Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Esmi Ultima Media Gateway Card Not Communicating with Modbus/BACnet Converter

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Esmi Ultima Media Gateway Card Not Communicating with Modbus/BACnet Converter
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Sandeep_Kumar006
    Sandeep_Kumar006

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
650 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Esmi Ultima Media Gateway Card Not Communicating with Modbus/BACnet Converter

Sandeep_Kumar006 Troubleshooter
‎2025-08-29 01:08 AM

Issue

The Media Gateway Card fails to transmit panel messages to the converter used for Modbus or BACnet translation. This results in loss of communication between the Esmi Ultima fire panel and the BMS.

Product Line

ESMI Fire Detection.

Environment

  • Esmi Ultima System
  • Media Gateway Card (FFSULH1007)
  • Integration with Modbus or BACnet

Warning

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

If you are unsure about any of the technical steps, or if you are not familiar with the Media Gateway Card configuration, contact Product Support for guidance before continuing.

Cause

The TCP/IP port on the Media Gateway Card is not functioning correctly, causing communication failure between the fire panel and the BMS interface.

Resolution

1. Verify Firmware Version

  1. Navigate to Engineer Options → System Information.
  2. Confirm cabling:
    • LAN cable connected to Media Gateway Card LAN port.
  3. Check the installed firmware version.
    • Expected firmware: S794_V01.109

If the firmware version is missing, unreadable, or outdated:

  • Perform a firmware update.
  • Refer to the article: Esmi Ultima Media Gateway Card Firmware Update

2. Configure Graphics / Third‑Party & VR Settings

Graphics / Third‑Party Settings

  1. Navigate to
    Engineer Options → Configuration → Panel Module → Media Gateway Card
  2. Select Graphics / Third‑Party Settings.
  3. Apply configuration values as shown in the reference images.

    Image (23).jpg

    Image (24).jpg

  4. Submit the settings.

VR Settings

  1. In the same menu, open VR Settings.
  2. Apply configuration values as per the reference images.

    Image (20).jpg

    Image (21).jpg

    Image (22).jpg

  3. Submit the settings.

Outcome

After completing the firmware verification and applying the required Graphics and VR settings, the Media Gateway Card should resume sending messages to the converter, restoring normal Modbus/BACnet communication with the BMS.

Labels (1)
Labels:
  • ESMI Fire Detection
Tags (2)
  • Find more articles tagged with:
  • SandeepKumar25
  • SandeepKumar26
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore