Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Duplicated Segment and Object Names Prior to EBO Transition

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Duplicated Segment and Object Names Prior to EBO Transition
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1853 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Duplicated Segment and Object Names Prior to EBO Transition

DavidChild Champion
‎2020-06-04 05:23 AM

Last Updated: CraigEl Champion ‎2025-11-02 11:34 PM

Issue

When transitioning from Sigma to EcoStruxure Building Operation (EBO), duplicated segment and object names in Sigma can cause issues during data import. Unlike Sigma, EBO does not allow duplicate names within the same folder or segment.


⚠️ Important Notice

Sigma is not supported in EBO 2022 and later.
To continue supporting Sigma devices, you can implement a multi-version system:

  • Keep Enterprise Servers with Sigma devices on Building Operation 3.2.
  • Add a Building Operation 2022 or later Enterprise Central
  • Upgrade the rest of the system to Building Operation 2022 or later.

You will not be able to upgrade EcoStruxure Building Operation servers that contain unsupported protocols, objects, or devices. Attempting to do so will result in failed upgrades or loss of functionality.

Product Line

Satchwell Sigma

Environment

  • Ecostruxure Building Operation
  • SigmaX

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

In Sigma, object names could be duplicated as long as their mnemonics were unique. However, EBO enforces stricter naming rules, disallowing duplicate names within the same context. This discrepancy can lead to import errors or unintended renaming during the transition.

Resolution

To ensure a smooth transition from Sigma to EBO:

  1. Understand EBO Naming Rules

    • EBO requires unique object names within the same folder or segment.
    • During data import, EBO automatically appends a postfix (e.g., room temperature2) to duplicated names to allow the import to proceed.
  2. Launch SigmaX.
    If you encounter issues such as Side-by-Side errors or missing SigmaX files, refer to the relevant Knowledge Base articles for troubleshooting.

  3. Use SigmaX to Identify Duplicates

    • Generate a report to identify duplicated segment and object names.
    • The report will list any duplicated index or object names that may cause issues during import.
  4. Rename Duplicates in SigmaX

    • Within SigmaX, rename duplicated objects to unique names of your choosing.
    • This ensures that the Data Import process uses the updated names without automatic postfixing.
  5. Watch the Tutorial Video.

    A step-by-step video is available demonstrating how to perform this check. This is the third video in a series:

    • Video 1: Checking for Database Errors
    • Video 2: Identifying Duplicated Names (this article)
    • Video 3: Checking for Multiple RETURN Types
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (3)
  • Find more articles tagged with:
  • CraigEllis25
  • DavidChild20
  • DavidChild22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore