Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Duplicate 03:00 Trend Log Entries After Daylight Saving Time Change

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Duplicate 03:00 Trend Log Entries After Daylight Saving Time Change
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
436 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Duplicate 03:00 Trend Log Entries After Daylight Saving Time Change

CraigEl Champion
‎2026-04-28 06:32 PM

on ‎2026-04-28 06:32 PM

Issue

After a Daylight Saving Time (DST) transition, interval trend logs in EcoStruxure Building Operation may display two entries with the same local timestamp, most commonly 03:00 AM, on the DST changeover day. This can be interpreted as duplicated or incorrect trend data.

Product Line

EcoStruxure Building Operation

Environment

  • SmartX IP Controllers (MP/RP)
  • EBO native Trend Log objects
  • BACnet Trend Log objects hosted in SmartX controllers
  • WorkStation and WebStation

Cause

EcoStruxure Building Operation servers and SmartX controllers operate internally using UTC (Coordinated Universal Time).

  • Trend data is stored and processed in UTC
  • Time zone and DST adjustments are applied only at the UI layer (WorkStation / WebStation)

It is important to distinguish between EBO native Trend Log objects and BACnet Trend Log objects used in SmartX IP controllers, as their configuration options differ.

EBO Native Trend Log Objects

  • Created on Automation Servers or Enterprise Servers
  • Support an Interval Time Zone setting
  • The Interval Time Zone setting controls how the next interval sample is scheduled (UTC or Server Local Time), particularly for long intervals such as daily logs
  • As described in the existing “Interval time zone setting in Trend log” article, using Server Local Time may result in intervals of 23 hours (DST start) or 25 hours (DST end)

This setting affects interval duration only. It does not change how timestamps are stored. All samples remain uniquely timestamped in UTC.

BACnet Trend Log Objects (SmartX MP/RP Controllers)

  • Implemented as standard BACnet Trend Log objects
  • Do not have an Interval Time Zone setting
  • Interval sampling is based on elapsed time using UTC and is unaffected by DST changes at the controller level

During a DST fallback (Autumn), the local clock hour is repeated. As a result, two distinct UTC timestamps may be converted by the UI into the same local time when displayed. This causes two trend entries to appear with the same local timestamp (for example, 03:00 AM).

There is no duplication or ambiguity in the stored trend data. The duplicated timestamp is a local-time display effect caused by UTC‑to‑local‑time conversion during a repeated hour.

Resolution

This behaviour is expected and correct.

  • Trend data remains accurate and uniquely timestamped in UTC
  • Duplicate local timestamps appear only when UTC timestamps are rendered in local time during a DST fallback
  • The Interval Time Zone setting does not prevent duplicate local timestamps
  • BACnet Trend Log objects do not support Interval Time Zone configuration
  • No supported fix exists to suppress one of the entries without discarding valid data

Customers should be advised that DST transition days may show repeated local times in trend logs

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • CraigEllis26
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore