Events Missing from the Status Page
  • Events Missing from the Status Page
  • AdamSteele
    AdamSteele
AdamSteele Champion
‎2026-10-29 08:59 PM
Door Open and Close events for certain doors are not displayed on the Status Page. Doors are functioning and the Door events are displayed correctly in an Event Search or default All Events report.
EcoStruxure Security Expert
  • Security Expert Client
  • Security Purpose Controller (SP-C)
The Event report used in the Status page configuration has an Event filter configured with the Record group set to "<Not set>".
Event report filterEvent report filter
Most Doors are also configured with the Record group field set to "<Not set>". These doors events are seen in the Status page.
Record group not setRecord group not set
A few Doors have a valid Record group assigned to them. These doors events are not seen in the Status page.
Record group setRecord group set
This is expected behavior. On an Event report’s Event filter, the Record group setting acts as a scope. <Not set> is the default “no record group” value, and it is treated as a record group not as “All record groups”.
An Event filter entry set to <Not set> only matches events whose records (e.g. doors) are also set to <Not set>. Records that have been assigned a specific record group won’t match that entry, which is why their events are missing from the Status page.
Either remove the Record Group setting from the affected doors or change the Event filter in the Door Event report to "Access all record groups" so that the doors are not filtered out.
Event filter record groupsEvent filter record groups