Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

GCM Integration Slows After Niagara R2 UNC Upgrade from Version 431 to 5xx

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • GCM Integration Slows After Niagara R2 UNC Upgrade from Version 431 to 5xx
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Leo_Tantalo
    Leo_Tantalo
  • Kim_Baze
    Kim_Baze
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7936 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

GCM Integration Slows After Niagara R2 UNC Upgrade from Version 431 to 5xx

Product_Support
‎2018-09-10 03:54 AM

Last Updated: CraigEl Champion ‎2025-12-17 08:15 PM

Issue

After upgrading a Niagara R2 UNC from version 431 to 5xx, GCM objects update more slowly than before. Users notice delayed polling and sluggish integration performance.

Product Line

TAC IA Series

Environment

  • Niagara R2 UNC-520 (all revisions)
  • GCM integration using GCMCommService

Cause

The station settings for GCMCommService may not be configured to recommended values after the upgrade. Older installations often retain legacy settings that do not align with current best practices.

Resolution

Review and adjust the following settings based on Appendix B of the Niagara Network 8000 Serial Driver Engineering Guide (F-27070) and Technical Bulletin 03_03:

  1. GCMCommService Settings

    • Navigate to the General - Config tab of GCMCommService.
    • Apply recommended changes from Technical Bulletin 03_03.

  2. GCM Object Poll Settings

    • Go to the Poll - Config tab of each GCM object.
    • Set cycleTime = 0 ms to synchronize the GCM's poll cycle with the GCMCommService.

    • Ensure both the GCMCommService and GCM object use the same cycleTime values.
  3. Reference Documentation

    • Niagara Network 8000 Serial Driver Engineering Guide (F-27070)
    • Technical Bulletin 03_03: Niagara R2 Network 8k Serial Driver
Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (2)
  • Find more articles tagged with:
  • 6529
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.