GCM Integration Slows After Niagara R2 UNC Upgrade from Version 431 to 5xx
Select a Country
  • GCM Integration Slows After Niagara R2 UNC Upgrade from Version 431 to 5xx
  • CraigEl
    CraigEl
  • Leo_Tantalo
    Leo_Tantalo
  • Kim_Baze
    Kim_Baze
‎2018-09-10 03:54 AM
Last Updated: CraigEl Champion ‎2025-12-17 08:15 PM
After upgrading a Niagara R2 UNC from version 431 to 5xx, GCM objects update more slowly than before. Users notice delayed polling and sluggish integration performance.
TAC IA Series
  • Niagara R2 UNC-520 (all revisions)
  • GCM integration using GCMCommService
The station settings for GCMCommService may not be configured to recommended values after the upgrade. Older installations often retain legacy settings that do not align with current best practices.
Review and adjust the following settings based on Appendix B of the Niagara Network 8000 Serial Driver Engineering Guide (F-27070) and Technical Bulletin 03_03:
  1. GCMCommService Settings
    • Navigate to the General - Config tab of GCMCommService.
    • Apply recommended changes from Technical Bulletin 03_03.
  2. GCM Object Poll Settings
    • Go to the Poll - Config tab of each GCM object.
    • Set cycleTime = 0 ms to synchronize the GCM's poll cycle with the GCMCommService.
    • Ensure both the GCMCommService and GCM object use the same cycleTime values.
  3. Reference Documentation
    • Niagara Network 8000 Serial Driver Engineering Guide (F-27070)
    • Technical Bulletin 03_03: Niagara R2 Network 8k Serial Driver
  • TAC IA Series
Tags (2)
  • 6529
  • CraigEllis25