Typical deployment cannot be converted to Large by changing the deployment size of the existing virtual machine.
  • A new Enterprise Download Server virtual machine must be deployed using the Large deployment size.
  • The new virtual machine must be allocated the CPU cores, RAM, and disk capacity required for the Large deployment size.
  • Controllers must be paired with the newly deployed Enterprise Download Server.

Resolution

To change an existing Enterprise Download Server deployment from Typical to Large, deploy a new Large Enterprise Download Server and retain the existing Typical deployment until the new environment has been successfully validated.

Prepare for the migration:

  • Plan an appropriate maintenance window for the Enterprise Download Server migration.
  • Create a current backup of the Security Expert SQL databases. The required Security Expert system data used by the software is stored in the SQL database tables.
  • Be aware that historical log data stored locally on the existing Enterprise Download Server will not be available after the old virtual machine is deleted.

Deploy the new Enterprise Download Server:

  1. Shut down the existing Enterprise Download Server virtual machine. Do not delete it at this stage.
  2. Start a new Enterprise Download Server deployment.
  3. Select Large as the deployment size.
  4. Ensure that the new virtual machine is allocated the required number of CPU cores, RAM, and disk capacity for a Large deployment.
  5. Complete the Enterprise Download Server deployment process.
  6. Pair all controllers with the newly deployed Enterprise Download Server.

Validate the new deployment:

  • Confirm that the new Enterprise Download Server virtual machine is running.
  • Confirm that the Enterprise Download Server was deployed using the Large deployment size.
  • Confirm that the virtual machine resources meet the Large deployment prerequisites.
  • Confirm that all controllers are successfully paired with the new Enterprise Download Server.
  • Confirm that controller communication and downloads through the new Enterprise Download Server are operating successfully.

Remove the previous deployment:

After the Large Enterprise Download Server has been successfully validated and all controllers are operating through the new deployment, the previous Typical Enterprise Download Server virtual machine can be deleted.

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • AndreasPettersen26
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore