Issue
When attempting to use the Save To function to create a local AS-P backup, WorkStation displays the error message "Value does not fall within the expected range" and the backup cannot be saved.
Product Line
EcoStruxure Building Operation
Environment
- Building Operation WorkStation
- Building Operation Automation Server
Cause
The issue is related to the backup path stored in the WorkStation user profile, where the previously used save location is no longer available.
Resolution
Close all WorkStation instances and delete the contents of the following folder:
%appdata%\Schneider Electric EcoStruxure\Building Operation\WorkStation
After clearing the WorkStation profile data, reopen WorkStation and perform the backup again.