Esmi Ultima Loop Explorer2 Configuration Software Licence Expired
Building Automation Knowledge Base
Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Loop Explorer (LE2) configuration software showing license expired and all the options are not working (like transfer configuration).
Product Line
ESMI Fire Detection.
Environment
Loop Explorer 2 (LE2) Configuration software.
Cause
The LE2 software was unable to validate the current license status using the locally stored license information. Updating the license information from the licensing server restored access to the restricted functions.
Resolution
To update the Esmi Ultima Loop explorer configuration software (LE2) license credentials:
Connect the PC running LE2 software to the internet.
Open the LE2 software.
Navigate to theHelptab.
ClickUpdate.
In the update window, select theLicensetab.
Review the displayed license login credentials.
ClickCheck Now.
The software will automatically check for an available license update and update the license information if required.
Confirm that the license expiry message is no longer displayed and that previously unavailable functions, such as configuration transfer, can be accessed and used successfully.
If the update does not complete successfully, verify internet connectivity and contact local Product Support for further assistance.