Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DALI Emergency Status Light – Interpretation of Status Values

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • DALI Emergency Status Light – Interpretation of Status Values
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Katha
    Katha

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
166 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

DALI Emergency Status Light – Interpretation of Status Values

Katha Troubleshooter
‎2026-07-31 06:16 PM

on ‎2026-07-31 06:16 PM

Issue

The DALI Emergency Status Light object contains several status-related properties that are represented as an Integer value. Each Integer value corresponds to one or more status flags reported by the DALI device.

 

The purpose of this article is to provide a clear mapping between the Integer values and their corresponding flags for each DALI Emergency Status property.

Product Line

EcoStruxure Building Operation

Environment

Dali Expansion Module

Cause

DALI Emergency Status properties are reported as integer values that represent one or more status flags combined using a bitmask calculation. A single displayed value may therefore correspond to multiple active device conditions.

Resolution

The DALI Emergency Status Light object reports several status-related properties as Integer values. Each value represents one or more active status flags using a bitmask calculation.

How to interpret a status value

  1. Identify the property being evaluated (for example, Emergency Mode or Emergency Status).
  2. Locate the corresponding flag table below.
  3. Compare the reported Integer value against the available flag values.
  4. Determine which flag values add up to the reported Integer value.
  5. The resulting flags represent the current state reported by the DALI emergency device.

Example

A device reports an Emergency Mode value of 10.

Value Flag
2 Normal Mode
8 Extended Emergency Mode

Because:

10 = 8 + 2

the following flags are active:

  • Normal Mode
  • Extended Emergency Mode

Multiple flags can be active simultaneously, resulting in a combined Integer value.

Light Information

Value Flag
1 Control gear failure
2 Lamp failure
4 Lamp on
8 Limit error
16 Fade running
32 Reset state
64 Short address not assigned
128 Power cycle seen

Emergency Mode

Value Flag
1 Rest Mode
2 Normal Mode
4 Emergency Mode
8 Extended Emergency Mode
16 Function test in progress
32 Duration test in progress
64 Hardwired inhibit is active
128 Hardwired switch is on

Emergency Features

Value Flag
1 Integral emergency control gear
2 Maintained control gear
4 Switched maintained control gear
8 Auto test capability
16 Adjustable emergency level
32 Hardwired inhibit supported
64 Physical selection supported
128 Re-light in rest mode supported

Emergency Failure Status

Value Flag
1 Circuit failure
2 Battery duration failure
4 Battery failure
8 Emergency lamp failure
16 Function test maximum delay exceeded
32 Duration test maximum delay exceeded
64 Function test failed
128 Duration test failed

Emergency Status

Value Flag
1 Inhibit Mode
2 Function test done and result valid
4 Duration test done and result valid
8 Battery fully charged
16 Function test request pending
32 Duration test request pending
64 Identification active
128 Physically selected

Validation

After decoding the reported value, compare the active flags against the current device condition, including:

  • Emergency lighting operating mode
  • Test status
  • Battery status
  • Reported device failures or alarms

Confirm that the decoded flags accurately reflect the observed state of the DALI emergency device before proceeding with further troubleshooting.

Important Notes

  • Each status flag is represented by a unique bit value.
  • Multiple active flags are combined into a single Integer value.
  • A higher value does not necessarily indicate a more severe condition.
  • Always decode the Integer value into its component flags to understand the actual device status being reported.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • KatharineVasquez26
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore