Issue
After moving one or more Automation Servers from an existing Enterprise Server to another Enterprise Server, existing bindings and references may become unresolved.
This may occur when:
- Consolidating Enterprise Servers.
- Migrating Automation Servers between Enterprise Servers.
- Enterprise Server or Automation Server names and object paths change during the migration.
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Enterprise Server (ES)
- Building Operation Enterprise Central (EC)
- Building Operation Automation Server (AS / AS-B / AS-P / AS-P-3)
- Multi-Server System
Cause
When an Automation Server is detached from an Enterprise Server, Enterprise Server-to-Automation Server bindings and references are removed.
This is expected behavior because those bindings depend on the relationship between the Enterprise Server and the Automation Server.
If the Automation Server is subsequently attached to an Enterprise Server with an identical structure, some bindings may reconnect automatically. However, automatic reconnection is not guaranteed and should always be validated after migration.
Resolution
After the Automation Server is attached to a different Enterprise Server:
- Validate all required Enterprise Server-to-Automation Server bindings.
- Recreate any bindings that no longer resolve.
- Do not rely on bindings being preserved during the detach process. There is no option to preserve these bindings when the Automation Server is detached.
- If the destination Enterprise Server has an identical binding structure, some bindings may reconnect automatically. Validate these bindings after migration rather than relying on automatic reconnection.
- If the destination Enterprise Server has a different structure, bindings may be unable to resolve and must be recreated.
To reduce the effort required to recreate bindings before migration:
- Export binding information where possible.
- Create binding templates.
- Use Find and Replace to update bindings where appropriate.
- Use Bindings Diagnostics before and after migration to identify unresolved or invalid references.
Where Automation Servers communicate with other Automation Servers, validate all cross-server references after the migration and recreate any references that are no longer valid.