Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Conversion of Continuum devices from i2 to b3 and vice-versa in the field

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Conversion of Continuum devices from i2 to b3 and vice-versa in the field
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
28800 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Conversion of Continuum devices from i2 to b3 and vice-versa in the field

AbeMeran Mentor
‎2022-12-06 09:57 AM

Issue

Continuum i2 and b3 field devices use the same hardware. With the exception of
their -V models and the bCX (bCX9640/bCX4040) controller, they were not
designed to have their firmware swapped from Infinet to BACnet (or BACnet to
Infinet) in the field.

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

  • Continuum i2 Controllers (except -V)
  • Continuum b3 Controller (except -V)

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

With the exception of the -V controllers, the devices were not designed to have their protocol (Infinet/BACnet) swapped in the field, however, due to changes in market needs R&D is now providing a method to allow the protocol to be changed in the field.

Resolution

IMPORTANT NOTES:

If a RoamIO2 is available, it can be used to do the conversion without the need to have Continuum Cyberstation and Continuum controllers.

https://community.se.com/t5/Building-Automation-Knowledge/Conversion-of-Continuum-devices-from-i2-to... 

 

If the device you are converting is of model i2/b3 865/866/885 STOP

First confirm that the device is NOT a -V device, this is accomplished by editing the device and inspecting its version number, -V devices have a "1" embedded in the second part (after the ".") of the version number

 

Screenshot 2026-06-24 112115.jpg

A non -v device will show the above version number as follow,,,

3.500027

 

To convert i2 field devices into b3 BACnet (or vice-versa) from CyberStation

  1. Contact PSS and request the conversion files for the specific model(s) you wish to convert.
  2. Follow the procedure detailed below or as per the attached document.

To swap the firmware of any non -V i2 device from one protocol to the other (in this case, from Infinet to BACnet b3), you use the following procedure.  For more information, see section 1.3 “Converting Infinet i2 Field Devices to BACnet b3 Devices from CyberStation” below.


NOTE: This procedure was developed by Schneider Electric’s R&D and tested in the Product Support Services (PSS) lab.

 

Before starting the procedure, you need the following items:

  • An I2 device(s) to be converted.
  • A Continuum CyberStation with i2 device(s) configured and online.
  • A special, conversion b3 upgrade file for the appropriate device model as provided by PSS
  • A b3 bootloader file for the appropriate device model, provided by PSS
  • Physical access to the device.  You need this to push its Restart switch or to access the switch or breaker where you can shut off power to the device to force a restart.
  • A bCX4040 controller configured in CyberStation

xP Expansion I/O Note

If the device to be converted from i2 to b3 has any expansion modules attached, make sure the modules do not exceed the power capacity of the expansion port (180 mA), it has been observed that the b3 devices adhere more strictly to the 180 mA limit than the i2 devices, resulting in loss of operation on IO channels located on the Expansion Port if the power limit is exceeded. 

See attached xP Expansion IO Datasheet for information on power consumption of each xP IO module.

 

1.2 Preparing the Field Bus for the i2 to b3 Device Conversion

To ensure a smooth conversion, it is necessary that you reduce the traffic on the field bus as much as possible in order to provide the necessary bandwidth to the upgrade operations required for the conversion. Before starting the process with the conversion file, be sure to follow these instructions. 

 

To prepare the field bus for the i2 to b3 device conversion

  1. Disable all the programs in all the devices residing in the field bus.
  2. Close all Continuum Workstations except the one performing the upgrade.
  3. In the Workstation performing the upgrade, close all graphics, List views, and anything else that could be polling data from the field bus.
  4. Make sure MS/TP field bus is on same baud rate as Infinet field bus, mainly
    19.2K

1.3 Converting i2 Field Devices into b3 BACnet from CyberStation
You can convert Infinet i2 field devices into b3 BACnet field devices by swapping the firmware of any non -V model i2 device.


IMPORTANT: When using this procedure, be aware of the following guidelines:

  • It applies ONLY to the firmware or communication protocol (Infinet or BACnet) of the device. It does not convert the control application in the device. Following conversion, the device’s memory is cleared, so you need to configure a new control application.
  • It may result in a loss of critical data if not performed properly. Before beginning, ensure that all important data is backed up in the event of data loss or the device losing its application and becoming non-operational.  For more information, see section 1.1 “Introduction” above.

To convert i2 field devices into b3 BACnet from CyberStation

  1. Contact PSS and request the conversion files for the specific model(s) you
    wish to convert.
    You will be provided with an application file (namely,
    i2920toB3920B4.500077.upd) and a boot loader file (namely,
    B3920BootB4.500077.upd).
  2. From CyberStation, edit the i2 device and record its Serial Number and Infinet id.
    Consult the General tab to locate this information.
  3. From the Runtime tab, perform a Reset to clear the device’s database.
  4. Upgrade the i2 device using the application file provided by PSS.
    Once the upgrade is complete, the i2 device stays Offline since its communication protocol has now been swapped from Infinet to BACnet.
  5. Disconnect the device from the Infinet field bus of its host master controller (for example, a CX9680 or a bCX9640).
  6. Connect it to the bCX4040 MS/TP field bus. (MAKE SURE MS/TP FIELD
    BUS IS RUNNING AT SAME BAUD AS INFINET FIELD BUS DEVICE
    WAS ON, NAMELY 19.2K BAUD)
  7. In the bCX4040, configure a b3 device using the appropriate model as well the Serial Number and ID recorded previously.
    NOTE: You will need to provide BACnet Device ID. Typically, it will be the same as the Serial Number. You can also use a Learn to bring the device online under the bCX4040 and automatically assign the model, id etc.  Refer to this Knowledge Base article on using the serial number for the Device ID.  Remember here to set the Comm Port for comm2.
  8. Restart the device either by power cycling or using the restart button.
    The device will come online under the bCX4040 as a b3 device.
  9. Perform an Update b3 OS operation to send the appropriate b3 boot loader file provided by PSS.
  10. Go to the Runtime tab, and reset the device once the update is finished.
  11. Once the device reboots and comes back online, you can confirm it has the right boot loader by looking at the device from the BACnet side.
    The screenshots that follow display the before and after results of the i2 to b3 conversion process.

Before:

ConversionFirmwareBefore.png

After:

ConversionFirmwareAfter.png

NOTE 1

If Continuum system is not available it is also possible to convert i2 to b3 using RoamIO and EBO server using the following steps

  1. Disconnect device from field bus and connect RoamIO directly to i2 device.
  2. Use InfinetServiceTool to send the application conversion file to the i2 device.
  3. After the uprev operation is done disconnect RoamIO and cycle power to the i2 device
  4. Connect converted device (now a b3) to MSTP of AS-P or other EBO server that supports BACnet MSTP
  5. Perform a b3 learn operation to bring the device online
  6. Right click the b3 device and proveed to 'Device->Update firmware...'
  7. Navigate to appropriate boot loader file for the b3 model
  8. After uprev of boot loader is complete, cycle power to the b3 device.

NOTE 2
Similar steps can be used to convert b3 device to i2 device.

Make sure to use the V2 version of the b3 to i2 conversion files as it was found the original set of b3 to i2 conversion files did not work in some cases.

b3toi2V2.JPG

Please note that once a b3 device has been converted to i2 using this procedure the device will ONLY accept conversion uprev files, attempt to uprev using regular uprev file will result in the following error:

 

This Uprev file does not match this type of controller.


This applies to b3 to i2 conversion only, it does not apply to i2 to b3 conversion.

Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Attachments
Tags (5)
  • Find more articles tagged with:
  • AbeMeran22
  • AbeMeran23
  • AbeMeran24
  • AbeMeran26
  • DavidShore23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore