Issue
When adding an Enterprise Server (ES) to an Enterprise Central (EC), the following error is displayed:
"Cannot add a server to the system with an already existing unique ID"
Product Line
EcoStruxure Building Operation
Environment
Building Operation Enterprise Server
Building Operation Enterprise Central
Cause
The Enterprise Server has the same Globally Unique Identifier (GUID) as another Enterprise Server in the system.
The GUID is a unique identifier associated with the server configuration and database structure. An Enterprise Server that has been cloned may retain the original GUID, resulting in a duplicate unique ID within the system.
Changing the GUID of an Enterprise Server by restoring a backup with new IDs is not supported due to system integrity and object referencing constraints within EcoStruxure Building Operation.
Resolution
Restoring an Enterprise Server with new IDs (GUIDs) is not supported.
To create an Enterprise Server with a unique GUID:
- Set up a new Enterprise Server instance.
- Use the Export/Import feature to transfer supported objects from the existing Enterprise Server.
- Manually recreate any settings or objects that cannot be exported.